02-05-2013, 10:15 PM #14
To clarify for others who will be testing. These motors are supplied with line voltage power all the time. They only energies to the selected "speed" when the correct low voltage tap is energized. Condemning an ECM motor only because it is getting 120V and not spinning could lead to a mis-diagnosis.
-
02-06-2013, 12:32 AM #15
Professional Member
- Join Date
- Oct 2012
- Location
- Sacramento,ca
- Posts
- 171
I am new here and i guess i should have gave more info. I only condemn when the tap is getting low voltage power and the motor has 120v. Not just 120v alone. Sorry for my vagueness. Thanks for clearing that up. I was just suggesting not spending alot of valuable time figuring out what part of the head might actually be broken. Even though it may be a cheap quick solder piece to fix it, to me that opens up your company for liability. I would rather replace with a complete factory built motor so if it ever caught fire or something they cant come back and say you modified the motor or something. Just my 2C.
-
02-06-2013, 01:02 AM #16
Also worth noting for those unaware, VS ECM motors are DC and not AC. There is a circuit similar to a diode bridge or wheatstone bridge that rectifies the incoming AC to DC. And also, troubleshooting the "control heads" is very simple.
The picture in my avatar is of the Houston Ship Channel and was taken from my backyard. I like to sit outside and slap mosquitos while watching countless supertankers, barges and cargo ships of every shape and size carry all sorts of deadly toxins to and fro. It's really beautiful at times.....just don't eat the three eyed fish....
¯`·.¸¸ .·´¯`· .¸>÷÷(((°>
`·.¸¸..· ´¯`·.¸ ¸.·´¯` ·.¸>÷÷(((°>
.·´¯`· .¸>÷÷(((°>
LMAOSHMSFOAIDMT
-
02-06-2013, 06:04 AM #17
-
02-06-2013, 08:51 AM #18
If troubleshooting a VS ECM motor is simple then I'd sure like to know how to do it. If you know of an easy way besides using a special tester designed to diagnose them please reply with " I'll explain in the Pro Residential forum". I'll start a thread on "Diagnosing VS motors". I'm not trying to put you on the spot but I would like to learn how to better diagnose a VS motor on the job & I'm sure a lot of other pros would too. When I condemn a VS motor (usually the module) I always feel I'm guessing out of process of elimination. So far I've been lucky & haven't been wrong yet but it can be an expensive mistake.
Gary
-----------
http://www.oceanhvac.com
An engineer designs what he would never work on.
A technician works on what he would never design.
-
02-06-2013, 10:25 AM #19
The special testers are nice for when you are troubleshooting odd behavior, or want/need to verify that the controls are sending the correct signals to the motor module, but for 99.9% of VS motor troubleshooting scenarios, all you need is a go/no go tester, and a couple of simple tests with a multimeter.
Basically, just verify the line voltage supply, if present, use something like the cheap tech mate switch to see if the motor runs.
If it has line voltage, and does not run when the control signal is applied with the tech mate, pull the module off and ohm out the motor windings.
If you don't get anything to ground on either of the 3 motor leads, and the resistance is the same lead to lead on all 3, and the motor bearings are good, replace the module only.
If any of the 3 resistance measurements lead to lead are different than the other 2 readings, but there is no reading to ground, or the motor bearings are bad, replace just the motor.
If you get a reading to ground on any of the 3 leads, replace both the motor and module.
You can even make a simple go/no go tester out of a spare 16 pin control harness, and a 9v battery.If more government is the answer, then it's a really stupid question.
-
02-06-2013, 05:20 PM #20
Professional Member*
- Join Date
- Apr 2010
- Location
- NC Sandhills
- Posts
- 181
I know, I figured with all of the module failures that the suppliers would have figured out it would save every one (except motor manufacturer but motors are out sourced) time and money. I have never seen a ecm motor where it wasnt the module and most the failures have been a few years old. I havent replaced many lately so hopefully the got the problem at least contained.
-
02-06-2013, 08:13 PM #21Gary
-----------
http://www.oceanhvac.com
An engineer designs what he would never work on.
A technician works on what he would never design.
-
02-06-2013, 09:12 PM #22
Thank you Mark. You took the time to concisely spell it out when I didn't have time to.
And Gary, I think a dedicated thread on ECM's is fantastic idea. I may be able to offer some insights into these mysterious black holes. I was once a product engineer for Carrier involved in one of the very first ECM deployments in a commercial airside product.The picture in my avatar is of the Houston Ship Channel and was taken from my backyard. I like to sit outside and slap mosquitos while watching countless supertankers, barges and cargo ships of every shape and size carry all sorts of deadly toxins to and fro. It's really beautiful at times.....just don't eat the three eyed fish....
¯`·.¸¸ .·´¯`· .¸>÷÷(((°>
`·.¸¸..· ´¯`·.¸ ¸.·´¯` ·.¸>÷÷(((°>
.·´¯`· .¸>÷÷(((°>
LMAOSHMSFOAIDMT
-
02-06-2013, 09:44 PM #23Gary
-----------
http://www.oceanhvac.com
An engineer designs what he would never work on.
A technician works on what he would never design.
-
02-07-2013, 07:43 PM #24
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,714
on the x13 motor if you have high voltage andlow voltage to the motor and it aint running its bad
The governent can not give anything to someone that it has not first taken from someone else
-
02-07-2013, 08:14 PM #25
Regular Guest
- Join Date
- Jun 2001
- Location
- Oklahoma City
- Posts
- 2,591
How many failures ahve you seen where the motor windings have failed vs. just the drive module?
-
02-07-2013, 09:06 PM #26