Results 1 to 13 of 17
Thread: Oil Pressure
-
01-11-2013, 07:15 PM #1
Regular Guest
- Join Date
- Dec 2009
- Location
- Fort Worth, Texas
- Posts
- 142
Oil Pressure
Technical Systems M# 20A0CS40 460 VOLT Condenser, Dunum Bush Air Handler very old. Copeland compressor model 6DS3R40M0-TSN-800. epr, suction acculator, reciever and hot gas defrost.
I am running 40 # suction 225# head pressure. 11 sc and 15 sh. 2 unloaders. Room temp to maintain 35 degrees. I have 2 systems and both are doing same thing.
My problem is loss of oil pressure. Solenoid holds on pump down, compressor valves do not leak by. 1 Unloader unloaded all the time the other unloader loads and unloads. oil foaming slightly when fully unloaded and a lot of foaming when partial unloaded. crankcase hot.
Any suggestions. Are these comprssors use hot gas bypass can you change to suction cutoff. i am stumped. Oil pressure never gets over 15# net oil pressure then will go to 10 and 5 at various times.
Any suggestions would be appreciated.
-
01-11-2013, 07:27 PM #2
Sump screen clean?
-
01-11-2013, 08:17 PM #3
-
01-11-2013, 10:46 PM #4
How does the oil taste?
-
01-11-2013, 11:12 PM #5
Regular Guest
- Join Date
- Dec 2009
- Location
- Fort Worth, Texas
- Posts
- 142
I think it has to do with the crankcase being to hot and thinning out the oil? I need to know if these compressors use suction cut off unloading or just bypass. I got 2 systems doing the same thing and one compressor is fairly new. But it could be the screen and thats one thing i will check.
-
01-12-2013, 06:07 PM #6
-
01-19-2013, 11:16 AM #7"The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield
-
01-21-2013, 02:45 PM #8
Regular Guest
- Join Date
- Aug 2010
- Location
- Dearborn MI
- Posts
- 26
Copeland hasn't used bypass style unloading for many years. The compressor you are asking about is the new Copeland model number meaning that it can't be very old. What happened to the last failure? The screen probably is plugged, but the contaminants are from the failed connecting rods. The low oil pressure is the result of worn rods caused by oil that is extremely diluted with liquid refrigerant. You need to address the floodback problem and prevent another compressor failure.
-
01-22-2013, 08:40 AM #9
Had a TS chiller, believe it has same comp, doing same thing. Comp had been replaced, by different company, previously. Ended up finding oil log was the problem. Pulled 6 gal of oil out of it and cleared rite up.
-
01-22-2013, 11:00 AM #10
Regular Guest
- Join Date
- Aug 2010
- Location
- Dearborn MI
- Posts
- 26
I don't understand. How could a high oil level cause a low oil pressure problem? Did something else change in addition to you removing the extra oil?
-
01-22-2013, 12:47 PM #11
I know rite? What we had was oil logged cooler/evap which caused flooding which foamed the sump.
-
01-22-2013, 01:41 PM #12
Professional Member
- Join Date
- Jun 2012
- Location
- Northeast
- Posts
- 115
-
01-22-2013, 03:12 PM #13


Reply With Quote