    Quote Originally Posted by Warlockamized2 View Post
    Only the heat pump will be using it.

    Should I cut the heat-pump off at or near the outside temp that it has to have help from the furnace ?
    YES. mid 20's

    Thermal Balance Point is in the range of 24'F to 28'F
    given the parameters that I have used (attacment)

    Economic balance point is nearly {essentially } the same.

    Demand Defrost operation should be checked.
    Attached Images Attached Images
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities