Thread: Bench testing flame sensors?
-
01-11-2013, 07:41 AM #1
New Guest
- Join Date
- Mar 2011
- Posts
- 5
Bench testing flame sensors?
I have a hand full of f/s . Was just wondering can they be tested out of a furnace with just a flame (torch or lighter) and meter? Kind of like testing a t-couple on a bench? If not I will just check them on the shop furnace.
Thanks
-
01-11-2013, 09:28 AM #2
I would think that if you simulate a flame rectification circuit by sending like 90 to 120 volts through the flame sensing rod and having it ground out on something similar to a burner face with flame in between and your meter hooked up, in theory that should work.
I would expect you would only get accurate results if the flame used was similar to a burner flame though; and the ground similar to 2, or a used burner.
I'm really just guessing here though
Sent from my GSIII on Tapatalk
-
01-11-2013, 11:20 AM #3“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.
-
01-11-2013, 11:37 AM #4
Probably not... I may be missing a few screws! Maybe i shouldn't answer things first thing in the morning. . : }
In rereading.. it should say "and the ground similar to a burner.. or use a used burner" so I guess that would basically be saying. No...why bother.
Sent from my GSIII on Tapatalk
-
01-11-2013, 06:11 PM #5
Professional Member
- Join Date
- May 2004
- Location
- SE Pennsylvania
- Posts
- 508
A flame sensor is not a magical device it is nothing but a metal rod with a ceramic or porcelain insulator. If you have continuity from the tip to the electrical connection, clean from excessive dirt and the insulator is not cracked it is good.
-
01-11-2013, 06:43 PM #6
Does anyone know what voltage is used in a typical furnace flame rectification circuit? Is it actually 120VAC? If so, I'm glad I never tried to touch the sensor while a furnace was try to ignite. I've measures many flame rectification circuits with my meter but have never be bitten by one.
"The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
"Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
"Beer is living proof that God loves us and wants us to be happy" --Benjamin Franklin
-
01-11-2013, 07:11 PM #7
Professional Member*
- Join Date
- Jul 2010
- Location
- nebraska
- Posts
- 1,165
Depends on the control board air1. Put one meter lead on the flame sensor wire and the other to ground and check a few. It only takes a second. BTW the voltage is not only present when it's trying to light. Many boards send constant voltage to the flame sensor,checking for flame when there should not be one.
-
01-11-2013, 07:25 PM #8
You can test flame rectification with most any voltage. I know of fireplaces that use a 3vdc system. It is the microamperage that counts. In order to test a flame rod in addition to a stable flame that closely approximates that of the subject appliance, you would need a ground that has a mass at least 4x that of the rod. Note that a rod which tests ok out of the unit does not guarantee it will work once installed so I see little benefit to this bench testing. As long as ceramic insulators are not cracked, there isn't much else to go wrong other than the actual electrical connections.
Keep the fire inside the fireplace.
-
01-11-2013, 07:28 PM #9
Interesting thread
Could you mount it next to a burner flame and use the diode checking function on your meter, testing between the burner ground and flame rod lead?
That may be a simple test, but I have never tried it
You have sparked my curiosity though
-
01-11-2013, 07:33 PM #10
-
01-11-2013, 09:21 PM #11
Professional Member*
- Join Date
- Oct 2009
- Location
- Raleigh, NC
- Posts
- 435
It is just a metal rod. This is somewhat oversimplified, but it just completes a circuit through the flame itself to prove ignition.
-
01-11-2013, 09:39 PM #12
I can't get a uA reading on my home furnace at all. Its an janitol with a spark igniter. flame sensor is coming from ignition module i know its good if i unplug it durners shut down and spark starts up and i know my meter is good ive tested the sensors at my school the same day. This has been bugging me can anyone please give me an explanation?
-
01-11-2013, 10:18 PM #13
Regular Guest
- Join Date
- Jun 2012
- Posts
- 33
Maybe I'm doing something wrong but I haven't replaced maybe a dozen flame sensors in 25 years


Reply With Quote
am I missing something here?