    Quote Originally Posted by motoguy128 View Post
    You said the contractor didn't install the combustion air inlet pipe. How long of a temporary pipe did he leave installed? Usually you need to have a minimum of 12" plus 1 elbow. Could be that the furance blew cold air because on the first attempt to light, it faulted out. The lockout sometimes requires the blower to run for 5 minutes before it will retry up to 3 times total.

    50% might be a stretch. Maybe a 1920's gravity furnace... but a late 1970's unit, Probably more like 70%. The standing pilots hurt AFUE a lot. Heat output won't be a lot different, but it does sound like the airflow could be set fairly high.
    I have seen late 70's to even present units well under rated efficiency.
    NCI class I took taught to use combustion as well as TESP to determine system efficiency(s).
    Actual name of test procedure is slipping my mind as of now, but I'm sure someone can chime in to back me up on this!


    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  2. #22
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Just seems like that at 50% effciency, you're looking at something like 350F flue temps. Is that normal. I natural draft gas water heaters run that hot.

  3. #23
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Quote Originally Posted by kamersoutdoor View Post
    First-off, let the installers finish their job!
    Nobody here has a clue as to your current situation being that the install is incomplete! If problems persist after installation is complete, then pictures may/can be helpful!


    sent from my Samsung Galaxy Note
    Be that as it may why are they using a furnace that is not fully installed???? WARNING this can be fatal.

  4. #24
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    3,275
    Post Likes
    Quote Originally Posted by toocoolforschool View Post
    Be that as it may why are they using a furnace that is not fully installed???? WARNING this can be fatal.
    Sorry, that is what I meant! I should have emphasized on that further when stating "Let installers complete"

    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  5. #25
    Join Date
    Jan 2013
    Posts
    51
    Post Likes
    Thread Starter

    Exclamation Had to Reboot/Reset a New Rheen RGPS..... WHY was this necessary ?

    We just had a brand new Rheem RGPS installed a few weeks ago. Overall it's been working good. That was until a few days ago.

    The inducer fan would come on, burners fire and then everything would immediately shut down. These "misfire" cycles were intermitten and sporadic. They became more frequent and to the point that the furnace would not kick on at all.

    Of course it's the weekend and hard to get hold of our installer.

    Finally did so and he said we needed to "RESET" the furnace. I'm at work (of course) so he had to come out to the house and do it himself.

    My question is "WHY would a brand new furnace NEED to be reset in the first place ??

    TIA

  6. #26
    Join Date
    Jan 2013
    Posts
    51
    Post Likes
    Thread Starter
    Quote Originally Posted by wahoo View Post
    Pulling return from the crawlspace? I'm assuming they'll correct that pronto as that's a big no-no.
    Yup. I know.

    They did come back and finish hooking up the intake vent pipes as they said they would.

    There is a separate issue now where we had to call them today. He came out and said he had to "RESET" the furnace. Whatever that means. ??
    Last edited by beenthere; 01-27-2013 at 06:48 AM. Reason: removed link to second thread

  7. #27
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I merged the threads, since it makes it easier for people to understand all the possible problems.

  8. #28
    Join Date
    Jan 2013
    Posts
    51
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    I merged the threads, since it makes it easier for people to understand all the possible problems.
    ok....Only thing is the original posting "short cycling" has been fixed and this new issue is not related that.

  9. #29
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    It shouldn't have to be reset, if it happens again I would dig a little deeper if not it could've been a fluke (power surge, power flicker etc)

  10. #30
    Join Date
    Jan 2013
    Posts
    51
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    It shouldn't have to be reset, if it happens again I would dig a little deeper if not it could've been a fluke (power surge, power flicker etc)
    Ok, Service Tech came out this AM, said it sounds like the flu pressure switch is tripping. There wasn't any codes stored since we were instructed to reset the furnace by turning the circuit breaker on/off/on.

    When he went down to check it out, the furnace turned ON without him even touching anything. I was standing right behind him and could verify this. We were both like "WTHeck" ? He powered off the furnace (safety switch installed outside the cabinet), took off the top front cover. He said the switch (looked like a hockey puck) mounting plate was bent a bit and could have been rubbing against the cabinet. That's the only thing he could see as a possibility.

    He showed me the troubleshooting lights and to call him with the codes if anything should happen.

    The house was 57 degrees and T-Stat set at 70 degrees..... Furnace ran fine until it hit 66 degrees and shut OFF. Normally, it would go to 70 degrees and shut off.

    I went down below to see if there were any Codes to read. There were NO lights what-so-ever. A few minutes passed and the furnace kicked back ON. It was OFF for around (20) minutes or so.

