    Has anybody found anything that can beat an H-10?

    First of all....Long time no see. I wonder if I still know people on here or if they know me. Man I've been busy. Kinda glad for a rainy day. OK, so here we go.....I have an H-10G and was looking to get an H-10PM. Has anybody found anything that compares to these - as far as I'm concerned- best leak detectors money can buy? JB Prowler is the biggest piece of junk I ever got talked into buying. I've never heard anything negative about an H-10, but I've heard plenty of negative about alot of others. What does everbody think? Money is not an issue. I'd rather pay more and save time. Time adds up to alot of money!

  2. #2
    Join Date
    Mar 2011
    Location
    Birmingham, AL
    Posts
    33
    I still use an H-10G myself. It is the only detector that I trust.
    I also have a 'Inficon Compass', but I get false positives with it on a regular basis.
    Another guy at work has a 'CPS LS790B', and he gets false positives every now and then as well.
    If the battery life is pretty long on the H-10PM, then I would think it would be a great tool.

  3. #3
    Join Date
    Dec 2012
    Location
    New Hampshire
    Posts
    4
    We have had the best feedback from our customers with the Inficon Dtect Select and the H-10PM when money isn't a limiting factor.

  4. #4
    Join Date
    Jan 2008
    Location
    LEHIGH VALLEY, PA
    Posts
    165
    i am using a dtect select , sometimes good but not always able to find a leak , i am would like to add a h10, as i only hear good stuff about them , except for power , there is a battery model, complaints about battery life ?, and a 115 v model , must me limiting on cord length roof tops etc , does the 115v model not have battery as well, are there real issues with power supply for these detectors ,

  5. #5
    Join Date
    May 2007
    Location
    Alabama
    Posts
    909
    I've only used the 115 ac model. Sometimes a pita to drag out cord. That's why I'm considering the H10PM. Can anybody chime in on battery life? Can you get adapters to charge in truck? Adapters to run on ac when battery is dead?

  6. #6
    Join Date
    Oct 2012
    Location
    United Arab Emirates
    Posts
    18
    Quote Originally Posted by BamaCool View Post
    First of all....Long time no see. I wonder if I still know people on here or if they know me. Man I've been busy. Kinda glad for a rainy day. OK, so here we go.....I have an H-10G and was looking to get an H-10PM. Has anybody found anything that compares to these - as far as I'm concerned- best leak detectors money can buy? JB Prowler is the biggest piece of junk I ever got talked into buying. I've never heard anything negative about an H-10, but I've heard plenty of negative about alot of others. What does everbody think? Money is not an issue. I'd rather pay more and save time. Time adds up to alot of money!
    To be honest I was really interested into buying the JB prowler as I guess it is the newest on the market. Problem is that I searched a lot for reviews and feedback in this forum but not much talks about it. I thought maybe it is still new so lets give it a try and really found a great deal for it on ebay. barely used in excellent condition JB prowler for $50!! I couldn't resist and won the bid for that price and waited tell it was delivered to me. Tested it out and was impressed with the performance. It senses difference in concentration like the other IR leak detectors do, but it senses everything!!

    I testes it on lighter and touched the tip and it went off, tested on butane in cooker for only small amount and went off. Tested on beer, rubbing alcohol and many different gases and it goes off easily. It is accurate I do not doubt it as my final test was on a 2 years old empty fully opened r134a tank which all leak detectors I own (tifzx, h10pm, accuprobe, d-tek select, srl2) just stayed silent when shaking the tank and sensing the port. Only prowler went crazy and showed a small amount of refrigerant reading .

  7. #7
    Join Date
    May 2007
    Location
    Alabama
    Posts
    909
    I went through 3 prowlers. None of them would pick up ANYTHING. I found a leak that I could HEAR. Found it with bubbles and then put the prowler right on the leak. Took over 2 minutes before it went to 1 bar for less than a second. Then silence. I moved it into fresh air and tried again. Never made another sound. Meanwhile, my H10 is 5 feet away screaming like hell. You must have got one on the other end of the spectrum - It goes off for anything!

  8. #8
    Join Date
    Oct 2012
    Location
    United Arab Emirates
    Posts
    18
    Quote Originally Posted by BamaCool View Post
    I went through 3 prowlers. None of them would pick up ANYTHING. I found a leak that I could HEAR. Found it with bubbles and then put the prowler right on the leak. Took over 2 minutes before it went to 1 bar for less than a second. Then silence. I moved it into fresh air and tried again. Never made another sound. Meanwhile, my H10 is 5 feet away screaming like hell. You must have got one on the other end of the spectrum - It goes off for anything!
    I do believe from what I read in this forum that concentration leak detection method can be a pain when finding large leaks as it seems it gets zero automatically without noticing or it just goes really crazy for such high concentration and doesn't even alarm. Someone was mentioning D-tek select and how it missed two large leaks that H10 could sense meters away and same apply to srl2 and prowler. I guess it all depends on the environment and leak size and from my experience I like heated sensors like H10pm and tifzx more because they actually sniff only refrigerant and not any kind of gases such as the prowler. I seem happy with prowler after few home testing but I am sure it would disappoint me when I search in polluted areas or windy days.

