    Quote Originally Posted by timebuilder View Post

    I recall that we had a rather spirited discussion about the validity of the test illustrated in that pdf.

    Perhaps someone will find it and link it to this thread.
    Here is one of them.........

    http://hvac-talk.com/vbb/showthread....acitor+testing
    Instead of learning the tricks of the trade, learn the trade.

  2. #22
    Join Date
    Jun 2009
    Location
    Jesup GA.
    Posts
    87
    Post Likes

    testing capactors

    [QUOTE=hvacrmedic;14977841]
    Quote Originally Posted by Cool_Air View Post



    The multiplier is derived from

    1,000,000/(2 x pi x hz)

    In this case hz is 60, so plugging into a calculator we get

    2652.5823848649222628147293895419...

    Rounding off to the nearest digit gives us

    2653 (but 2650 is close enough)

    For those on 50 hz systems the factor works out to

    3183
    haacrmedic thanks for this information

  3. #23
    Join Date
    Oct 2009
    Location
    Arizona
    Posts
    80
    Post Likes
    Double post.

  4. #24
    Join Date
    Oct 2009
    Location
    Arizona
    Posts
    80
    Post Likes
    this may help you.

    Unfortunately, some capacitor checkers we use in the field are ineffective at testing for a bleeding/leaking capacitor because there is no load on the capacitor at the time that it’s being tested.
    The good news is that there is a fairly reliable way to test a capacitor under load.
    While the compressor is running, measure the ac voltage across the run capacitor. You will be reading the voltage that the compressor is generating. The term for this is “back electromotive force.” Measure the amperage being drawn through the start wire between the capacitor and the compressor start terminal.
    Be sure to keep your amp meter away from the components in the control box - that could distort your reading. Use the voltage and amperage readings you’ve obtained in the following formula:
    Amps X 2,650 ÷ Voltage = Actual microfarads.

    If the solution to your test gives you a microfarad rating that is 5% below the capacitor’s labeled rating, be suspicious. If the results of your test show the capacitor to be 10% or more below the labeled rating on the capacitor, replace it.


    The most important amp draw reading to take is of the start winding (the wire that is connected to the run cap). If it is approx. half of the run winding then the run cap is good. For example if the run winding is 14 and the start winding is 3 then we have a problem. This is one of the biggest call back producers in our industry. Techs think that the run caps are either bad or good (not true) many many are just weak.
    See if no current is going thru the start winding (run cap weak/bad) then all the current will go thru the run winding and the amps will show much higher than normal. This is the reason you will find melted/loose connection on the common or run terminal of a compressor. You will never see it on the start terminal

  5. #25
    Join Date
    Oct 2009
    Location
    Arizona
    Posts
    80
    Post Likes
    Double post

  6. #26
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Thank you robert

  7. #27
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Another handy tool is an ESR tester. It sends a high frequency signal through the capcitor and measures internal AC resistance. Test can be done in circuit, no disconnecting required. Since the signal is high frequency very little passes through the motor windings. As capacitors dry out thier ESR increases. As ESR goes up capacitors run hotter. Eventually the capacitor overheats an the top bubbles up.

    http://en.wikipedia.org/wiki/ESR_meter

  8. #28
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    There is a low price kit for "blue ESR capacitor tester meter" on eBay.

    I believe this is the same technology used in battery conductance testers, which gives a better picture of battery condition than a simple load test.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  9. #29
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by timebuilder View Post
    There is a low price kit for "blue ESR capacitor tester meter" on eBay.

    I believe this is the same technology used in battery conductance testers, which gives a better picture of battery condition than a simple load test.
    The ebay kit is the one I have if it's the one I think you are talking about. Translucent plastic.

  10. #30
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    How do you like it?

  11. #31
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Works well, but I would choose removable leads if I was to design one of my own. The only caps it has a problem detecting bad are those that break down under load.

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •