    Vykon JACE-200 no station

    Hi, recently I sourced a second hand Vykon JACE-200. It's pretty old, arrived with Tridium 3.0.99 shell. My experiences is really limited to JCI FX-20&60 & workbench, tried upgrading all files in the on-board flash to 3.3 through workbench as that's what the imbed license can support up to.

    However, there is no station loaded. After copying a standard JCIStation, I'm getting these errors:

    ERROR [22:32:54 21-Apr-13 EST][tz database] error loading timezones.jar manifest: null
    ERROR [22:32:54 21-Apr-13 EST][sys] Cannot boot
    java.lang.ExceptionInInitializerError
    at java.lang.J9VMInternals.initialize(J9VMInternals.j ava:167)
    at javax.baja.sys.BAbsTime.<clinit>(BAbsTime.java)
    at java.lang.J9VMInternals.initializeImpl(Native Method)
    at java.lang.J9VMInternals.initialize(J9VMInternals.j ava:161)
    at javax.baja.sys.Clock.time(Clock.java)
    at javax.baja.sys.Clock.time(Clock.java)
    at com.tridium.sys.resource.ResourceManager.this(Reso urceManager.java)
    at com.tridium.sys.resource.ResourceManager.<init>(Re sourceManager.java)
    at com.tridium.sys.Nre.boot(Nre.java)
    at com.tridium.sys.Nre.boot(Nre.java)
    at com.tridium.sys.Nre.main(Nre.java)
    Caused by: java.lang.NullPointerException
    at javax.baja.timezone.TimeZoneDatabase.isZoneIdSuppo rted(TimeZoneDatabase.java)
    at javax.baja.timezone.TimeZoneDatabase.getHistorical TimeZone(TimeZoneDatabase.java)
    at javax.baja.timezone.TimeZoneDatabase.getHistorical TimeZone(TimeZoneDatabase.java)
    at javax.baja.timezone.BTimeZone.getTimeZone(BTimeZon e.java)
    at javax.baja.timezone.BTimeZone.<clinit>(BTimeZone.j ava)
    at java.lang.J9VMInternals.initializeImpl(Native Method)
    at java.lang.J9VMInternals.initialize(J9VMInternals.j ava:161)

    Appreciated if someone could shed some light on how to resolve the issue.

    BTW: Can I create a new station? All I'm after is to use BACnet MSTP.

  2. #2
    Join Date
    Aug 2011
    Posts
    86
    Post Likes
    I would make a new station. I believe its Tools --> New Station. You may need to be in the app director

  3. #3
    Join Date
    May 2010
    Posts
    13
    Post Likes
    Thread Starter
    Thanks. I tried that, however the station directory automatically points to the workbench installation directory (e.g. c:\jci\fxserverltd-2.2\stations\) and it's greyed out hence not editable.

  4. #4
    Join Date
    Aug 2011
    Posts
    86
    Post Likes
    Are you in the platform of your computer? Make sure you are in the platform of your jace

  5. #5
    Join Date
    May 2010
    Posts
    13
    Post Likes
    Thread Starter
    I'm using workbench pro 2.2, JACE is in application director under PLATFORM.

  6. #6
    Join Date
    Aug 2011
    Posts
    86
    Post Likes
    Ok you should see the one and only station on your jace. Delete it and then go to Tools, New Station. Hope this helps.

  7. #7
    Join Date
    May 2010
    Posts
    13
    Post Likes
    Thread Starter
    Originally, there wasn't a station, just blank.

    Tools -> New station can only allow me to create a station in the host (PC)

    Quote Originally Posted by overdue View Post
    the station directory automatically points to the workbench installation directory (e.g. c:\jci\fxserverltd-2.2\stations\) and it's greyed out hence not editable.

  8. #8
    Join Date
    Jul 2009
    Location
    Charlotte, NC
    Posts
    423
    Post Likes
    You create the station locally, then sens it to the JACE.

  9. #9
    Join Date
    May 2010
    Posts
    13
    Post Likes
    Thread Starter
    Do you mean copy the station via station copier?

  10. #10
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,303
    Post Likes
    Quote Originally Posted by overdue View Post
    Do you mean copy the station via station copier?
    No, create station on your lappy, send station you created to JACE and this done via the commissioning wizard so that the needed modules may be installed as well.

  11. #11
    Join Date
    May 2010
    Posts
    13
    Post Likes
    Thread Starter
    Quote Originally Posted by Chris_Worthington View Post
    No, create station on your lappy, send station you created to JACE and this done via the commissioning wizard so that the needed modules may be installed as well.
    OK, used commissioning wizard this time, but it still gives me same error message in application director.

    During commissioning wizard, screen shots below are what went through.

    Name:  4.jpg
Views: 1337
Size:  56.5 KBName:  2.PNG
Views: 1250
Size:  21.3 KBName:  3.PNG
Views: 1277
Size:  15.4 KB

    ERROR [08:19:08 22-Apr-13 MST][tz database] error loading timezones.jar manifest: null
    ERROR [08:19:08 22-Apr-13 MST][sys] Cannot boot
    java.lang.ExceptionInInitializerError
    at java.lang.J9VMInternals.initialize(J9VMInternals.j ava:167)
    at javax.baja.sys.BAbsTime.<clinit>(BAbsTime.java)
    at java.lang.J9VMInternals.initializeImpl(Native Method)
    at java.lang.J9VMInternals.initialize(J9VMInternals.j ava:161)
    at javax.baja.sys.Clock.time(Clock.java)
    at javax.baja.sys.Clock.time(Clock.java)
    at com.tridium.sys.resource.ResourceManager.this(Reso urceManager.java)
    at com.tridium.sys.resource.ResourceManager.<init>(Re sourceManager.java)
    at com.tridium.sys.Nre.boot(Nre.java)
    at com.tridium.sys.Nre.boot(Nre.java)
    at com.tridium.sys.Nre.main(Nre.java)
    Caused by: java.lang.NullPointerException
    at javax.baja.timezone.TimeZoneDatabase.isZoneIdSuppo rted(TimeZoneDatabase.java)
    at javax.baja.timezone.TimeZoneDatabase.getHistorical TimeZone(TimeZoneDatabase.java)
    at javax.baja.timezone.TimeZoneDatabase.getHistorical TimeZone(TimeZoneDatabase.java)
    at javax.baja.timezone.BTimeZone.getTimeZone(BTimeZon e.java)
    at javax.baja.timezone.BTimeZone.<clinit>(BTimeZone.j ava)
    at java.lang.J9VMInternals.initializeImpl(Native Method)
    at java.lang.J9VMInternals.initialize(J9VMInternals.j ava:161)

  12. #12
    Join Date
    Apr 2007
    Location
    San Diego, CA
    Posts
    1,535
    Post Likes
    Try this:
    Go to Platform Administration and click "Change Date/Time"
    Click "Use Local", then Save.

    Go to the File Transfer client and browse to niagara/lib on the JACE (right side), and browse to c:\jci\fxserverltd-2.2\lib on your computer (left side).

    Compare the CRC for timezones.jar and timezones.xml
    Copy from your host to the JACE, overriding the existing files.
    Last edited by digo; 04-22-2013 at 11:40 AM. Reason: typos

  13. #13
    Join Date
    May 2010
    Posts
    13
    Post Likes
    Thread Starter
    Quote Originally Posted by digo View Post
    Try this:
    Go to Platform Administration and click "Change Date/Time"
    Click "Use Local", then Save.

    Go to the File Transfer client and browse to niagara/lib on the JACE (right side), and browse to c:\jci\fxserverltd-2.2\lib on your computer (left side).

    Compare the CRC for timezones.jar and timezones.xml
    Copy from your host to the JACE, overriding the existing files.
    Thanks everyone, it worked. In fact, there wasn't even a timezone.jar in the JACE. It is at last trying to boot now.

    Unfortunately, more error messages followed, sorry to dump them all here. Does it look like JACE is lacking some files or do I need to acquire extra license to make it work?
    Name:  license.jpg
Views: 1368
Size:  38.2 KB


    MESSAGE [02:05:34 23-Apr-13 EST][sys.registry] Up-to-date [314ms]
    MESSAGE [02:05:36 23-Apr-13 EST][sys] Baja runtime booted ("/ffs0/niagara")
    MESSAGE [02:05:38 23-Apr-13 EST][sys.registry] Loaded [1678ms]
    MESSAGE [02:05:41 23-Apr-13 EST][sys] Loading "/ffs0/niagara/stations/FX20/config.bog"...
    MESSAGE [02:05:55 23-Apr-13 EST][sys] Loaded (14685ms)
    ERROR [02:06:27 23-Apr-13 EST][platform] Unable to create archive RAM disk
    ERROR [02:06:27 23-Apr-13 EST][alarm] Cannot open alarm database.
    java.io.IOException: Cannot create: /alarm/alarm.adb
    at java.io.File.createNewFile(File.java:1051)
    at com.tridium.alarm.db.file.BFileAlarmDatabase.doOpe n(BFileAlarmDatabase.java)
    at javax.baja.alarm.BAlarmDatabase.open(BAlarmDatabas e.java)
    at javax.baja.alarm.BAlarmService.initAlarmDb(BAlarmS ervice.java)
    at javax.baja.alarm.BAlarmService.serviceStarted(BAla rmService.java)
    at com.tridium.sys.service.ServiceManager.startServic e(ServiceManager.java)
    at com.tridium.sys.service.ServiceManager.startAllSer vices(ServiceManager.java)
    at com.tridium.sys.station.Station.initServices(Stati on.java)
    at com.tridium.sys.station.Station.bootStation(Statio n.java)
    at com.tridium.sys.station.Station.main(Station.java)
    at java.lang.reflect.AccessibleObject.invokeV(Accessi bleObject.java:203)
    at java.lang.reflect.Method.invoke(Method.java:253)
    at com.tridium.sys.Nre.runClass(Nre.java)
    at com.tridium.sys.Nre.main(Nre.java)
    ERROR [02:06:28 23-Apr-13 EST][service] Unlicensed: /Services/WebService
    javax.baja.license.FeatureNotLicensedException: tridium:web
    at com.tridium.sys.license.NLicenseManager.getFeature (NLicenseManager.java)
    at javax.baja.web.BWebService.getLicenseFeature(BWebS ervice.java)
    at javax.baja.sys.BAbstractService.checkLicense(BAbst ractService.java)
    at javax.baja.sys.BAbstractService.fwServiceStarted(B AbstractService.java)
    at javax.baja.sys.BAbstractService.fw(BAbstractServic e.java)
    at com.tridium.sys.service.ServiceManager.startServic e(ServiceManager.java)
    at com.tridium.sys.service.ServiceManager.startAllSer vices(ServiceManager.java)
    at com.tridium.sys.station.Station.initServices(Stati on.java)
    at com.tridium.sys.station.Station.bootStation(Statio n.java)
    at com.tridium.sys.station.Station.main(Station.java)
    at java.lang.reflect.AccessibleObject.invokeV(Accessi bleObject.java:203)
    at java.lang.reflect.Method.invoke(Method.java:253)
    at com.tridium.sys.Nre.runClass(Nre.java)
    at com.tridium.sys.Nre.main(Nre.java)
    ERROR [02:06:39 23-Apr-13 EST][platform] Unable to create archive RAM disk
    ERROR [02:06:40 23-Apr-13 EST][sys.service] Service start failed: History Service
    java.lang.NullPointerException
    at com.tridium.history.db.BLocalHistoryDatabase.listD evicesFromFile(BLocalHistoryDatabase.java)
    at com.tridium.history.db.ConfigIndex.init(ConfigInde x.java)
    at com.tridium.history.db.BLocalHistoryDatabase.doOpe n(BLocalHistoryDatabase.java)
    at javax.baja.history.db.BHistoryDatabase.open(BHisto ryDatabase.java)
    at javax.baja.history.BHistoryService.serviceStarted( BHistoryService.java)
    at com.tridium.sys.service.ServiceManager.startServic e(ServiceManager.java)
    at com.tridium.sys.service.ServiceManager.startAllSer vices(ServiceManager.java)
    at com.tridium.sys.station.Station.initServices(Stati on.java)
    at com.tridium.sys.station.Station.bootStation(Statio n.java)
    at com.tridium.sys.station.Station.main(Station.java)
    at java.lang.reflect.AccessibleObject.invokeV(Accessi bleObject.java:203)
    at java.lang.reflect.Method.invoke(Method.java:253)
    at com.tridium.sys.Nre.runClass(Nre.java)
    at com.tridium.sys.Nre.main(Nre.java)
    MESSAGE [02:06:40 23-Apr-13 EST][sys] Services Initialized (24249ms)
    MESSAGE [02:06:40 23-Apr-13 EST][sys.mixin] Updated [40ms]
    javax.baja.history.DatabaseClosedException: The requested operation is not allowed while the database is closed.
    at javax.baja.history.db.BHistoryDatabase.checkOpen(B HistoryDatabase.java)
    at com.tridium.history.db.BLocalHistoryDatabase.exist s(BLocalHistoryDatabase.java)
    at com.tridium.history.audit.BAuditHistoryService.ini tHistory(BAuditHistoryService.java)
    at com.tridium.history.audit.BAuditHistoryService.sta rtAudit(BAuditHistoryService.java)
    at com.tridium.history.audit.BAuditHistoryService.sta rted(BAuditHistoryService.java)
    at com.tridium.sys.engine.EngineUtil.started(EngineUt il.java)
    at com.tridium.sys.engine.EngineManager.start(EngineM anager.java)
    at com.tridium.sys.schema.ComponentSlotMap.start(Comp onentSlotMap.java)
    at javax.baja.sys.BComponent.start(BComponent.java)
    at com.tridium.sys.engine.EngineManager.start(EngineM anager.java)
    at com.tridium.sys.schema.ComponentSlotMap.start(Comp onentSlotMap.java)
    at javax.baja.sys.BComponent.start(BComponent.java)
    at com.tridium.sys.engine.EngineManager.start(EngineM anager.java)
    at com.tridium.sys.schema.ComponentSlotMap.start(Comp onentSlotMap.java)
    at javax.baja.sys.BComponent.start(BComponent.java)
    at com.tridium.sys.station.Station.startStation(Stati on.java)
    at com.tridium.sys.station.Station.bootStation(Statio n.java)
    at com.tridium.sys.station.Station.main(Station.java)
    at java.lang.reflect.AccessibleObject.invokeV(Accessi bleObject.java:203)
    at java.lang.reflect.Method.invoke(Method.java:253)
    at com.tridium.sys.Nre.runClass(Nre.java)
    at com.tridium.sys.Nre.main(Nre.java)
    javax.baja.history.DatabaseClosedException: The requested operation is not allowed while the database is closed.
    at javax.baja.history.db.BHistoryDatabase.checkOpen(B HistoryDatabase.java)
    at com.tridium.history.db.BLocalHistoryDatabase.exist s(BLocalHistoryDatabase.java)
    at com.tridium.history.log.BLogHistoryService.initHis tory(BLogHistoryService.java)
    at com.tridium.history.log.BLogHistoryService.startCo llecting(BLogHistoryService.java)
    at com.tridium.history.log.BLogHistoryService.started (BLogHistoryService.java)
    at com.tridium.sys.engine.EngineUtil.started(EngineUt il.java)
    at com.tridium.sys.engine.EngineManager.start(EngineM anager.java)
    at com.tridium.sys.schema.ComponentSlotMap.start(Comp onentSlotMap.java)
    at javax.baja.sys.BComponent.start(BComponent.java)
    at com.tridium.sys.engine.EngineManager.start(EngineM anager.java)
    at com.tridium.sys.schema.ComponentSlotMap.start(Comp onentSlotMap.java)
    at javax.baja.sys.BComponent.start(BComponent.java)
    at com.tridium.sys.engine.EngineManager.start(EngineM anager.java)
    at com.tridium.sys.schema.ComponentSlotMap.start(Comp onentSlotMap.java)
    at javax.baja.sys.BComponent.start(BComponent.java)
    at com.tridium.sys.station.Station.startStation(Stati on.java)
    at com.tridium.sys.station.Station.bootStation(Statio n.java)
    at com.tridium.sys.station.Station.main(Station.java)
    at java.lang.reflect.AccessibleObject.invokeV(Accessi bleObject.java:203)
    at java.lang.reflect.Method.invoke(Method.java:253)
    at com.tridium.sys.Nre.runClass(Nre.java)
    at com.tridium.sys.Nre.main(Nre.java)
    WARNING [02:06:43 23-Apr-13 EST][web] HTTP and HTTPS are both disabled.
    ERROR [02:06:43 23-Apr-13 EST][sys.engine] Failed stationStarted: Web Service
    java.lang.NullPointerException
    at com.tridium.history.log.BLogHistoryService.publish (BLogHistoryService.java)
    at javax.baja.log.Log.log(Log.java)
    at javax.baja.log.Log.warning(Log.java)
    at javax.baja.web.BWebService.stationStarted(BWebServ ice.java)
    at com.tridium.sys.engine.EngineUtil.stationStarted(E ngineUtil.java)
    at com.tridium.sys.engine.EngineManager.stationStarte d(EngineManager.java)
    at com.tridium.sys.engine.EngineManager.stationStarte d(EngineManager.java)
    at com.tridium.sys.engine.EngineManager.stationStarte d(EngineManager.java)
    at com.tridium.sys.station.Station.startStation(Stati on.java)
    at com.tridium.sys.station.Station.bootStation(Statio n.java)
    at com.tridium.sys.station.Station.main(Station.java)
    at java.lang.reflect.AccessibleObject.invokeV(Accessi bleObject.java:203)
    at java.lang.reflect.Method.invoke(Method.java:253)
    at com.tridium.sys.Nre.runClass(Nre.java)
    at com.tridium.sys.Nre.main(Nre.java)
    ERROR [02:06:43 23-Apr-13 EST][sys] Cannot boot
    java.lang.NullPointerException
    at com.tridium.history.log.BLogHistoryService.publish (BLogHistoryService.java)
    at javax.baja.log.Log.log(Log.java)
    at javax.baja.log.Log.error(Log.java)
    at com.tridium.sys.engine.EngineUtil.stationStarted(E ngineUtil.java)
    at com.tridium.sys.engine.EngineManager.stationStarte d(EngineManager.java)
    at com.tridium.sys.engine.EngineManager.stationStarte d(EngineManager.java)
    at com.tridium.sys.engine.EngineManager.stationStarte d(EngineManager.java)
    at com.tridium.sys.station.Station.startStation(Stati on.java)
    at com.tridium.sys.station.Station.bootStation(Statio n.java)
    at com.tridium.sys.station.Station.main(Station.java)
    at java.lang.reflect.AccessibleObject.invokeV(Accessi bleObject.java:203)
    at java.lang.reflect.Method.invoke(Method.java:253)
    at com.tridium.sys.Nre.runClass(Nre.java)
    at com.tridium.sys.Nre.main(Nre.java)
    ERROR [02:06:44 23-Apr-13 EST][sys] Cannot boot
    java.lang.NullPointerException
    at com.tridium.history.log.BLogHistoryService.publish (BLogHistoryService.java)
    at javax.baja.log.Log.log(Log.java)
    at javax.baja.log.Log.error(Log.java)
    at com.tridium.sys.Nre.runClass(Nre.java)
    at com.tridium.sys.Nre.main(Nre.java)
    Exception in thread "main" java.lang.NullPointerException
    at com.tridium.history.log.BLogHistoryService.publish (BLogHistoryService.java)
    at javax.baja.log.Log.log(Log.java)
    at javax.baja.log.Log.error(Log.java)
    at com.tridium.sys.Nre.main(Nre.java)
    ENGINE WATCHDOG TIMEOUT STACK DUMP @ Tue Apr 23 02:07:53 2013


    Full thread dump [10/15]
    "<unknown>" (ptid 0, condvar wait)
    "Nre:Engine" (ptid 3, runnable)
    at java/lang/Thread.sleep(JI)V
    at java/lang/Thread.sleep(J)V
    at com/tridium/sys/engine/EngineManager$EngineThread.run()V
    "Nre:Lease" (ptid 4, runnable)
    at java/lang/Thread.sleep(JI)V
    at java/lang/Thread.sleep(J)V
    at com/tridium/sys/engine/LeaseManager$LeaseThread.run()V
    "Finalizer thread" (ptid 5, condvar wait)
    "Nre:Console" (ptid 6, runnable)
    at java/lang/Thread.sleep(JI)V
    at java/lang/Thread.sleep(J)V
    at com/tridium/sys/Console.readLine()Ljava/lang/String;
    at com/tridium/sys/Console.read()[Ljava/lang/String;
    at com/tridium/sys/Console.run()V
    "Fox:FailsafeTimeout" (ptid 7, runnable)
    at java/lang/Thread.sleep(JI)V
    at java/lang/Thread.sleep(J)V
    at com/tridium/fox/session/Fox$FailsafeTimeoutThread.run()V
    "Alarm:ServiceWorker" (ptid 8, condvar wait)
    at java/lang/Object.wait(JI)V
    at java/lang/Object.wait(J)V
    at javax/baja/util/Queue.dequeue(I)Ljava/lang/Object;
    at javax/baja/util/Queue.todo(I)Ljava/lang/Runnable;
    at javax/baja/util/Worker$Processor.run()V
    at java/lang/Thread.run()V
    "CategoryService:Update" (ptid 9, runnable)
    at java/lang/Thread.sleep(JI)V
    at java/lang/Thread.sleep(J)V
    at javax/baja/category/BCategoryService$UpdateThread.run()V
    "CloseUnusedHistoriesWorker" (ptid 10, condvar wait)
    at java/lang/Object.wait(JI)V
    at java/lang/Object.wait(J)V
    at javax/baja/util/Queue.dequeue(I)Ljava/lang/Object;
    at javax/baja/util/Queue.todo(I)Ljava/lang/Runnable;
    at javax/baja/util/Worker$Processor.run()V
    at java/lang/Thread.run()V
    "Tuning:NiagaraNetwork" (ptid 11, runnable)
    at java/lang/Thread.sleep(JI)V
    at java/lang/Thread.sleep(J)V
    at javax/baja/driver/point/BTuningPolicyMap$BackgroundThread.run()V
    "Plat:EngineMonitor" (ptid 13, runnable)
    at java/lang/Thread.sleep(JI)V
    at java/lang/Thread.sleep(J)V
    at com/tridium/platform/BSystemPlatformService$EngineMonitor.run()V
    at java/lang/Thread.run()V
    event->u.monitor_dump.begin 49785018
    event->u.monitor_dump.end 4978568a





    App Failed