    scotsman nugget ice machine woes

    Scotsman N0922A

    This unit is still under warrenty and only two months old.

    Last week it had a error for no water in resivour. Water was runnning into the reservoir into the freeze chamber and down the drain.

    Spoke with tech support and found the lower water seal bad. Ordererd a new one and returned today to install. Got the new seals installed but still leak not much though.

    Unit was running and producing good ice. Keptt going out on error code for ref pressurs too high/low. Found high side of 100 and low of 20. Unit installed in a garage that is not heated and was 52°.

    Spec sheet said lowest amb temp is 50. We are having them install a heater so we can recheck. Im just worried about the leaking.
    You can't kiss death without it kissing you back. Death is a passionate kisser.


  2. #2
    Join Date
    Dec 2009
    Posts
    162
    Post Likes
    Quote Originally Posted by marter View Post
    Scotsman N0922A

    This unit is still under warrenty and only two months old.

    Last week it had a error for no water in resivour. Water was runnning into the reservoir into the freeze chamber and down the drain.

    Spoke with tech support and found the lower water seal bad. Ordererd a new one and returned today to install. Got the new seals installed but still leak not much though.

    Unit was running and producing good ice. Keptt going out on error code for ref pressurs too high/low. Found high side of 100 and low of 20. Unit installed in a garage that is not heated and was 52°.

    Spec sheet said lowest amb temp is 50. We are having them install a heater so we can recheck. Im just worried about the leaking.

    Inlet water temperature should not be any lower than 45f

  3. #3
    Join Date
    Mar 2013
    Posts
    2
    Post Likes

    nugget ice machine , contact me @ 1-800-533-6006, call for tech assistance.

    Quote Originally Posted by marter View Post
    Scotsman N0922A

    This unit is still under warrenty and only two months old.

    Last week it had a error for no water in resivour. Water was runnning into the reservoir into the freeze chamber and down the drain.

    Spoke with tech support and found the lower water seal bad. Ordererd a new one and returned today to install. Got the new seals installed but still leak not much though.

    Unit was running and producing good ice. Keptt going out on error code for ref pressurs too high/low. Found high side of 100 and low of 20. Unit installed in a garage that is not heated and was 52°.

    Spec sheet said lowest amb temp is 50. We are having them install a heater so we can recheck. Im just worried about the leaking.
    There should be no water leaks at any point of operation,the water seal is suspect or was installed improperly. As for the amb. temp 52/f is also a concern. you need a warmer room. I'll need a few more details please call the number listed. Thank you.

  4. #4
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,309
    Post Likes
    What ive seen on some machines is that the inlet water pressure was too high and preventing the water inlet from closing. The water feeding in causes the reservoir to overflow and dump down the drain.


    Sent from my iPad using Tapatalk HD
    Every customer you take for granted today will be someone else's tomorrow.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •