    walk in freezer icing after expansion valve

    When I arrived discharge temp from evap was about 10 degrees.
    everthing after expansion valve frosted over.
    Sight glass was not clear
    outside ambient temp about 20 degrees
    only one condensor fan running due to ambient temp
    cond labeled R404A but there is possibility of mixed refrigerants according to owner
    low psi 3 lb high around 150 and sub cooling to low to read accurately.
    Since I knew siht glass should be flooded wspecially with such low ambient temps I added some 404a.
    low only rose to about 5 lbs high rose to about 250 and sub cooling also went up to about 15 degrees
    Discharge temp in box droped to about 10 degrees and sight glass was still bubbling although not as much.

    At this point something happened between my boss and owner I guess about price so I was asked to pack up and leave but was wondering what you veterens would have done next and if you had to guess what would you think the problem was.

    Also did put into defrost and defrost cyle was working although there did not seem to be any type of pumpdown. Condensor just turned off when t went into defrost.

    Thaks in advance for your response

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,497
    Wht shouldn't a freezer ice up after the valve? Sounds like you have other issues. We need more info before proceeding.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  3. #3
    Understood but I was not there long enough to collect any other data and generally dont spend much time working on freezers. I would expect some frost after expansion valve but is solid ice normal? wouldnt defrost cycle knock that down?

    again was not looking for an answer just some general opinions. More interested in why high side was high but still had bubbles in sight glass. If expansion valves was closeing for any reason plugged, broken overcharged whatever , would that not cause sight glass to clear even faster as liquid backed up to condensor?

  4. #4
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,834
    Your low side pressure too low for a freezer running 404a. Is your dryer before or after sg?

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,333

  6. #6
    Join Date
    May 2003
    Location
    Utah
    Posts
    718
    Quote Originally Posted by indoorairpro View Post
    low psi 3 lb high around 150 and sub cooling to low to read accurately.

    Seriously????

    I would love to hear an explanation on the sub cooling being too low to measure accurately.

  7. #7
    Join Date
    Apr 2010
    Location
    working overtime
    Posts
    829
    Step1 if mixture of refrigerants is suspected than before anything else recover, change drier, evacuate and recharge.

  8. #8
    Join Date
    Nov 2011
    Location
    New Hampshire
    Posts
    14
    If I was told there may be mixed gas in system I would have pulled the charge and also changed out FD on system. also after the txv there could be moisture in the system causing the ice up on the lines. next step would have been to do an efficiency test on the comp.

  9. #9
    Join Date
    Aug 2012
    Posts
    39
    Quote Originally Posted by Navy06 View Post
    If I was told there may be mixed gas in system I would have pulled the charge and also changed out FD on system. also after the txv there could be moisture in the system causing the ice up on the lines. next step would have been to do an efficiency test on the comp.
    I'm curious, do you actually repair commercial refrigeration equipment?

    Don't mean to be rude but your recommendations, and a couple of others, really has me wondering...

  10. #10
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    477
    txv and feeds freezing..........is normal in LT.

    Some of our bigger MT evaps even show frosting at times...dew and freezing point.

    I think when you mentioned subcool is too low to measure, you meant there was NO subcooling, as you indicated the sight glass was flashing.

    As mentioned you need to establish solid liquid to txv, and then measure SH from the evap.

    From there you can make other judgement calls..........but seeing you got called off, its obvious the customer is looking for cheap and dirty fix.

    Look at the TXV label to see what possible refrigerant is in the system.

  11. #11
    Join Date
    Apr 2010
    Location
    working overtime
    Posts
    829
    It doesn't matter what the system is doing as long as he has a zcontaminated system with mix of refigerants this unit won't work

  12. #12
    Join Date
    Aug 2012
    Posts
    39
    Quote Originally Posted by cavalieri85 View Post
    It doesn't matter what the system is doing as long as he has a zcontaminated system with mix of refigerants this unit won't work
    Customers can sometimes provide useful information or clues. In this example the customer said that there was a possibility of mixed refrigerant. That information may or may not be helpful, depending on what information they are basing that assessment on.

    At what point would you step back from changing parts and actually diagnose the fault?

  13. #13
    Join Date
    Apr 2010
    Location
    working overtime
    Posts
    829
    Well with an erratic system and only having limited info given to me at this point. Eliminating any possibility of mixed gases seems a good option. Of course looking at my superheat subcool comp amps and performance of system are a prerequisite to my suggestion. I am confused about what you are suggesting. Of course I would diagnose the unit!! Usually when a customer says this may have happened means it definitely did

Page 1 of 4 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event