    Did u put a manometer on to see what the differential pressure is? Checking for debris doesn't mean anything
  2. #28
    Sep 2010
    Gering, NE
    I had a older Lennox unit doing the same thing a couple weeks ago what I found was a weak inducer motor that when the burners light up would cause the pressure switch to open briefly but never did get an error code just kept trying to relight without locking out
  3. #29
    Nov 2007
    Mississippi
    I've had a goodman do the exact same thing to me as post #28.
  4. #30
    Jan 2011
    Ottawa, Canada
    Quote Originally Posted by tkhvacguy View Post
    I had one do this to me too. I cleaned everything and left it working and tested x5 and the next day the on-call guy (seasoned tech) found the p/s fluttering.
    how did you find out it was a weak inducer? pressure draw?
    Sent from my BlackBerry Runtime for Android Apps using Tapatalk 2
  5. #31
    N.E. Ok.
    Quote Originally Posted by stay gold jonny View Post
    What is the tool you have, and where can it be purchased?
    Probably talking about a molex pin extractor, Radio Shack or google.
  6. #32
    Oct 2011
    Toronto
    You could have a crack in the porcelain around the flame sensor that once heated expands and grounds out
  7. #33
    Sep 2010
    Gering, NE
    Quote Originally Posted by DeHeatify View Post
    Yes used my manometer to get the pressure draw on the pressure switch
  8. #34
    Houston,Tx.
    Quote Originally Posted by captube View Post
    Correct! we have a great little electronics supply house, not far from me that has everything, you could build the space shuttle with all that's in that store. I buy all my solderless terminals and etc. in there, they have bigger bulk packages and cost less than my supply house.
  9. #35
    Houston,Tx.
    Quote Originally Posted by GastecD View Post
    Could you eloborate a little on how this would happen? Thanks!
  10. #36
    Houston,Tx.
    This is why you carry plenty jumpers, you jump one safety at a time till you find the issue. I always check/jump all the safety's first then once they are ruled out I move on.
  11. #37
    Sep 2011
    you can check your ground by checking continuity between neutral and ground. Ground and neutral are electrically connected (bonded) inside the breaker box. though i don't know if the unit cares about earth ground or just ground as a reference. carrier support told me that their units need a good earth ground even if ground reference is good. don't ask me why.
    Last edited by wdshea; 01-09-2013 at 06:32 PM. Reason: sorry, didn't realize this post was 3 pages...
  12. #38
    Houston,Tx.
    Quote Originally Posted by wdshea View Post
    Exactly! this is why I mentioned to check from the neutrals on the board to a cabinet ground, if I suspect an issue, I always jumper from the neutral/neutrals on the board to the cabinet ground.
  13. #39
    Southeastern Pa
    The process of ground checking in this situation is to eliminate any high resistance points between the board/module and the burners. The burners are the negative side of the rectification circuit, and the flame sense rod is the positive side. The board or module supplies an AC voltage to the sensor rod, referenced to the burner ground, and then it looks for the DC microamp current, as a result of the flame rectification.
    You MUST have a good connection between the burners and the ground connection on the board or module. In rooftop units, you can apply a jumper from the burner array to the module, and if the problem goes away, you know you have a ground connection issue.