Thread: Question? Minimum burner gas pressure on a Dukane 70K 92% gas furnace

  1. #1
    Join Date
    Jun 2009
    Posts
    1
    Post Likes

    Question? Minimum burner gas pressure on a Dukane 70K 92% gas furnace

    I have a 2 year old Dukane 70,000BTU 92% gas furnace at home, it is slightly oversized, 63Deg Temp rise with 3.5" Hg gas pressure to manifold which is OK, it works great but my question is how can I de-rate this furnace a little to keep it running longer. My thought was maybe drop to say 3" HG gas pressure to manifold or lower but would that alone cause any other problems? I've been in the business long enough (but not residential) to accept if its working properly Leave it be!

  2. #2
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    The gas input rate is fairly critical for normal operation. Multi-stage furnaces are designed to compensate both the combustion airflow and indoor airflow in low fire to maintain normal heat exchanger temperatures and efficient combustion. Single stage furnaces don't have that capability.

  3. #3
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,890
    Post Likes
    You run the risk of poor combustion, lower efficiency and reduced equipment life expectancy. If you are capable of doing proper combustion analysis, fine. If not, leave well enough alone. You could work toward reducing temp rise by increasing duct efficiency.
    A good HVAC tech knows how, an educated HVAC tech knows why!

    DEM


Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •