    Pressure Reducing Station Information.

    To Whom It May Concern:
    With regard to a Pressure reducing station 100# to 30# to 5#. The 5# end stage of reducer that goes downline to HX Control Valve. Can that end Prs fluctuate a little under 5# to a little over 6#. Is that just a demand +/-1# differential for load varying? We have a watts regulator. Should This 5# be on the money?

    Bob C.

  2. #2
    Join Date
    Sep 2004
    Location
    crossville
    Posts
    613
    Post Likes
    i am guessing your reffering to a gas( vaporous) system. or are you asking about a different fluid?

    flucation will be more about the demand load. especialy if its a load close to the regulators max flow. regulators are rated for minimum and max load size. generally one should size regulator size so that minimum load is higher than 25% of regulator rated , and max load is 7/8 of max rated, this cuts down on hunting of regulator,

    and the flucation is the regulator working. and load of demand.
    If you cant cool it
    HEAT THE Hello out of it