    Hmm Intellipack RTU

    Hello All:
    I'm having an issue the compressor circuit #1, on a call for cooling compressors energize and then trip on high head, condensers fan motors do not come on, is there is sensor, in series with the condenser fans contactors?????. I know something is locking the fans out.
    Any help is gratly appreciated it.

  2. #2
    Join Date
    Feb 2012
    Location
    EVERYWHERE
    Posts
    197
    First are you 100% sure the it is going off on high head? Also are all the fans and all the fuses for the fans good? The condenser fans are staged by condenser saturation temperature sensor on condenser coil.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    24,943

  4. #4
    Join Date
    Jan 2013
    Location
    Atlanta GA
    Posts
    64
    Thank you for the response FixitRight:

    I'm pretty sure is going off on high head pressure, I will go back to the job in the morning and check the condenser coil sensor, either way the fans are not energizing. What else could be in the circuit, besides the fuses and the sensor????? I was thrown at this job, intellipack are new to me.

    Thanks again pal.

  5. #5
    Join Date
    May 2003
    Location
    Utah
    Posts
    689
    For a start, you might try looking at the electrical schematic to see exactly what sensors/switches are in the control circuit of the cond fan contactor. Then trace the circuit and see what is preventing the coil from energizing.

  6. #6
    Join Date
    Feb 2012
    Location
    EVERYWHERE
    Posts
    197
    First you can test and make sure the fans work by putting unit in test. Go to service mode and turn everything off except for for your condedser fans. Then push test start and verify all condenser fan work. If they work in test check your saturated condenser temp sensor. It is on the u bends of the condenser coil. One for each circuit so make sure it is the right one you look at.

  7. #7
    Join Date
    Feb 2012
    Location
    EVERYWHERE
    Posts
    197
    Quote Originally Posted by bunny View Post
    For a start, you might try looking at the electrical schematic to see exactly what sensors/switches are in the control circuit of the cond fan contactor. Then trace the circuit and see what is preventing the coil from energizing.
    The control voltage for the contactors for the condenser fans comes from the compressor module. The fans stage off of temperature it gets from the saturated condenser temp sensor.

  8. #8
    Join Date
    Jan 2013
    Location
    Atlanta GA
    Posts
    64
    Got it.

    thanks a lot

  9. #9
    Join Date
    Jan 2013
    Location
    Atlanta GA
    Posts
    64
    Thank you bunny, I will do that.

  10. #10
    Join Date
    Jan 2013
    Location
    Atlanta GA
    Posts
    64
    Thank you FixitRight, I just got to job site and took the panels off at the condenser and the saturated temperature sensor was off the "U" bend just hanging, not se sing. The temperature, put sensor back in place and fans came on, thank you for advice, now circuit#2 is blowing the TF4, for no reason, it's got to be a direct short in the wiring, you got to love HVAC field, always a challenge everyday, thanks God for all of you guys that willing to give an advice.