  1. #1

    x-13 evap motors...

    Who else loathes them with a passion

  2. #2
    Join Date
    Oct 2011
    Location
    between here and over there
    Posts
    453
    I love them they keep me busy

  3. #3
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,007
    Me too I love em. Cant get easier to troubleshoot or replace. They are actually nice little motors.

  4. #4
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    1,403
    I've replaced enough to last a lifetime.
    They usually fail between 18-36 months from installation.

    If you come across one that hasn't failed, check duct static. Keep TESP below .6", that should prevent the failure.

    They're supposedly failing due to prolonged runs times under high static. More failures in the south/humid areas due to wet coil operation nearly 8 months out of the year.

  5. #5
    Hello gentleman I have 0 experiance with the x-13 well up untill last week one of my customers relocated his barber shop to a small shoping center and called me a/c not cooling. he's got a commercial rheem pac unit 3 phase, float switch was triped, acid washed pan,blew-out drain pipe all good. Yeah till the next afternoon. Evap fan won't go unless you turn power off about 10min. then it comes on for a few hours or till the next day. The motor is 1 HP. 230volt date on motor is 2011 unit is 2009 so I guess its already been replaced. By what I just in these posts you guys are very familiar with this motor. I would greatly appreciate some direction so I can solve this issue.Thanks in advance! George

  6. #6
    The x13 is a single phase motor/module assembly. 3 phase motors are typically belt driven in my experience. I haven't seen a 3 phase ECM/x13. But I don't work on commercial equipment. Mostly residential. Did you verify you are not loosing a leg of power ?

  7. #7
    sorry for not being more specific the x-13 is single phase

  8. #8
    I have had them work after power cycles. Honestly I would just forgo the inevitable and replace the motor and module. The x13 is junk to say the least. Bullet proof solution would be to scrap that pos and put on a PSC motor.

  9. #9
    Join Date
    Mar 2012
    Location
    West Chester, PA
    Posts
    511
    regal x-13 motors have had 2 significant manufacturer defects that have been causing increased failures. This goes beyond the failure at high static. .6 as mentioned earlier is a great number to shoot for but is a somewhat dubious proposition in many of the duct systems that are out there. I have found around 0.8" to be the point at which these motors begin to fail.

  10. #10
    Genteq motors are just as unreliable. I have seen voltage drop and power outages become a killer of them where I live. Apparently the voltage interruption flashes the processor clean and it causes it to just sit and rock. But I've also heard we can reflash them in the field if you have the software

  11. #11
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    3,220
    Pull off the control module and look for a small fried resistor looking object labled SL22. If it's toast, see if you can twist the leads together for temporary operation until you can get a new module. Some have sucessfully found them online and soldered it back in...I wouldn't bother except for a charity case.

    They are finding it is seldom the motor, most always the module regardless of which type of ECM.

    The motor is pretty easy to check - just a three pin connector for the windings. Ohm each winding to one another, should all be under 20 ohms and within 10% of each other. Then each to ground - should all be OL or > than 100K. If the motor passes these two tests it is deemed good. Assuming it's not locked up tight.

    From there it's either the board or the motor control module. If the board is passing line voltage thru the line voltage plug, and control voltage thru the control voltage plug (be it AC, DC, 12v, 5v, 3 volt, pulsating volt etc.) then it's the motor control module that has failed. Assuming the wiring harness is intact, of course.

    Moisture is the biggest enemy of ECM motors, make sure the wiring harness to motor has a drip leg.

  12. #12
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    1,403
    Quote Originally Posted by hurtinhvac View Post
    Pull off the control module and look for a small fried resistor looking object labled SL22. If it's toast, see if you can twist the leads together for temporary operation until you can get a new module. Some have sucessfully found them online and soldered it back in...I wouldn't bother except for a charity case.

    They are finding it is seldom the motor, most always the module regardless of which type of ECM.

    The motor is pretty easy to check - just a three pin connector for the windings. Ohm each winding to one another, should all be under 20 ohms and within 10% of each other. Then each to ground - should all be OL or > than 100K. If the motor passes these two tests it is deemed good. Assuming it's not locked up tight.

    From there it's either the board or the motor control module. If the board is passing line voltage thru the line voltage plug, and control voltage thru the control voltage plug (be it AC, DC, 12v, 5v, 3 volt, pulsating volt etc.) then it's the motor control module that has failed. Assuming the wiring harness is intact, of course.

    Moisture is the biggest enemy of ECM motors, make sure the wiring harness to motor has a drip leg.
    The resistor trick is for true ECM motors. That doesn't apply to X13 motors.

  13. #13
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    3,220
    Quote Originally Posted by Brent Ridley View Post
    The resistor trick is for true ECM motors. That doesn't apply to X13 motors.
    How so? I have an X13 on my bench that has one. Are you saying it can't be soldered back in?

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event