    Distech ECC-VAVS ?

    How do you override the damper by way of the plug-in? and how do you clear alarms that show up in the monitor display?

  2. #2
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    The I/O and priority of...

    and alarms where?

  3. #3
    Join Date
    Dec 2001
    Posts
    218
    Post Likes
    Quote Originally Posted by gazoo View Post
    how do you clear alarms that show up in the monitor display?
    In the screen shot you will see the UCPT to modify to "Unknown" and this should clear the monitor plug-in alarm. Most likely it is on WIRED_LCD_SENSOR by default. If you are using a standard thermistor wall sensor it will generate the error in the monitor plug-in.

    Name:  DistechMonPlugInError.png
Views: 500
Size:  71.3 KB

  4. #4
    Join Date
    Aug 2008
    Posts
    1,104
    Post Likes
    Thread Starter
    i clicked on the flashing red "device in alarm" and status showed good. nothing in alarm anymore. shouldnt going to the object manager in the cofiguration plug in and clicking the "clear status button" do the same?

  5. #5
    Join Date
    Dec 2001
    Posts
    218
    Post Likes
    Quote Originally Posted by gazoo View Post
    i clicked on the flashing red "device in alarm" and status showed good. nothing in alarm anymore. shouldnt going to the object manager in the cofiguration plug in and clicking the "clear status button" do the same?
    No

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •