Thread: Fluke CNX3000
-
01-12-2013, 04:14 PM #1
Professional Member*
- Join Date
- May 2007
- Location
- Central NJ Area
- Posts
- 628
Fluke CNX3000
I believe that this meter does not do microamps to check flame sensor. Is it possible to use mA or mV to check flame sensors? I really like the fact it possible to have all those modules to check voltage, amps and other readings to be displayed on the multimeter.
-
01-12-2013, 04:53 PM #2
I'm afraid not. It only goes down to .01 milliamp.
It would have to show .0001 milliamp to show the tenths of a microamp needed to measure flame rectification.
That's one thing about Fluke, they always leave something out, can't seem to make a true all in one meter. Looks like a nice system otherwise.
-
01-12-2013, 08:00 PM #3
-
01-19-2013, 12:20 AM #4
New Guest
- Join Date
- Jan 2013
- Posts
- 1
Or you could use your AUA2 with a iDVM lte to wirelessly measure and log micro amps from a distance.
-
01-19-2013, 09:12 AM #5
Honestly I'd like to see the difference between the two systems.
When I see the reading in the video jumping around I'm not sure if its a issue with meter accuracy, accessory head accuracy or a combination of both. Since both units record to a graph what does all that bouncing around look like?
From what I've seen so far I'd have to say the Fluke system looks like a lot more bang for the buck.If You Can Dodge A Wrench You Can Dodge A Ball