Thread: York RTU stays stuck in heating...

  1. #1
    Join Date
    Jan 2013
    Posts
    5
    Post Likes

    York RTU stays stuck in heating...

    Even when w1 is diconnected, 24v power is at w1 terminal. I replaced board, tested by jumping heat on and off. Problem solved. No, got a call that unit won't come out of heat again..any suggestions??

  2. #2
    Join Date
    Feb 2009
    Location
    Miami, Florida
    Posts
    12
    Post Likes
    That should be the only possible reason of having 24 VAC out of the heat output, main board have to be shorted out.

  3. #3
    Join Date
    Jan 2013
    Posts
    3
    Post Likes
    possible control wire rubbing a 24v line? its a long shot but worth checking if you have changed the board

  4. #4
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    What's the model# of the unit?

  5. #5
    Join Date
    Dec 2012
    Location
    Illinois
    Posts
    535
    Post Likes
    Heat circuit load too high? (Bad ignition module, partially shorted valve) Excess load welded relay on new board?

    That's my two cents. Good luck, definitely odd sounding issue though.

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Is it a sunline unit. If it is, I know whats wrong. Are you a tech? You need to check your low voltage circuit. In my experience runaway heat on the sunlines is only caused by 1 thing.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  7. Likes VTP99 liked this post.
  8. #7
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    I'll even give you a hint: Something is welded shut. If it's a tan unit it's one thing, and if it's the newer brown units it's another.
    Last edited by 2sac; 01-09-2013 at 11:07 PM.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  9. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by 2sac View Post
    I'll even give you a hint: Something is welded shut. If it's a tan unit it's one thing, and if it's the newer brown units it's another.
    You are SUCH a tease!
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #9
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by timebuilder View Post
    You are SUCH a tease!
    I am, aren't I
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  11. #10
    Join Date
    Jan 2013
    Posts
    5
    Post Likes
    Thread Starter
    Yea I am a tech. Tan D4CG series

  12. #11
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    I'm not going to make it easy on you. LOL Look at the heating circuit in your schematic. There is a 3 wire switch whose contacts are welded closed on both sets of contacts. If you follow the schematic, you will see why you have runaway heat. When you replace this you need to order the replacement kit from York, not just the part.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  13. #12
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    Quote Originally Posted by canmex View Post
    Even when w1 is diconnected, 24v power is at w1 terminal. I replaced board, tested by jumping heat on and off. Problem solved. No, got a call that unit won't come out of heat again..any suggestions??
    there are 3 ice cube relays, replace the one in the middle.

  14. #13
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by valdelocc View Post
    there are 3 ice cube relays, replace the one in the middle.
    Not on the tan units
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  15. #14
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    Quote Originally Posted by 2sac View Post
    Not on the tan units
    missed the "tan" part, if my memory doesn't fail me, in the older yorks w1 powers the inducer and after the centrifugal swt closes, the 24v travels through the safties and lands on the Johnson, right? I dont do RTu's as much anymore.

  16. #15
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    The tan units have (2) 24v supplies to the JC ignition control The control needs to see voltage at both before firing off
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  17. #16
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    2,617
    Post Likes
    Quote Originally Posted by 2sac View Post
    I'm not going to make it easy on you. LOL Look at the heating circuit in your schematic. There is a 3 wire switch whose contacts are welded closed on both sets of contacts. If you follow the schematic, you will see why you have runaway heat. When you replace this you need to order the replacement kit from York, not just the part.
    Seen this many times

  18. #17
    Join Date
    Jan 2013
    Posts
    5
    Post Likes
    Thread Starter

    Yup.

    Quote Originally Posted by 2sac View Post
    Not on the tan units
    Looks that limit switch was the deal. Thanks for all the insite. Never had that one before! Thanks again!And yea it's an assembley you get not just the switch.

  19. #18
    Join Date
    Jan 2013
    Posts
    5
    Post Likes
    Thread Starter
    Yea. After tracing it all out,that limit switch was the issue. And Yea you get the assembley not just the switch. Thanks for all the input and advise. Never seen that one before...

  20. #19
    Join Date
    Nov 2009
    Location
    Saskatchewan
    Posts
    494
    Post Likes
    I had one run away over xmass. The customer had a HUGE fish tank. All you could smell was fish. It was so hot
    in the bay it melted his hard drives, and cooked his fish. Just some bones bobbing around in the tank. It was the
    3 wire limit issue.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •