    HVAC Heat/Cool Load calculation example ?

    I'm posting a Heat/Cooling load calculation that I did using a fantastic program posted here on this website (posted by permission).

    Just about everyone here has stated the importance of doing a heat/cooling load calculation by experts who know how to do them. Just to understand how they might work I tried the program and came up with the following results.





    To me (with the untrained eye) my results below look low. Especially when two of the possible HVAC companies that I contacted that did do a load calculation came up with much higher values:

    Company One: 2 stage 78K/50K BTU with a 4 ton H.P.
    Company Two: 2 stage 37K/58K BTU with a 3 ton H.P.
    Currently Have: mid 90's Single stage 100K/80% with a 3ish H.P.

    2800 SqFt
    My Results: Heating: 35,826 Cooling: 40632 (sorry about the small size of the graphics below)

    Name:  hvac-top.jpg
Views: 2836
Size:  42.1 KB
    Name:  step4-btm.jpg
Views: 1796
Size:  37.4 KB





    I realize that these load calculations are only one "tool" and require some artistic application, but again----just for my curiously---why would there be such a large difference ?


    Thanks for the comments
    Last edited by mixer440; 01-08-2013 at 02:49 PM. Reason: added info

  2. #2
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,617
    Post Likes
    I live in SW WI & have a 57,500-Btuh propane furnace; with the temp at around 12-F & wind chill at -3-F it only takes 16,292-Btu during with one houir & 7 minutes off.

    I use a SWING temp room- thermostat set at a 7-setting for over a 3 close to 4-F swing.

    Runtime was 17-minutes at 958.333-Btu/per minute, or 16,292-Btu.

    It would take high winds at deep sub-zero temps to get to the 57,500-Btuh capacity of the furnace; if it ever does!

    Of course, it's a 95% with outdoor combustion air intake; the much colder weather combustion air temp drops the fire chamber's temps as it dilutes it; similar to pouring real cold cream into a boiling hot cup of coffee.

    Winter design at La Crosse WI at 99% is -13-F; at 97.3% it's -9.
    Madison WI is the same distance north; 99% is -11-F; 97.5% is -7-F.

    It will be cruising at those temps because, I've checked it below zero, - but can't find those results to publish.

    For those rare periods when it's extremely cold you could have a portable electric heater to supplement the furnace for those short periods of time; ... if ever needed.

    I couldn't see the square footage of your home? Mine is a 2-story with a deep basement & heating around only 1000-sf.
    Last edited by udarrell; 01-08-2013 at 03:39 PM.
    AOP Forum Rules:

    Rules for Posting

    Rules For Equipment Owners

    Equipment Owners Find a Contractor HERE!

    Free online whole house load calculator & Sizing: http://www.loadcalc.net/ Anyone can use it...!

    udarrell

  3. #3
    Join Date
    Dec 2012
    Posts
    62
    Post Likes
    Thread Starter
    That would be 2800 sqft single level, medium tight, W:R21/C:R42/F:R25, Ducts in vented crawl:R6

    Quote Originally Posted by udarrell View Post
    .....

    I couldn't see the square footage of your home? Mine is a 2-story with a deep basement & heating around only 1000-sf.

  4. #4
    Join Date
    Oct 2006
    Location
    So. NH
    Posts
    826
    Post Likes
    Quote Originally Posted by udarrell View Post
    I live in SW WI & have a 57,500-Btuh propane furnace; with the temp at around 12-F & wind chill at -3-F it only takes 16,292-Btu during with one houir & 7 minutes off.

    I use a SWING temp room- thermostat set at a 7-setting for over a 3 close to 4-F swing.

    Runtime was 17-minutes at 958.333-Btu/per minute, or 16,292-Btu.

    It would take high winds at deep sub-zero temps to get to the 57,500-Btuh capacity of the furnace; if it ever does!

    Of course, it's a 95% with outdoor combustion air intake; the much colder weather combustion air temp drops the fire chamber's temps as it dilutes it; similar to pouring real cold cream into a boiling hot cup of coffee.

    Winter design at La Crosse WI at 99% is -13-F; at 97.3% it's -9.
    Madison WI is the same distance north; 99% is -11-F; 97.5% is -7-F.

    It will be cruising at those temps because, I've checked it below zero, - but can't find those results to publish.

    For those rare periods when it's extremely cold you could have a portable electric heater to supplement the furnace for those short periods of time; ... if ever needed.

