  1. #14
    Valves aren't what they used to be. I heat sink the valves with extra rags...makes brazing a little tougher, but at least I don't cook any more cheap Chinese valves.

    I'd hate to be the guy using a Turbo Torch these day...you have to use them full open and you can't adjust the flame size. Makes for any easy overheat situation.

    I know few guys who can use a Turbo with out over heating line set and valves.

  2. #15
    Join Date
    Dec 2011
    Location
    ms
    Posts
    122
    what the brand of that pinch off tool.

  3. #16
    Join Date
    Jan 2010
    Posts
    6,829
    Quote Originally Posted by trai View Post
    what the brand of that pinch off tool.
    Imperial tools makes one.

  4. #17
    Join Date
    Jan 2010
    Posts
    6,829
    For what it's worth I personally would not use a pinch off tool on a thru type line. On a process tube or to remove a pressure switch is one thing. Pinching a line then re rounding it is h*ll on the tube wall. That's my

  5. #18
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,217
    Quote Originally Posted by VTP99 View Post
    For what it's worth I personally would not use a pinch off tool on a thru type line. On a process tube or to remove a pressure switch is one thing. Pinching a line then re rounding it is h*ll on the tube wall. That's my
    I agree.

  6. #19
    Join Date
    Jun 2010
    Location
    Jacksonville, Florida
    Posts
    54
    Quote Originally Posted by timjimbob View Post
    myott- get a pinchoff tool or two. You can stop the refrigerant in copper tube like it was a valve and open it later.

    Great for adding a LL filter without having to pump down system, or if your service valve is broke.
    If you do crimp off area to add a liquid line dryer how do then evacuate the area between the crimped area? Adding a shrader valve?


    Sent from my iPad using Tapatalk HD
    Solutions Heating and Air, Inc. Jacksonville, Florida "Solutions for All Your HVAC Needs"

  7. #20
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,335
    Quote Originally Posted by myott View Post
    If you do crimp off area to add a liquid line dryer how do then evacuate the area between the crimped area? Adding a shrader valve?


    Sent from my iPad using Tapatalk HD
    just use the low side valve port

    you will have low side valve closed off , so the shrader will still be available to you on the evap side

  8. #21
    Join Date
    Oct 2002
    Posts
    1,394
    you could add a 1/4" tap. Use two pinch offs, cut out old filter and reinstall filter w/ shrader and pull a 5 minute vacuum. reform tube.

    I'm not a fan of pulling vacuum through a TXV.

  9. #22
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,335
    Now that I think about it , if you did the pinch off way , your better off adding a shrader near the bad valve , otherwise you wont be able to flow nitro while brazing. Now you can pull a vac from both sides as well.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event