    I tried to customize my H10PM to use a 12v lithium battery pack instead of the old battery inside that doesn't hold a charge, and also bought a large 12v AGM battery which I curry in my bag and directly connect it to the H10PM. It can stay working for hours continuously and I would not worry about power anymore . Really great detector and I own 3 units for my shop

  9. #9
    Join Date
    Oct 2012
    Location
    United Arab Emirates
    Posts
    18
    Quote Originally Posted by BamaCool View Post
    I've only used the 115 ac model. Sometimes a pita to drag out cord. That's why I'm considering the H10PM. Can anybody chime in on battery life? Can you get adapters to charge in truck? Adapters to run on ac when battery is dead?
    I forgot to answer about the H10PM battery. The device need a bit high voltage to operate well so when the voltage across battery goes down a bit the low batt LED will come on and then the device won't function well. I would say 30+min continues use and then need to recharge a bit. If you want to use a DC adapter pick a 12v with 2A current rating and that is more than sufficient. You can buy it off ebay or any electronic shop. If you have a PC hard disk which works on DC adapter then it work well as I am using a hard disk DC adapter currently, same 12v 2A current. The DC adapter from bacharach part list is around 13.6v i guess with 1.7A current, I don't have that and just use 12v 2A and works flawlessly.

  10. #10
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    21,577
    H-10 PM works for me... battery is one of those sealed lead-acid batteries. I generally buy one every season at this local supply house that sells only batteries (specialty place). Costs around $25/ea... other places may be different.

    The issue with the H-10 is... it does not sniff 410 very well for me. Works GREAT for any other refrigerant... however one has to concentrate (careful procedures) to use it effectively for 410. Still... it is my favourite (and only) leak detector.

    Keep the battery charged. The sealed battery type does better the less it is discharged. My unit can run from the charger... so long timed use I will plug it in if I can.
    GA-HVAC-Tech

    Quality work at a fair price with excellent customer service!

    Romans Ch's 5-6-7-8

    2 Chronicles 7:14

  11. #11
    Join Date
    May 2007
    Location
    Alabama
    Posts
    909
    Quote Originally Posted by ga-hvac-tech View Post
    H-10 PM works for me... battery is one of those sealed lead-acid batteries. I generally buy one every season at this local supply house that sells only batteries (specialty place). Costs around $25/ea... other places may be different.

    The issue with the H-10 is... it does not sniff 410 very well for me. Works GREAT for any other refrigerant... however one has to concentrate (careful procedures) to use it effectively for 410. Still... it is my favourite (and only) leak detector.

    Keep the battery charged. The sealed battery type does better the less it is discharged. My unit can run from the charger... so long timed use I will plug it in if I can.
    Hey GA, I do remember you from some time back! Thanks for the info. I see you're still using the H10 for 410 - since you said it is the only one you have. I've never had any problem picking up 410 with mine. Maybe not as sensitive as with 22, but still effective. Have you tried anything else for 410? I have and still can't beat the H10. The only other option to me was a D-Tek, but I've heard alot of no responses from them too that the H10 would pick up.

  12. #12
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    21,577
    Quote Originally Posted by BamaCool View Post
    Hey GA, I do remember you from some time back! Thanks for the info. I see you're still using the H10 for 410 - since you said it is the only one you have. I've never had any problem picking up 410 with mine. Maybe not as sensitive as with 22, but still effective. Have you tried anything else for 410? I have and still can't beat the H10. The only other option to me was a D-Tek, but I've heard alot of no responses from them too that the H10 would pick up.
    Yeah... I have been around since 2005... spend WAAAAY too much time in ARP...

    Where you been? Busy... or vacation from the mess?

    I dropped my faithful H-10 I had for almost a decade... the circuit board cracked. Bought a new one last year and bought a used 120V unit (smaller pack case) also.

    Since I only do resi... chasing a leak is usually about a 10 min effort.

    IMO the key to taking care of the H-10PM battery is to keep it charged. Do not let it run down... charge it regularly whether you used it or not. I used to be more careful with mine... then I got lazy and let it go all fall/winter w/out charging... usually messed the battery up pretty bad. Now I just get a new batt every spring. Might fiddle with patching in a LI power tool batt sometime... just to see if it will work. Would be cool to have a socket in the tray and plug in a large version of an M-12...

    Congrats on taking the BCA championship from NotreDame... good game!
    GA-HVAC-Tech

    Quality work at a fair price with excellent customer service!

    Romans Ch's 5-6-7-8

    2 Chronicles 7:14

  13. #13
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,870
    H10PM is my 'weapon' of choice in leak detection.

    I've still got a corded model, but I don't often have to use it.

    The Dtek Select is pure crap, IMO. I've done side-by-side tests with most common refrigerants in use in refrigeration duty and the D-tek can't hold a candle to the H-10.


    I've heard good things about the Tif ZX-1 (I think that's the one, don't hold me to it), but have no personal experience with it so am reluctant to give it an endorsement.

Page 1 of 4 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event