    capacitor

    Can you tell if a capacitor is failing from output voltage alone?

  2. #2
    Join Date
    Sep 2011
    Posts
    95
    Post Likes
    i always just check the mF against the rating... you can discharge a cap by setting your meter to VAC and stick it across its terminals.

  3. #3
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    No. Use a meter with a microfarad scale to measure its capacitance. Lacking that discharge it first by shorting across the terminals, then use the resistance scale. Hold the probes on the terminals and the resistance should rise as the capacitor stores the charge. Also test for continuity from the terminals to the capacitor case. There should be no continuity.

  4. #4
    Join Date
    Sep 2011
    Posts
    95
    Post Likes
    cant you damage a cap by shorting across the terminals? thats why i suggest the "voltage test" across the terminals...

  5. #5
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    The proper way to discharge a capacitor is with a resistor i forget what ohm rating but i think one off an old start cap will work. And from what ive been taught capacitors dont increase voltage they help smooth out the voltage drop in AC cycles witch is why their not needed for three phase. So no i dont think its possible to check with voltage

  6. #6
    Join Date
    Jan 2013
    Location
    Central, FL
    Posts
    29
    Post Likes
    I always use a mfd setting on my meter. After discharging of course.

  7. #7
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    Quote Originally Posted by Core_d View Post
    The proper way to discharge a capacitor is with a resistor i forget what ohm rating but i think one off an old start cap will work
    I just use my tongue. Beats drinking energy drinks

    Sent from my SGH-T999 using Tapatalk 2

  8. #8
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    The capacitor has no "output voltage " you would be reading back emf voltage of motor and that alone does not tell
    You mfd. However there is a formula to use two parameters and determine mfd of said capacitor.

  9. #9
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by hvac wiz 79 View Post
    I just use my tongue. Beats drinking energy drinks.
    +1...beats a cup of coffee in the morning anytime.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  10. #10
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,248
    Post Likes
    Quote Originally Posted by Core_d View Post
    The proper way to discharge a capacitor is with a resistor i forget what ohm rating but i think one off an old start cap will work.
    That would be a 15,000 ohm, 2 watt resistor. Here is what I use - see attachment.
    Attached Images Attached Images
    Instead of learning the tricks of the trade, learn the trade.

  11. #11
    Join Date
    Nov 2011
    Location
    Philadelphia, PA
    Posts
    335
    Post Likes
    Thread Starter
    I always check voltage to them then I wondered the other day why I was doing this. So basically that number tells me nodda, right?

  12. #12
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Jesjen829 View Post
    I always check voltage to them then I wondered the other day why I was doing this. So basically that number tells me nodda, right?

    The ressssst....of the story is this:

    You use that voltage AND a current reading to calculate a value that tells you if the capacitor can supply the correct value of microfarads while under its normal load.

    As for myself, I remove the cap wires and use my meter to measure uF directly.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  13. #13
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    [QUOTE=timebuilder;14958021]The ressssst....of the story is this:

    You use that voltage AND a current reading to calculate a value that tells you if the capacitor can supply the correct value of microfarads while under its normal load.

    Any chance i could get a solid formula on this? Ide like to mess around with this.

  14. #14
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    [QUOTE=Core_d;14964881]
    Quote Originally Posted by timebuilder View Post
    The ressssst....of the story is this:

    You use that voltage AND a current reading to calculate a value that tells you if the capacitor can supply the correct value of microfarads while under its normal load.

    Any chance i could get a solid formula on this? Ide like to mess around with this.
    mfd = amps x 2653 / volts

    Another reason to check the voltage is to see whether the capacitor's voltage rating is being exceeded. If it is, then this could indicate one of several issues that need to be addressed. It would mean that either the voltage rating of the cap is too low for the application, the motor is severely underloaded, the motor is oversized, the capacitor mfd rating is too high for the application, or the incoming line voltage is too high. Any of these conditions will lead to premature capacitor failure and can also lead to motor failure.

  15. #15
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    [QUOTE=hvacrmedic;14965021]
    Quote Originally Posted by Core_d View Post

    mfd = amps x 2653 / volts

    Another reason to check the voltage is to see whether the capacitor's voltage rating is being exceeded. If it is, then this could indicate one of several issues that need to be addressed. It would mean that either the voltage rating of the cap is too low for the application, the motor is severely underloaded, the motor is oversized, the capacitor mfd rating is too high for the application, or the incoming line voltage is too high. Any of these conditions will lead to premature capacitor failure and can also lead to motor failure.
    Thank you

  16. #16
    Join Date
    Jun 2009
    Location
    Jesup GA.
    Posts
    87
    Post Likes

    How to test a capacitor while the unit is running

    [QUOTE=Core_d;14964881]
    Quote Originally Posted by timebuilder View Post
    The ressssst....of the story is this:

    You use that voltage AND a current reading to calculate a value that tells you if the capacitor can supply the correct value of microfarads while under its normal load.

    Any chance i could get a solid formula on this? Ide like to mess around with this.
    2650 X amps. Divided by volts while the condensor is running this will give you microfereds of your capacitor under a load.

  17. #17
    Join Date
    Jun 2009
    Location
    NYC
    Posts
    501
    Post Likes
    2650, 2652,2653,2654 same formula.

    You can use a light bulb too, to check a cap.
    Attached Images Attached Images

  18. #18
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    The four digit number used as a constant is good only for a 60 Hz test. Other frequencies, such as 50 Hz, will use a different number for that constant.

    I recall that we had a rather spirited discussion about the validity of the test illustrated in that pdf.

    Perhaps someone will find it and link it to this thread.

    There was a concern about whether or not the methodology was valid as a test for a weak cap, i.e., the comparison of the amperage readings, as illustrated.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  19. #19
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    [QUOTE=Cool_Air;14977221]
    Quote Originally Posted by Core_d View Post
    2650 X amps. Divided by volts while the condensor is running this will give you microfereds of your capacitor under a load.

    The multiplier is derived from

    1,000,000/(2 x pi x hz)

    In this case hz is 60, so plugging into a calculator we get

    2652.5823848649222628147293895419...

    Rounding off to the nearest digit gives us

    2653 (but 2650 is close enough)

    For those on 50 hz systems the factor works out to

    3183
    Last edited by hvacrmedic; 01-12-2013 at 06:37 PM.

  20. #20
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by timebuilder View Post
    The four digit number used as a constant is good only for a 60 Hz test. Other frequencies, such as 50 Hz, will use a different number for that constant.

    I recall that we had a rather spirited discussion about the validity of the test illustrated in that pdf.

    Perhaps someone will find it and link it to this thread.

    There was a concern about whether or not the methodology was valid as a test for a weak cap, i.e., the comparison of the amperage readings, as illustrated.
    It's specifically Test 1 in that .pdf that's invalid, just to clarify. Test 2 is perfectly ok.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •