Went out today to do a simple coil-pull-and -clean and low and behold a huge problem. Went to do a pump down and shut the liquid line service valve and guess what? It would not shut down. I took and pressed down on it to get the threads started but that did not work. Duhhhhhhhh......
Had to explain to the customer that I now need to replace service valve as well as the coil clean. Lucky he understood and I grabbed the recover tank and recovery machine to reclaim the R22. Cut coil out and cleaned with my coil gun, man I love that thing.
Reinstalled coil and added new heat pump dryer while at it. Cut service valve out and installed new one. Charged to proper superheat using my Amp-probe to take WB readings and plugged in the super heat reading to SMAN3 to dial it in.
I am thinking the installer must have cooked the valve and when he opened the valve on start up , front seated to valve to much. What do you guys think?
Sent from my iPad using Tapatalk HD
Solutions Heating and Air, Inc. Jacksonville, Florida "Solutions for All Your HVAC Needs"
Sounds practical.
If Lennox, these are one shot valves and will not close.
Yes, back seated valve.
myott- get a pinchoff tool or two. You can stop the refrigerant in copper tube like it was a valve and open it later.
Great for adding a LL filter without having to pump down system, or if your service valve is broke.
Same tool .does both
Thanks, that will come in handy.
I miss you mom and dad.
**** happens and valves fail to hold all the time, no need to automatically blame the installer or a person.. That effing valve was probably made in China anyway.
Valves aren't what they used to be. I heat sink the valves with extra rags...makes brazing a little tougher, but at least I don't cook any more cheap Chinese valves.
I'd hate to be the guy using a Turbo Torch these day...you have to use them full open and you can't adjust the flame size. Makes for any easy overheat situation.
I know few guys who can use a Turbo with out over heating line set and valves.
Valves aren't what they used to be. I heat sink the valves with extra rags...makes brazing a little tougher, but at least I don't cook any more cheap Chinese valves.
I'd hate to be the guy using a Turbo Torch these day...you have to use them full open and you can't adjust the flame size. Makes for any easy overheat situation.
I know few guys who can use a Turbo with out over heating line set and valves.
what the brand of that pinch off tool.
For what it's worth I personally would not use a pinch off tool on a thru type line. On a process tube or to remove a pressure switch is one thing. Pinching a line then re rounding it is h*ll on the tube wall. That's my