Thread: Practical question regarding ductwork

  1. #1
    Join Date
    Jan 2013
    Posts
    69
    Post Likes

    Practical question regarding ductwork

    So, I decided to install powerful inline fan in my attic capable of moving close to 3000 CFM and do air exchange every 4-6 minutes. This will be my whole house fan solution for the 2-nd floor only.

    I will install main trunk and then branch off to each individual bedroom/bathroom on a second floor. I have to use silencers because fan is definitely loud (seems like close to 70 db) and in addition to fan noise I would have to address aerodynamic noise coming from moving air @ pretty decent velocity through the ductwork.

    The immediate problem is that the largest available silencer off the shelf is only 12" and my fan requires 16" so I can't install it without further restricting air flow through both inlet and exhaust side of it.
    Secondly, I am torn apart what material/pipe to use as 16" galvanized pipe in 26 gauge is definitely not cheap and in addition I would have to spend extra time and money to further insulate it to reduce aerodynamic noise from air movement.

    Therefore I was thinking about insulated flexible pipe (very cheap and easy to install) but this one has its own issues as there are a lot of spirals/ridges inside it and in order to avoid potential problems I would have to increase its diameter from 16" to 18" or even 20" to reduce air velocity.

    So, what do I do? Any suggestions from Pro's?

  2. #2
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Where does the air replacing all this exhausted air come in at?

    Is this a belt drive centrifugal fan?

  3. #3
    Join Date
    Jan 2013
    Posts
    69
    Post Likes
    Thread Starter
    The air comes from open windows and it is large inline fan, like Fantech FKD series which I believe is direct drive

  4. #4
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    silencers only reduce sound of air velocity at terminals. not the sound of the fan if you were standing next to it or standing underneath it in your bedroom.

  5. #5
    Join Date
    Jan 2013
    Posts
    69
    Post Likes
    Thread Starter
    Hmm..exactly opposite to what I was told by Fantech tech support

  6. #6
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    doubt they have ever installed one themselves
    Quote Originally Posted by ProperVenting View Post
    Hmm..exactly opposite to what I was told by Fantech tech support

  7. #7
    Join Date
    Jan 2013
    Posts
    69
    Post Likes
    Thread Starter
    So what do I do?

  8. #8
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Live with the noise, or enter the 21st century and install an hvac system.

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Large ducts, large diameter fan(s), slower blade speed.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #10
    Join Date
    Jan 2013
    Posts
    69
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    Live with the noise, or enter the 21st century and install an hvac system.
    If u refer to A/C and Heating system, I am already in 21-st century and I am installing this one in addition. And my last observation, you should be less presumptuous in your opinions.

  11. #11
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    well... 16" round flex will do what you want at a velocity of roughly 1100fpm for about 50-70 feet. they do make a blanket material you can use to reduce sound. or live with it. using flex alone will silence some of the sound of the fan at the terminals.

  12. #12
    Join Date
    Jan 2013
    Posts
    69
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    Large ducts, large diameter fan(s), slower blade speed.
    Tim, thanks for the suggestions. So forget silencers? I did mention that I am planning to oversize my ducts, what about using flex vs regular pipe? I really need to find a solution for the fan noise. If you guys are telling me that silencers will only help with aerodynamic noise and not fan noise, I am start questioning the whole installation idea.

  13. #13
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    silencers reduce the sound at the registers only.

  14. #14
    Join Date
    Jan 2013
    Posts
    69
    Post Likes
    Thread Starter
    Quote Originally Posted by chrisevansac View Post
    silencers reduce the sound at the registers only.
    Thanks, Chris..so what do I do with 70db motor noise?? That is hell of a lot of noise near bedrooms and with these levels I can wake up all my neighbors. It is friggin loud

  15. #15
    Join Date
    Oct 2012
    Location
    Torrington CT
    Posts
    130
    Post Likes
    did you start the fan with no ducts on it

  16. #16
    Join Date
    Jan 2013
    Posts
    69
    Post Likes
    Thread Starter
    Quote Originally Posted by mattt787 View Post
    did you start the fan with no ducts on it
    No, I do not have the fan yet and I am only passing the information I got from tech support. I'm talking about FKD-16 variety

  17. #17
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    70 db is no louder than the common TRANE condensing unit. Lol

  18. #18
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    Quote Originally Posted by ProperVenting View Post
    Thanks, Chris..so what do I do with 70db motor noise?? That is hell of a lot of noise near bedrooms and with these levels I can wake up all my neighbors. It is friggin loud
    Check out ATC removable insulation

  19. #19
    Join Date
    Feb 2009
    Location
    Wisconsin
    Posts
    412
    Post Likes
    You have to fight through some bad days to earn the best days of your life.
    You can learn something from EVERYONE.

  20. #20
    Join Date
    Jan 2013
    Posts
    69
    Post Likes
    Thread Starter

    Confused

    Quote Originally Posted by thermofridge View Post
    Because I do not believe in this solution as it implies that there is 1 (One!!) central location from where it is pulling all air. They are not powerful enuf and what happens when all bedrooms doors are closed. Where it will suck the air from??!!

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •