New furnace and heat pump installed today
Our Lennox SLP98 and XP17 were installed today and I'd like to get some critiques of the install. How does it look? I can provide more pics if needed.
Out with the old....



In with the new....

-
01-08-2013, 11:36 PM #2
Looks pretty good.
-
01-08-2013, 11:36 PM #3
well done..... the only issue i have is no return air elbow..... nice work though.......
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
01-08-2013, 11:46 PM #4
Regular Guest
- Join Date
- Sep 2010
- Location
- Gering, NE
- Posts
- 14
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.
Last edited by jpsmith1cm; 01-09-2013 at 05:48 AM. Reason: non AOP member
-
01-09-2013, 12:11 AM #5
Regular Guest
- Join Date
- Jun 2011
- Location
- North Dakota
- Posts
- 38
-
01-09-2013, 01:11 AM #6If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?feature...&v=2kX_3y3u5Uo
http://www.youtube.com/watch?v=JVAhr4hZDJE
http://www.youtube.com/watch?v=-TC2xTCb_GU
-
01-09-2013, 05:48 AM #7
tkhvacguy
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.
-
01-09-2013, 06:10 AM #8
I'd hate to ever have to work on that heat pump. Line set and seal tight should have been ran down the wall then over to it.
-
01-09-2013, 09:34 AM #9
the unit is to close to the house Im sure in the install instructions it will state a min. clearence of prob. 18" or even 2'
also the fact that it faces the wrong way with the lines crossing the access pannel will be hard to service
though it is a fairly nice looking install clean looks and good workmanship
its allways eiseir to stand back and pick apart someonelses work to say would-a should-a could-a
-
01-09-2013, 09:43 AM #10
+1 on hte dryer vent. I really hope that's a fresh air intake of some sort. A codnenser coil will make a fine lint catcher and the warm moist air will make nice ice, droppping effciency by putting you into defrost a little quicker.
-
01-09-2013, 09:45 AM #11
-
01-09-2013, 10:19 AM #12
lineset needs to be elbowed down and routed for free access to service, an inspector should catch that and make them move it, there is no way to service compressor,and internal components, electrical likewise....FAIL
Total Energy Management, inc
-
01-09-2013, 11:51 AM #13
Professional Member*
- Join Date
- Mar 2009
- Location
- Mount Holly, NC
- Posts
- 1,615
there is no trap on the condensate line. so the vent is ALWAYS blowing air. I bet if you check the installation instructions, a trap is required.
The TRUE highest cost system is the system not installed properly...
The three big summer hearththrobs...
Mel Gibson
Dwane Johnson
The A/C repairman