Results 1 to 13 of 22
Thread: Bad liquid service valve
Threaded View
-
01-14-2013, 09:31 PM #1
Bad liquid service valve
Went out today to do a simple coil-pull-and -clean and low and behold a huge problem. Went to do a pump down and shut the liquid line service valve and guess what? It would not shut down. I took and pressed down on it to get the threads started but that did not work. Duhhhhhhhh......
Had to explain to the customer that I now need to replace service valve as well as the coil clean. Lucky he understood and I grabbed the recover tank and recovery machine to reclaim the R22. Cut coil out and cleaned with my coil gun, man I love that thing.
Reinstalled coil and added new heat pump dryer while at it. Cut service valve out and installed new one. Charged to proper superheat using my Amp-probe to take WB readings and plugged in the super heat reading to SMAN3 to dial it in.
I am thinking the installer must have cooked the valve and when he opened the valve on start up , front seated to valve to much. What do you guys think?
Sent from my iPad using Tapatalk HDSolutions Heating and Air, Inc. Jacksonville, Florida "Solutions for All Your HVAC Needs"


Reply With Quote