Page 1 of 2 12 LastLast
Results 1 to 13 of 19
  1. #1
    Join Date
    May 2012
    Location
    Grand Junction, CO
    Posts
    284
    Post Likes

    Proper gas connection

    Picture is a little dark. Saw this today. I love the black nipple for a flex coupling.
    Attached Images Attached Images  

  2. #2
    Join Date
    Jan 2013
    Location
    California
    Posts
    95
    Post Likes
    You would think that the installer would at least put the nipple where it enters the furnace cabinet to make it look a little better with the doors on (as well as be somewhat safer). And I guess a drip leg was too much to ask for also.

  3. #3
    Join Date
    May 2012
    Location
    Grand Junction, CO
    Posts
    284
    Post Likes
    Thread Starter
    Quote Originally Posted by Strkout499 View Post
    You would think that the installer would at least put the nipple where it enters the furnace cabinet to make it look a little better with the doors on (as well as be somewhat safer). And I guess a drip leg was too much to ask for also.
    I agree. There was enough slack in the flex, he could have at least pulled the nipple through the cabinet!

  4. #4
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,418
    Post Likes
    the nipple is the only good thing...lol
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  5. #5
    Join Date
    Jan 2010
    Posts
    12,751
    Post Likes
    Quote Originally Posted by GJ-HVAC/R View Post
    I agree. There was enough slack in the flex, he could have at least pulled the nipple through the cabinet!
    And what happens when the flex line rubs thru on the knock out hole ?
    Last edited by VTP99; 01-09-2013 at 01:03 AM. Reason: clarification

  6. #6
    Join Date
    May 2012
    Location
    Grand Junction, CO
    Posts
    284
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    And what happens when the flex line rubs thru on the the knock out hole ?
    Exactly my point

  7. #7
    Join Date
    Jan 2010
    Posts
    12,751
    Post Likes
    Quote Originally Posted by GJ-HVAC/R View Post
    Exactly my point
    Refrigerant is one thing but natural gas is a lot less forgiving
    I hope you correct that potential bomb.

  8. #8
    Join Date
    May 2012
    Location
    Grand Junction, CO
    Posts
    284
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    Refrigerant is one thing but natural gas is a lot less forgiving
    I hope you correct that potential bomb.
    Yep. I corrected it about an hour after i saw it. Now its piped black from the gas valve to outside the furnace. I wont leave something running unsafe!! :beer:

  9. #9
    Join Date
    May 2011
    Location
    tallahassee,fl
    Posts
    380
    Post Likes
    Good call

  10. #10
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,123
    Post Likes
    You are allowed to use ONE flexible appliance connector but it must not penetrate the cabinet. It can be inside the cabinet or outside but not through it. You can NOT splice two connectors as done here.

    A typical proper application with a flex connector would be piping to an approved shutoff, sediment trap, branch turns 90 degrees, ground union, steel through the cabinet, flex connector to the appliance valve.

  11. #11
    Join Date
    Oct 2004
    Location
    So Cal, Maui, & Kauai
    Posts
    4,013
    Post Likes
    Quote Originally Posted by hearthman View Post
    You are allowed to use ONE flexible appliance connector but it must not penetrate the cabinet. It can be inside the cabinet or outside but not through it. You can NOT splice two connectors as done here.

    A typical proper application with a flex connector would be piping to an approved shutoff, sediment trap, branch turns 90 degrees, ground union, steel through the cabinet, flex connector to the appliance valve.
    Why would you need a union when you're using a flex connector?

  12. #12
    Join Date
    Jan 2010
    Posts
    12,751
    Post Likes
    Quote Originally Posted by precision hvac View Post
    Why would you need a union when you're using a flex connector?
    That's a legitimate question. Could someone please explain ?

  13. #13
    Join Date
    Feb 2008
    Location
    Altmar, New York, United States
    Posts
    6,673
    Post Likes
    Quote Originally Posted by precision hvac View Post
    Why would you need a union when you're using a flex connector?
    i have never had an inspection fail because of not using one. i always thought it was a union. now i wonder if i was wrong and the inspector doesn't know any better.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.