Thread: Flame sensor needs cleaned monthly

  1. #1
    Join Date
    Sep 2010
    Location
    Gering, NE
    Posts
    14
    Post Likes

    Flame sensor needs cleaned monthly

    Had a no heat call today on a system I was at a month ago for regular maintenance and found today that the flame sensor was dirty I was reading .2 ua so I cleaned the flame sensor check my ua and it was back up to 2.8 after cleaning my problem with that though was that I cleaned the flame sensor on the maintenance call and was reading 2.8 ua after cleaning it then as well I got to looking at the work history on this call and saw that our company (i have only worked with this company for the past 7 months) has been out there 3-4 times a year cleaning this flame sensor and has even been replaced twice any suggestions as to why this may be getting dirty so quick so I can get this problem resolved and keep a good loyal customer from getting angry with the company

  2. #2
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    Check for leaky dryer vent, open laundry detergent containers, open paint cans, litter boxes, or anything else of that nature.
    Then check for adequate combustion air supply.

  3. #3
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,427
    Post Likes
    Something in the air is contaminating it. Find the source and remove it or find a different source of combustion air. The next problem you'll probably be seeing is a HE failure if you don't.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  4. #4
    Join Date
    Apr 2004
    Location
    Minnesnowta
    Posts
    2,364
    Post Likes
    If it's sealed combustion, make sure the intake is pulling in clean air. No recirculation, no other exhausts nearby etc. If it draws combustion air from the room, as mentioned by others, check for contaminants and remove.
    Wisdom has been chasing you, but you have always been faster.

    In your darkest hour, when the demons come, call on me brother and we shall fight them together.

    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  5. #5
    Join Date
    Sep 2010
    Location
    Gering, NE
    Posts
    14
    Post Likes
    Thread Starter
    Thanks everyone for the replies this is a residential furnace 80 percent however it is installed in a dry clean drop off building meaning clothes are dropped off at this building the clothes are then removed from the building washed and the reaturned so the litter box for a cat is out, the dryer vent is out because there is no dryer They don't do any cleaning at all in this building laundry deteregent is out and it's mounted in a suspended ceiling with plenty of combustion air. Kinda like wtf is going on because it is a very clean building

  6. #6
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    If you cleaned it with sandpaper it might be corroding.

  7. #7
    Join Date
    Sep 2010
    Location
    Gering, NE
    Posts
    14
    Post Likes
    Thread Starter
    Cleaned it with a steel brush

  8. #8
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    I think steel wool is the way to go. Might have chinese drywall or oil refinery near by, just throwing darts.

  9. #9
    Join Date
    Apr 2012
    Location
    Cleveland
    Posts
    744
    Post Likes
    Have the burners been cleaned? I've seen crud in the burners come out and coat the sensor.

  10. #10
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    So dirty clothes come in to the building?
    Where do you think dryer lint comes from?
    What does the sensor look like when you remove it?
    Ash coated? Discoloured? Burnt? Or clean?

  11. #11
    Join Date
    Sep 2010
    Location
    Gering, NE
    Posts
    14
    Post Likes
    Thread Starter
    Looks spotless

  12. #12
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,427
    Post Likes
    Quote Originally Posted by tkhvacguy View Post
    Looks spotless
    Well if cleaning it increases the ma, it's not spotless.......... that is unless.......... the connection is the culprit. That'd be a new one on me.

    Contamination of the sensor can be in many forms. Something is increasing the resistance of it.

    Did you say it was mounted above a suspended ceiling? Is the ceiling the fiberglass ceiling tile type with the metal grid work? Might be microscopic fiberglass particles being melted onto the sensor. Glass is a good insulator and would be hard to see.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  13. #13
    Join Date
    Sep 2010
    Location
    Gering, NE
    Posts
    14
    Post Likes
    Thread Starter
    That's a good point I do believe its a fiberglass tile not only that bit it's got the pink rolls of insulation right above it I could very well be getting insulation on it ill have to check it out but if that's the case the only way to correct it is to get its combustion air from outside and we would probably have to put a 90 percenter in instead well see what comes of it thanks for the help guys

  14. #14
    Join Date
    Jul 2012
    Location
    Cincinnati ohio
    Posts
    252
    Post Likes
    Quote Originally Posted by tkhvacguy View Post
    Had a no heat call today on a system I was at a month ago for regular maintenance and found today that the flame sensor was dirty I was reading .2 ua so I cleaned the flame sensor check my ua and it was back up to 2.8 after cleaning my problem with that though was that I cleaned the flame sensor on the maintenance call and was reading 2.8 ua after cleaning it then as well I got to looking at the work history on this call and saw that our company (i have only worked with this company for the past 7 months) has been out there 3-4 times a year cleaning this flame sensor and has even been replaced twice any suggestions as to why this may be getting dirty so quick so I can get this problem resolved and keep a good loyal customer from getting angry with the company
    What is the gas pressure set at? Cleaning a flame sensor with anything abrasive is a bad idea. I use a shop rag or the flap of my cargo pocket. It doesn't take much to remove the buildup...unless someone cleaned it once with a wire brush or sand paper and now it is corroding. I would replace the flame sensor and start fresh.

  15. #15
    Join Date
    Sep 2010
    Location
    Gering, NE
    Posts
    14
    Post Likes
    Thread Starter
    Gas pressure is 3.48 " wc

  16. #16
    Join Date
    Dec 2009
    Location
    plymouth mass
    Posts
    7
    Post Likes
    Try reversing hi voltage to the unit , a class i attended claims polarity will cause flame sensor fault .

  17. #17
    Join Date
    Jul 2008
    Posts
    1,589
    Post Likes
    The flame is conductive and the circuit is between the flame rod and the burner. So be sure to clean the metal parts of the burner near the flame rod so you get good current. You should also put a meter in series with the flame rd and see what your getting.

  18. #18
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    could be highly underfired or lack of post purge. this is causing the acids in the flue gas to attack the flame rod at off cycle.

  19. #19
    Join Date
    Jan 2011
    Location
    Massachusetts
    Posts
    131
    Post Likes
    I have a 2 stage Ruud furnace that once a month amber light blink clean it and I comes back in a month later replaced sensor now gonna change the board this is direct vent to outside 12 ft above the ground

  20. #20
    Join Date
    Jan 2002
    Location
    Chicago area, Il.
    Posts
    675
    Post Likes
    Do you mind if I ask exactly what brand and model of furnace this is. I ask, because over the years, at times manufacturers have had service bulletins, and changed components for exactly the reasons you have described, which has included flame sensor changes, relocation changes, and ignition module/circuit board changes. Myself or other members here might be able to help you if we have the exact unit you are referring to. If not, have you called the manufacturer tech support to see if they have made changes.
    Hi, my name is Glenn, and I'm a Toolaholic!

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •