Results 1 to 7 of 7
  1. #1
    Join Date
    May 2003
    Location
    Connecticut
    Posts
    561
    Post Likes

    Alerton AX Driver

    Is there an alerton AX Driver? if so, has anyone tried it?

  2. #2
    Join Date
    Mar 2008
    Location
    Council Bluffs, Iowa
    Posts
    128
    Post Likes
    There is not one that i am aware of. You still need to program the controllers using the Ebt Platform and then add the controllers as a dynamic device on the Ax Platform.

  3. #3
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    1,099
    Post Likes
    There has been talk about an IBEX driver for a couple of years now, but I have not seen one. Is this an older IBEX site or a newer BacTalk site?

  4. #4
    Join Date
    May 2003
    Location
    Connecticut
    Posts
    561
    Post Likes
    Thread Starter
    Quote Originally Posted by CB_Matt View Post
    There is not one that i am aware of. You still need to program the controllers using the Ebt Platform and then add the controllers as a dynamic device on the Ax Platform.
    I have a few sites that are alerton and they want me to put an jace on it as a front end. Backtalk is bacnet right? I am not sure yet wether these are ibex or bactalk.

  5. #5
    Join Date
    May 2011
    Location
    North Carolina
    Posts
    332
    Post Likes
    I have a FX JACE on a couple Alerton Bacnet controls and it works just fine. It discovered the controllers and points. You will need to know the BV and AV as they pull as just that AV and BV.

  6. #6
    Join Date
    Mar 2008
    Location
    Council Bluffs, Iowa
    Posts
    128
    Post Likes
    If they are Bactalk controllers then they are Bacnet and will pull right into the Jace, if you have the Bacnet MS/TP Driver. When you discover the points, you will notice that they pull in as the AV or BV as SysControl stated, Unless someone has done their job and added descriptions to the points. They probably did not.

    If this project is Ibex controllers, but has a BCM_Eth, and BCM_Tux added, you can also pull these into the Jace via BacnetIP.

    I can probably help you with the points list if you need assistance. Most use the Alerton files for common units and the points are all the same. Let me know if i can be of assistance.

  7. #7
    Join Date
    May 2003
    Location
    Connecticut
    Posts
    561
    Post Likes
    Thread Starter
    Thank you for the offer. I am not sure if they are bactalk yet. I will have to investigate further.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.