Liebert Intellislot Card ?
Results 1 to 2 of 2
  1. #1

    Liebert Intellislot Card ?

    I am trying to set up this card for bacnet comms. I have enabled bacnet in the card, but am having problems setting the device name. No matter what name I put in, it comes back saying "...must be greater than or equal to and less than or equal to -". I even tried "-". Anybody?

  2. #2
    I set one of these up a couple of years ago and did it via the RS-232 port on the card. The device name you are putting in is a number, right? This should be your device or instance ID and has to be unique. This was on a CRAC unit that had a graphic panel interface which is where i thought you had to make the changes, found out later it was not, had to be on the actual interface card. I used hyper terminal to get into the card.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event