    CARRIER 30RB controls

    Hello gents, Prodialog topic here, I was looking at two 30rb chillers yesterday master and slave on ccn setting between the two, While scrolling through the run hours I found master @94hrs and slave @14hrs, quite unbalanced , Then I started reading into the controls manual section on this , and it states that master will always run up first until a set# of hours in Service/Submenu , then will automatically swap master over to slave ,vice versa? correct?

    1) is this parameter in USER2 submenu 5&6? "schedule clock" with a max number of hours @99?
    also there is a reference to designating master/slave which will be the lead unit , but I dont see this param.??

    2)I tried the default password 11, incorrect, wasnt sure how to enter this exactly correctly , I`m pretty good with Prodialog but never had to get in this far, both chillers need to be local/off mode? in USER2 par.11 password is changed? can this be accessed without entering the initial password?


    thanks for responses , not an emergency just something I`m looking into stan
    Keep it simple to keep it cool!

  2. #2
    Join Date
    Oct 2011
    Location
    La.
    Posts
    280
    Maybe needs to be asked in pro forum

  3. #3
    Join Date
    Aug 2002
    Location
    Greenville SC
    Posts
    431
    factory password is 1111

  4. #4
    Join Date
    Feb 2003
    Location
    Wichita Ks
    Posts
    1,467
    Quote Originally Posted by chilbrig View Post
    factory password is 1111
    should be 0111

  5. #5
    Join Date
    Mar 2005
    Posts
    664

  6. #6
    Join Date
    Mar 2005
    Posts
    664
    something went wrong with link after I edited post , sorry.
    Keep it simple to keep it cool!

  7. #7
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,705
    Quote Originally Posted by stanbyyourword View Post
    something went wrong with link after I edited post , sorry.
    Thanks that's what I thought it looked like.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  8. #8
    Join Date
    Aug 2002
    Location
    Greenville SC
    Posts
    431
    Quote Originally Posted by freonrick View Post
    should be 0111
    Your right. Wasn't thinking on that one.

  9. #9
    Join Date
    Mar 2005
    Posts
    664
    damn I really thought these keypads were in usa ... :/
    Keep it simple to keep it cool!

  10. #10
    Join Date
    Apr 2007
    Location
    uk
    Posts
    179
    Service Menu is 88

  11. #11
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,705
    Stan can you post a picture of the Prodialogue panel?

  12. #12
    Join Date
    Mar 2005
    Posts
    664
    [url]http://www.google.co.uk/imgres?start=181&um=1&hl=en&tbo=d&rlz=1C1CHIK_en-GBGB459GB462&tbm=isch&tbnid=LmcaYvmqQXWN2M:&imgref url=http://www.comronusedfreezers.com/en/products/productsdetails/cat/3/pid/657/cu/waterchillers/merk/carrier/pn/carrier_30gx267a_0063_air_cooled_water_chiller_.as px&docid=1YO_gTdhsk_uLM&itg=1&imgurl=http://www.comronusedfreezers.com/portals/24/images/product/DSCN6318.JPG&w=640&h=480&ei=pGnvUIDYMOiY1AWoqoDQCw &zoom=1&iact=hc&vpx=753&vpy=186&dur=262&hovh=191&h ovw=255&tx=139&ty=60&sig=108417246815047084128&pag e=7&tbnh=138&tbnw=181&ndsp=28&ved=1t:429,r:6,s:200 ,i:22&biw=1366&bih=667[/url


    Were these controls used in American market? stan
    Last edited by stanbyyourword; 01-10-2013 at 08:46 PM.
    Keep it simple to keep it cool!

  13. #13
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,705
    What the hell was that ????? The link didn't really work. We only have the Pro-dialog touch screen over here so far. Maybe someday we will get Pro-dialog +LCD and even Pro-dialog Pro someday. Who knows.


    Quote Originally Posted by stanbyyourword View Post
    [url]http://www.google.co.uk/imgres?start=181&um=1&hl=en&tbo=d&rlz=1C1CHIK_en-GBGB459GB462&tbm=isch&tbnid=LmcaYvmqQXWN2M:&imgref url=http://www.comronusedfreezers.com/en/products/productsdetails/cat/3/pid/657/cu/waterchillers/merk/carrier/pn/carrier_30gx267a_0063_air_cooled_water_chiller_.as px&docid=1YO_gTdhsk_uLM&itg=1&imgurl=http://www.comronusedfreezers.com/portals/24/images/product/DSCN6318.JPG&w=640&h=480&ei=pGnvUIDYMOiY1AWoqoDQCw &zoom=1&iact=hc&vpx=753&vpy=186&dur=262&hovh=191&h ovw=255&tx=139&ty=60&sig=108417246815047084128&pag e=7&tbnh=138&tbnw=181&ndsp=28&ved=1t:429,r:6,s:200 ,i:22&biw=1366&bih=667[/url


    Were these controls used in American market? stan
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.