    Any idea WHY the furnace would now shut off 4 degrees BEFORE the setting when it did NOT before hand ?

    BTW, I believe I forgot to mention about that the Tech did replace the T-Stat last week with a digital type. Model Pro 1 IAQ T701 1 Stage.

  11. #31
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    It's tripping either a high temp limit from long run times with inadequate duct, low fan speed, dirty filter, or some type of air flow restriction or the vent pipe is too small or too long or without the correct pitch. Could be done other things but this gives you an idea.

  12. #32
    Join Date
    Jan 2013
    Posts
    51
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    It's tripping either a high temp limit from long run times with inadequate duct, low fan speed, dirty filter, or some type of air flow restriction or the vent pipe is too small or too long or without the correct pitch. Could be done other things but this gives you an idea.
    ok.... I'll post pics of the furnace/install a bit later today.

    The chimney is clear for sure (cleaned it out last year) so I now that is not the issue. The vent pipe off the furnace is the same diameter as the initial connection point (furnace), it does bend up a few feet and is spliced into the larger diameter flu pipe that goes to the chimney.

    Furnace still running since my last posting (14 minutes ago)..... 68 degrees in here.....T-Stat at 70...

  13. #33
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    What size is the return ducting (side of airflow where the filter is located)?

  14. #34
    Join Date
    Jan 2013
    Posts
    51
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    What size is the return ducting (side of airflow where the filter is located)?
    2- (12") flexible duct work.

  15. #35
    Join Date
    May 2000
    Location
    anywhere my RV is
    Posts
    18,754
    Post Likes
    possible reverse polarity on the 120v incoming power???

    Has the Tech tried jumping out the thermostat???

    which furnace is this, the rheem? what other thread was merged here??? Does it involve a different furnace?
    Why am I the only naked person at this gender reveal party

  16. #36
    Join Date
    Jan 2013
    Posts
    51
    Post Likes
    Thread Starter
    Quote Originally Posted by jmac00 View Post
    possible reverse polarity on the 120v incoming power???

    Has the Tech tried jumping out the thermostat???
    I don't think so.

    Quote Originally Posted by jmac00 View Post
    which furnace is this, the rheem? what other thread was merged here??? Does it involve a different furnace?
    Yes, same Rheem furnace.

    The Moderator merged these threads. I'm not sure why, the issues aren't related.... it is the same furnace though. ??

  17. #37
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    What's the complete model # of the furnace? Need to know size to see if duct is too small. 2-12" metal pipes with straight runs will provide approximately 1200cfm which is enough for a 3 ton ac or ~70kbtu gas furnace. How big are the return air grilles? They will add restriction if too small, of its flexible duct they cause restriction as well.

  18. #38
    Join Date
    May 2000
    Location
    anywhere my RV is
    Posts
    18,754
    Post Likes
    is this in an attic?
    Why am I the only naked person at this gender reveal party

  19. #39
    Join Date
    May 2000
    Location
    anywhere my RV is
    Posts
    18,754
    Post Likes
    Quote Originally Posted by jtrammel View Post
    What's the complete model # of the furnace? Need to know size to see if duct is too small. 2-12" metal pipes with straight runs will provide approximately 1200cfm which is enough for a 3 ton ac or ~70kbtu gas furnace. How big are the return air grilles? They will add restriction if too small, of its flexible duct they cause restriction as well.
    ya, I would like to see a whole bunch more info on this thing

    ∆T

    Manometer reading for Vent motor/pressure switch

    gas pressure

    vent tube size and length

    is the duct work sealed? length, tonnage/blower speed
    Why am I the only naked person at this gender reveal party

  20. #40
    Join Date
    Jan 2013
    Posts
    51
    Post Likes
    Thread Starter
    Quote Originally Posted by jmac00 View Post
    is this in an attic?
    No, it's in a crawl space under the house. The house is 101 years old.

    Here's a video I just took.

    http://www.youtube.com/watch?v=baxBd...ature=youtu.be

    I believe the model is a RGPS. Gas, updraft. I need to find the papers on it...

    As for the registers.... there are 5 downstairs and 4 upstairs. The are all approximately
    (did not measure).... 4" x 10" each. One downstairs is kept closed since it's only 4 feet from the T-Stat. The house is pretty small Sq Ft about 1100 or so.

    I just remembered..... Here are some pics of the old furnace when we bought the house 17 years ago. I cleaned up a lot of that mess since. You're gonna love how the previous owner had the AC condensation drain set up!!

    http://katmanduonline.net/pics/ACFURNACEPics/index.html

    To give a better idea of the size house, here's pics of it.

    http://katmanduonline.net/pics/NewHousePaint2006/

Page 2 of 4 FirstFirst 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •