    Niagara LON 'ping fail' alarms

    Some of my sites generate ping fail alarms on the LON networks. In most cases the ping returns to normal within a second or two.
    Is there a way to delay the ping response time of to make the system generate the alarm after maybe 2 or 3 ping failures?
    "Controls is a lifestyle not a job" -klrogers

  2. #2
    Join Date
    Jan 2002
    Location
    Fort Worth\Dallas, Texas
    Posts
    1,700
    I don't know of anyway to do that, but you could increase the ping frequency up from the default of 5 minutes.
    Go Rangers!

  3. #3
    Join Date
    Jun 2004
    Location
    SC
    Posts
    139
    Look at the poll scheduler statistics, what's the dibs bucket doing?

  4. #4
    Join Date
    Nov 2012
    Location
    Sydney, Australia
    Posts
    8
    Have you got your EOL terminations done?

  5. #5
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,281
    Assuming the LON Utilities Manager yields no errors.... and No one needs to know immediately on ?.... why not just change the alarm class?

    From there you could do something with an active alarm count or something along those lines to indicate a comm failure to the default/whatever alarm class. Including a delay.

  6. #6
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,281
    Better yet change the class, add a status demux to device, add a delay to the down, link to whatever alarm.

  7. #7
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,281
    I do both, but VAV's I don't really care about unless several has given up the ghost.... Plant controls diff story

  8. #8
    Join Date
    Jul 2008
    Posts
    1,474
    Quote Originally Posted by dapper View Post
    Some of my sites generate ping fail alarms on the LON networks. In most cases the ping returns to normal within a second or two.
    Is there a way to delay the ping response time of to make the system generate the alarm after maybe 2 or 3 ping failures?
    sounds like poor comms to me.
    are all links bound or polled?
    nciSndHrtBt and nciMinOutTime set on all the the field devices?
    1 + 1 = 3 ( *** for very large values of 1)

    ...everybody wants a box of chocolates and long stemmed rose

  9. #9
    Join Date
    Mar 2003
    Location
    NY
    Posts
    2,146
    Thanks for the replies guys. EOLs are all installed, Dibs are at 0%, points are polled. Will try some of the other suggestions and see if something works. Chris, most devices are not critical but a ping failure is the only way to tell if a unit goes down from a tripped breaker or blown fuse etc. All controllers use the unit 24v for power.
    "Controls is a lifestyle not a job" -klrogers

  10. #10
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,281
    Quote Originally Posted by dapper View Post
    Thanks for the replies guys. EOLs are all installed, Dibs are at 0%, points are polled. Will try some of the other suggestions and see if something works. Chris, most devices are not critical but a ping failure is the only way to tell if a unit goes down from a tripped breaker or blown fuse etc. All controllers use the unit 24v for power.
    I'm with ya there, but who cares about a VAV going down in the middle of the night or a weekend? Not me and not any building engineer that I know, but if I lost multiple then that I would like to know about.

    Once you change the Alarm classes and by adding status demux to each critical device, from there you can do many things with the Boolean outputs to COV a alarm.

  11. #11
    Join Date
    Jul 2008
    Posts
    1,474
    Quote Originally Posted by dapper View Post
    ... points are polled.
    Recommend that you dont poll
    1 + 1 = 3 ( *** for very large values of 1)

    ...everybody wants a box of chocolates and long stemmed rose

  12. #12
    Join Date
    Mar 2003
    Location
    NY
    Posts
    2,146
    Thanks Matrix, I have since bound all the points.
    "Controls is a lifestyle not a job" -klrogers

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event