Results 1 to 13 of 15
-
01-08-2013, 01:46 PM #1
Regular Guest
- Join Date
- Dec 2012
- Posts
- 61
HVAC Heat/Cool Load calculation example ?
I'm posting a Heat/Cooling load calculation that I did using a fantastic program posted here on this website (posted by permission).
Just about everyone here has stated the importance of doing a heat/cooling load calculation by experts who know how to do them. Just to understand how they might work I tried the program and came up with the following results.
To me (with the untrained eye) my results below look low. Especially when two of the possible HVAC companies that I contacted that did do a load calculation came up with much higher values:
Company One: 2 stage 78K/50K BTU with a 4 ton H.P.
Company Two: 2 stage 37K/58K BTU with a 3 ton H.P.
Currently Have: mid 90's Single stage 100K/80% with a 3ish H.P.
2800 SqFt
My Results: Heating: 35,826 Cooling: 40632 (sorry about the small size of the graphics below)
I realize that these load calculations are only one "tool" and require some artistic application, but again----just for my curiously---why would there be such a large difference ?
Thanks for the commentsLast edited by mixer440; 01-08-2013 at 01:49 PM. Reason: added info
-
01-08-2013, 02:22 PM #2
I live in SW WI & have a 57,500-Btuh propane furnace; with the temp at around 12-F & wind chill at -3-F it only takes 16,292-Btu during with one houir & 7 minutes off.
I use a SWING temp room- thermostat set at a 7-setting for over a 3 close to 4-F swing.
Runtime was 17-minutes at 958.333-Btu/per minute, or 16,292-Btu.
It would take high winds at deep sub-zero temps to get to the 57,500-Btuh capacity of the furnace; if it ever does!
Of course, it's a 95% with outdoor combustion air intake; the much colder weather combustion air temp drops the fire chamber's temps as it dilutes it; similar to pouring real cold cream into a boiling hot cup of coffee.
Winter design at La Crosse WI at 99% is -13-F; at 97.3% it's -9.
Madison WI is the same distance north; 99% is -11-F; 97.5% is -7-F.
It will be cruising at those temps because, I've checked it below zero, - but can't find those results to publish.
For those rare periods when it's extremely cold you could have a portable electric heater to supplement the furnace for those short periods of time; ... if ever needed.
I couldn't see the square footage of your home? Mine is a 2-story with a deep basement & heating around only 1000-sf.Last edited by udarrell; 01-08-2013 at 02:39 PM.
AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
01-08-2013, 02:54 PM #3
Regular Guest
- Join Date
- Dec 2012
- Posts
- 61
-
01-08-2013, 03:43 PM #4
your cooling load falls right between 3 and 4 tons so it looks like you're in the ball park there. The heat load looks low but it could be correct. usually the smallest resi furnace is 60k or 80k
-
01-08-2013, 04:20 PM #5
Regular Guest
- Join Date
- Dec 2012
- Posts
- 61
Thanks ADillon.
So if the smallest furnace is around 60K then you'd want that for the 1st stage--or--whatever stage is used least. Right ?
Off Topic: I like your picture, but have you seen this version: http://www.kulfoto.com/funny-picture...urger-and-head
-
01-08-2013, 04:29 PM #6
Professional Member*
- Join Date
- Feb 2009
- Location
- Portland OR
- Posts
- 1,509
I think that heat loss seems possible, so you might want a 3.5 ton air conditioner, but not all 60K BTU furnaces have a blower motor that can do 3.5 tons of airflow. You have to match the BTU's on the furnace, airflow on the furnace and coil and condenser so sometimes the correct combination does not meet the ideal heat load. If the 3 ton heat pump has been working for you I probably would not get a larger 3.5 ton, if your 3 ton has not been keeping up then I would look at the 3.5 ton heat pump. If you choose the 3 ton heat pump pretty much any two stage 60K BTU furnace will match up with that heat pump size.
Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
Like us on FACEBOOK if you like our advice here!
-
01-08-2013, 04:51 PM #7
60,000 would be second stage.
-
01-08-2013, 06:01 PM #8
Regular Guest
- Join Date
- Dec 2012
- Posts
- 61
-
01-08-2013, 06:25 PM #9
Professional Member*
- Join Date
- Feb 2009
- Location
- Portland OR
- Posts
- 1,509
Based on that model number it is a 3.5 Ton. If you look at the model look for a number with a 0 before it, then take that number, divide by 12 and that is how many tons the unit is for about 98% of equipment.
All companies have half sizes until you get to two stage units.Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
Like us on FACEBOOK if you like our advice here!
-
01-08-2013, 06:31 PM #10
Regular Guest
- Join Date
- Dec 2012
- Posts
- 61
Thanks for the info.
Q: Let's say for example then that you have/need 3.5 tons. If you get a 2 stage HP, then how do you size that ?
Q: What's your opinion on 2 stage units from Carrier or Trane ?
-
01-08-2013, 09:55 PM #11
Professional Member*
- Join Date
- Oct 2006
- Location
- So. NH
- Posts
- 652
-
01-08-2013, 10:12 PM #12
Professional Member*
- Join Date
- Oct 2006
- Location
- So. NH
- Posts
- 652
Just found this.
The temperature of incoming combustion air affects the measured efficiency: measured
SSE will be slightly lower in cold weather and slightly higher in warm weather. AFUE
ratings for sealed-combustion furnaces that use outdoor air are based on a national
average outdoor temperature of 42oF. A furnace will test about 1 to 1.5 percentage points
below AFUE on a cold winter day based solely on the difference in intake air temperature
2
(and a furnace tested on a hot summer day will similarly test about 1 to 1.5 percentage
points above AFUE).
Copied the info from here http://homeenergyplus.wi.gov/docview.asp?docid=13851
-
01-08-2013, 10:30 PM #13
Regular Guest
- Join Date
- Dec 2012
- Posts
- 61
AFUE
So, I guess that a 97% furnace is really a 95% furnace, since you'll never be using it in the summer and almost never above 40 degrees if you have a heat pump. Oh well, what's approximately 2 degrees over 10 years life ? (Hmm, let's see: 60,000 BTU/2%Xheating days below 40x10years=)


Reply With Quote