    How to increase air flow to bedroom

    Classic problem I suppose. The bedroom duct furthest from the furnace puts out very little air. There is a return near that sucks very strong. The duct is 8'x6" that converts to 6" round inside the wall, but even in the basement, the duct itself isnt warm to the touch when the heat is on. There is a little air movement, but really not very much.

    I cant really run new ducts all over the place, so I was thinking about some kind of booster fan. Think that would help?

  2. #2
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    6,964
    Post Likes
    unlikely.

    best way to get air where it is needed is to adjust everyplace else for less air.
    the entire system needs to be balanced.
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  3. #3
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,374
    Post Likes
    Quote Originally Posted by vstech View Post
    unlikely.

    best way to get air where it is needed is to adjust everyplace else for less air.
    the entire system needs to be balanced.
    True -- I agree this is definitely the correct (and only) way to correct existing duct systems with many portions inaccessible. However, on older systems you have to be careful. Depending on the actual duct layout, when you start the add and adjust dampers you should also be prepared for a higher total ESP which is (not always, but likely) already high to begin with. A restrictive or dirty filter added into the equation would only add to the performance deficiency. The overarching solution is to thoroughly examine the duct system, make improvements to minimize pressure drops, and/or make improvements in existing equipment.

    Joey: Does this 8x6 come off the main supply plenum off the furnace/coil? What is the approximate length (if you had to guess)? The number and types of fittings will also affect airflow. What are the size(s) of the other trunk lines from the main plenum? Also curious roughly how big the bedroom is (is it a master?) to require one 6" round duct.

  4. #4
    Join Date
    Jan 2008
    Posts
    2,904
    Post Likes
    Make sure there is no manual damper closed off in the run-would most likely be close to the furnace or main duct.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.