    Went out today to do a simple coil-pull-and -clean and low and behold a huge problem. Went to do a pump down and shut the liquid line service valve and guess what? It would not shut down. I took and pressed down on it to get the threads started but that did not work. Duhhhhhhhh......

    Had to explain to the customer that I now need to replace service valve as well as the coil clean. Lucky he understood and I grabbed the recover tank and recovery machine to reclaim the R22. Cut coil out and cleaned with my coil gun, man I love that thing.

    Reinstalled coil and added new heat pump dryer while at it. Cut service valve out and installed new one. Charged to proper superheat using my Amp-probe to take WB readings and plugged in the super heat reading to SMAN3 to dial it in.

    I am thinking the installer must have cooked the valve and when he opened the valve on start up , front seated to valve to much. What do you guys think?

    Sent from my iPad using Tapatalk HD
    Solutions Heating and Air, Inc. Jacksonville, Florida "Solutions for All Your HVAC Needs"

  2. #2
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Sounds practical.

  3. #3
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Quote Originally Posted by myott View Post
    Cut coil out and cleaned with my coil gun, man I love that thing.

    Do you always remove the coil to clean ?

    I am thinking the installer must have cooked the valve and when he opened the valve on start up , front seated to valve to much. What do you guys think?

    Sent from my iPad using Tapatalk HD
    Did you mean to say back seated the valve to much ?

  4. #4
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    If Lennox, these are one shot valves and will not close.

  5. #5
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    Quote Originally Posted by timjimbob View Post
    If Lennox, these are one shot valves and will not close.
    when they did use them it was only on the suction line, they have not been used in quite a few years though.

  6. #6
    Join Date
    Jun 2010
    Location
    Jacksonville, Florida
    Posts
    58
    Post Likes
    Thread Starter
    Yes, back seated valve.

  7. #7
    Join Date
    Jun 2010
    Location
    Jacksonville, Florida
    Posts
    58
    Post Likes
    Thread Starter
    Quote Originally Posted by timjimbob View Post
    If Lennox, these are one shot valves and will not close.
    It was a Carrier

  8. #8
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    myott- get a pinchoff tool or two. You can stop the refrigerant in copper tube like it was a valve and open it later.

    Great for adding a LL filter without having to pump down system, or if your service valve is broke.

  9. #9
    Join Date
    Oct 2007
    Location
    Broward County, FL.
    Posts
    675
    Post Likes
    Quote Originally Posted by timjimbob View Post
    myott- get a pinchoff tool or two. You can stop the refrigerant in copper tube like it was a valve and open it later.

    Great for adding a LL filter without having to pump down system, or if your service valve is broke.
    Never thought of this. Do you open the tubing using a flaring block?
    I miss you mom and dad.

  10. #10
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Same tool .does both

  11. #11
    Join Date
    Oct 2007
    Location
    Broward County, FL.
    Posts
    675
    Post Likes
    Thanks, that will come in handy.
    I miss you mom and dad.

  12. #12
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,257
    Post Likes
    **** happens and valves fail to hold all the time, no need to automatically blame the installer or a person.. That effing valve was probably made in China anyway.

  13. #13
    Join Date
    Jan 2013
    Posts
    1,179
    Post Likes
    Valves aren't what they used to be. I heat sink the valves with extra rags...makes brazing a little tougher, but at least I don't cook any more cheap Chinese valves.

    I'd hate to be the guy using a Turbo Torch these day...you have to use them full open and you can't adjust the flame size. Makes for any easy overheat situation.

    I know few guys who can use a Turbo with out over heating line set and valves.

  14. #14
    Join Date
    Jan 2013
    Posts
    1,179
    Post Likes
    Valves aren't what they used to be. I heat sink the valves with extra rags...makes brazing a little tougher, but at least I don't cook any more cheap Chinese valves.

    I'd hate to be the guy using a Turbo Torch these day...you have to use them full open and you can't adjust the flame size. Makes for any easy overheat situation.

    I know few guys who can use a Turbo with out over heating line set and valves.

  15. #15
    Join Date
    Dec 2011
    Location
    ms
    Posts
    124
    Post Likes
    what the brand of that pinch off tool.

  16. #16
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Quote Originally Posted by trai View Post
    what the brand of that pinch off tool.
    Imperial tools makes one.

  17. #17
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    For what it's worth I personally would not use a pinch off tool on a thru type line. On a process tube or to remove a pressure switch is one thing. Pinching a line then re rounding it is h*ll on the tube wall. That's my

  18. #18
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,424
    Post Likes
    Quote Originally Posted by VTP99 View Post
    For what it's worth I personally would not use a pinch off tool on a thru type line. On a process tube or to remove a pressure switch is one thing. Pinching a line then re rounding it is h*ll on the tube wall. That's my
    I agree.

  19. #19
    Join Date
    Jun 2010
    Location
    Jacksonville, Florida
    Posts
    58
    Post Likes
    Thread Starter
    Quote Originally Posted by timjimbob View Post
    myott- get a pinchoff tool or two. You can stop the refrigerant in copper tube like it was a valve and open it later.

    Great for adding a LL filter without having to pump down system, or if your service valve is broke.
    If you do crimp off area to add a liquid line dryer how do then evacuate the area between the crimped area? Adding a shrader valve?


    Sent from my iPad using Tapatalk HD
    Solutions Heating and Air, Inc. Jacksonville, Florida "Solutions for All Your HVAC Needs"

  20. #20
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by myott View Post
    If you do crimp off area to add a liquid line dryer how do then evacuate the area between the crimped area? Adding a shrader valve?


    Sent from my iPad using Tapatalk HD
    just use the low side valve port

    you will have low side valve closed off , so the shrader will still be available to you on the evap side

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •