    Liebert Intellislot Card ?

    I am trying to set up this card for bacnet comms. I have enabled bacnet in the card, but am having problems setting the device name. No matter what name I put in, it comes back saying "...must be greater than or equal to and less than or equal to -". I even tried "-". Anybody?

  2. #2
    Join Date
    Apr 2012
    Posts
    17
    Post Likes
    I set one of these up a couple of years ago and did it via the RS-232 port on the card. The device name you are putting in is a number, right? This should be your device or instance ID and has to be unique. This was on a CRAC unit that had a graphic panel interface which is where i thought you had to make the changes, found out later it was not, had to be on the actual interface card. I used hyper terminal to get into the card.