Charging R410a and R422D
Can anyone direct me to a website that shows the proper way to charge R410a, and have any of you guys converted over to the new R22? I'm hearing different ways to convert. One of the ways was to change the valve stem and just charge the normal way, but there are other ways as well.
Thanks
-
02-06-2013, 05:53 PM #2
Professional Member*
- Join Date
- Mar 2003
- Posts
- 1,215
Charge it like you would any other system using either sub-cool if a txv system or superheat if a fixed orifice...or weigh it in and check both. Beware of the new r-22 some have butane/propane properties.
-
02-06-2013, 06:15 PM #3
Professional Member*
- Join Date
- May 2011
- Location
- Ripley, WV
- Posts
- 818
Also keep in mind you're supposed to Charge blended refrigerants in liquid form (Be sure to throttle it in).