Hi
New to the forum. So here goes
On the last ship I was on there was a problem with the walk in chiller freezer. Its running on R404a seawater cooled condensors
Problem was unit was freezing the suction line right back to the compressor.
Am i right in assuming that the problem was caused by someone charging with gas and not liquid? or is there a problem with the systems TX valves causing liquid carry over
Thanks in advance
Sam
-
12-14-2006, 08:33 PM #2
Maybe it is just like that. What was your temp and pressure, superheat?
-
12-14-2006, 09:57 PM #3
Regular Guest
- Join Date
- Dec 2006
- Location
- Brisbane Australia
- Posts
- 4
Thanks freezeking
From memory the pressure were 240 and 20 psi
Super heat not known Condensor was showing what appaered to be a good quarter of an inch of oilly looking substance on the top of the liquid level. At leat three persons wre fiddling with the unit and problem was still there when I left the vessel. Just looking for some reasons Vessel had only the pressure gauges on the compressor for diagnostics
Thanks Sam
-
12-14-2006, 10:20 PM #4
Professional Member
- Join Date
- Dec 2003
- Location
- Location!, Location!
- Posts
- 929
404a @ 20psig sat. pressure = -14°F, That'll draw frost 4 sure. What was walk in temp? Not all line frosting indicates liquid floodback. It's dependent upon many factors-ambient humidity, sat. vapor T-P relationship.
-
12-14-2006, 11:06 PM #5
Regular Guest
- Join Date
- Dec 2006
- Posts
- 40
It is common for freezers to frost the suction line back to the compressor. If the compressor itself is frosting then you have a problem. Possibly with the superheat. Adjusting the TXV to obtain proper superheat can solve this.
-
12-14-2006, 11:11 PM #6Not necessarily, it just means that part of the compressor is below freezing. Than can happen with SH well within range.If the compressor itself is frosting then you have a problem.
-
12-15-2006, 02:28 AM #7
Regular Guest
- Join Date
- Dec 2006
- Location
- Brisbane Australia
- Posts
- 4
Thanks guys for the quick responses
The walk in fridge temp was +10 Deg C and the Freezer was running -13 deg c
The compressor was starting to ice up and the head temperature was coll enough to place the hand on it
As far as I am aware noone adjusted the TX valve due to laek which was found in the freezer only Freon was added
Many thanks for the replies
Sam
-
12-15-2006, 07:04 AM #8The cool discharge line can be an indication of low superheat which will also cause the suction line icing. You would want to put a superheat thermometer on it and adjust to specs, typically around 6*F for a freezer at the evap and 20-30*F at the compressor.Originally posted by simomatra
Thanks guys for the quick responses
The walk in fridge temp was +10 Deg C and the Freezer was running -13 deg c
The compressor was starting to ice up and the head temperature was coll enough to place the hand on it
As far as I am aware noone adjusted the TX valve due to laek which was found in the freezer only Freon was added
Many thanks for the replies
Sam
-
12-15-2006, 06:11 PM #9
Regular Guest
- Join Date
- Dec 2006
- Location
- Brisbane Australia
- Posts
- 4
Thanks K_fridge
As I tend to be thrown these problems whilst away on the ships I think I will invest in some professional test gear and carry with me. Most ships tend to have little in the way of test gear for the HVAC and fridges semms a forgotten area even with all the new strict rules they don't comply too
Many thanks once again
Merry Christmass to all from down under
Sam