Carrier Screw Comp. Oil PSI ?
I have a Carrier Screw Compressor (ECC360-336LRCP) The chiller is about 5 years old. I have this problem from day one-- when the unit starts it will go off on a alarm A030 (Compressor A1 Pre-Start Oil Pressure) This will go on for a few times and go away for 2 or 3 weeks, The oil pump has been replaced , oil solenoid has been replaced, the check valve has been changed, oil transducer has been changed-- when I vent a small amount of oil from the ascess valve by the oil inlet to comperssor after falure, the oil comes out like it has liquid refergerant in it-- The unit does not have oil heaters on it-- after I do a vent the unit will start a run like a champ-- should the oil solid, no foam-- The Carrier tech is lost--no help!!! Has any one had a problem like this??
-
02-03-2012, 03:08 PM #2
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
Air cooled? Water cooled? Not recognizing that model number what part of the world are you near?
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
02-03-2012, 07:29 PM #3
I feel your pain. i have a pair of 30hxc machines doing the exact same things.
i have swapped parts,replaced parts, sat on a 5 gallon bucket for hours with laptop hooked-up monitoring everything and still have not figured it out. Mainly on circuit "b".
Tech support gave up on me. My last option is to temporary install an ivue and trend all pressures. good luck.
-
02-03-2012, 07:55 PM #4
Professional Member*
- Join Date
- Aug 2002
- Location
- Greenville SC
- Posts
- 398
I don't recognize the number for mandangle either. On the 30hxc to develope oil pressure you have to develope discharge pressure. The discharge pressure pushes the oil. If your condenser water is to cold, and your discharge pressure is slow developing, you will have a low oil pressure trip. You might already know all this, but I thought I would throw it out there just in case.
-
02-03-2012, 08:40 PM #5I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!
-
02-03-2012, 09:27 PM #6
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
02-03-2012, 09:28 PM #7
New Guest
- Join Date
- Feb 2011
- Location
- El Segundo CA.
- Posts
- 4
Oil psi
I have good oil psi after it starts,when it starts. It will not build pressure at start up, It is like it is vaper locked. The oil looks like it has liquid refregrant in it,It looks all bubbles,foam-- when it starts it will be 110 at pump-10.5 psi at filter, the oil is clean--new oil filters-- this has been going on for 5 #ucking years, I get no support from service. I think I will just have to live with it? Will not run it in a lead unit-- should have gotten a York!!
-
02-03-2012, 09:35 PM #8
Regular Guest
- Join Date
- Dec 2009
- Location
- Fort Worth, Texas
- Posts
- 142
check and see if compressor is not flooding if it is then check charge, temp sensors and exv, also check your motor cooling solenoid and motor temp sensor.
-
02-03-2012, 09:42 PM #9
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
02-03-2012, 09:44 PM #10
New Guest
- Join Date
- Feb 2011
- Location
- El Segundo CA.
- Posts
- 4
I will do this on Monday, The unit is a E- Pack, a big package unit with cooling tower, pumps 2 systems with 4 compressors all in one unit--- Junk? I think so, It looks like a box car on a rail road train. I will post what I find out--- I am using staged loading- the oil temp. I will have to get, the unit does not have oil heaters on it, More info on Monday
Last edited by Mandanglelow; 02-03-2012 at 09:48 PM. Reason: More info
-
02-03-2012, 09:45 PM #11
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
Ok I did some research and you have a 30HXA with a shared condenser. What is the ambient temp in you "package"?
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
02-03-2012, 09:48 PM #12
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
-
02-03-2012, 10:55 PM #13
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.


Reply With Quote