    I couldn't see the square footage of your home? Mine is a 2-story with a deep basement & heating around only 1000-sf.
    Hmmm, I never thought about how the outside combustion air temp may effect efficiency. I'm curious, I might have to dig into that. I would guess that the rating is based on a standard outdoor temp but have no idea how big the change might be.

  5. #5
    Join Date
    Oct 2006
    Location
    So. NH
    Posts
    826
    Post Likes
    Just found this.

    The temperature of incoming combustion air affects the measured efficiency: measured
    SSE will be slightly lower in cold weather and slightly higher in warm weather. AFUE
    ratings for sealed-combustion furnaces that use outdoor air are based on a national
    average outdoor temperature of 42oF. A furnace will test about 1 to 1.5 percentage points
    below AFUE on a cold winter day based solely on the difference in intake air temperature
    2
    (and a furnace tested on a hot summer day will similarly test about 1 to 1.5 percentage
    points above AFUE).

    Copied the info from here http://homeenergyplus.wi.gov/docview.asp?docid=13851

  6. #6
    Join Date
    Dec 2012
    Posts
    62
    Post Likes
    Thread Starter

    AFUE

    So, I guess that a 97% furnace is really a 95% furnace, since you'll never be using it in the summer and almost never above 40 degrees if you have a heat pump. Oh well, what's approximately 2 degrees over 10 years life ? (Hmm, let's see: 60,000 BTU/2%Xheating days below 40x10years=)


    Quote Originally Posted by stvc View Post
    Just found this.

    A furnace will test about 1 to 1.5 percentage points
    below AFUE on a cold winter day based solely on the difference in intake air temperature
    (and a furnace tested on a hot summer day will similarly test about 1 to 1.5 percentage
    points above AFUE).

    Copied the info from here http://homeenergyplus.wi.gov/docview.asp?docid=13851

  7. #7
    Join Date
    Mar 2012
    Location
    West Chester, PA
    Posts
    530
    Post Likes
    your cooling load falls right between 3 and 4 tons so it looks like you're in the ball park there. The heat load looks low but it could be correct. usually the smallest resi furnace is 60k or 80k

  8. #8
    Join Date
    Dec 2012
    Posts
    62
    Post Likes
    Thread Starter
    Thanks ADillon.

    So if the smallest furnace is around 60K then you'd want that for the 1st stage--or--whatever stage is used least. Right ?

    Off Topic: I like your picture, but have you seen this version: http://www.kulfoto.com/funny-picture...urger-and-head


    Quote Originally Posted by ADillon View Post
    your cooling load falls right between 3 and 4 tons so it looks like you're in the ball park there. The heat load looks low but it could be correct. usually the smallest resi furnace is 60k or 80k

  9. #9
    Join Date
    Feb 2009
    Location
    Portland OR
    Posts
    2,577
    Post Likes
    I think that heat loss seems possible, so you might want a 3.5 ton air conditioner, but not all 60K BTU furnaces have a blower motor that can do 3.5 tons of airflow. You have to match the BTU's on the furnace, airflow on the furnace and coil and condenser so sometimes the correct combination does not meet the ideal heat load. If the 3 ton heat pump has been working for you I probably would not get a larger 3.5 ton, if your 3 ton has not been keeping up then I would look at the 3.5 ton heat pump. If you choose the 3 ton heat pump pretty much any two stage 60K BTU furnace will match up with that heat pump size.
    Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
    Like us on FACEBOOK if you like our advice here!

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    75,563
    Post Likes
    60,000 would be second stage.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #11
    Join Date
    Dec 2012
    Posts
    62
    Post Likes
    Thread Starter
    SkyHeating: I'm unsure of the exact size of the Heat Pump and who knows what it is after 20 years. Here's the number:

    Name:  evco.jpg
Views: 1619
Size:  141.7 KB

    I'm curious, what does a dealer do if a company doesn't have 1/2 sizes----go up or down ?

  12. #12
    Join Date
    Feb 2009
    Location
    Portland OR
    Posts
    2,577
    Post Likes
    Quote Originally Posted by mixer440 View Post
    SkyHeating: I'm unsure of the exact size of the Heat Pump and who knows what it is after 20 years. Here's the number:

    Name:  evco.jpg
Views: 1619
Size:  141.7 KB

    I'm curious, what does a dealer do if a company doesn't have 1/2 sizes----go up or down ?
    Based on that model number it is a 3.5 Ton. If you look at the model look for a number with a 0 before it, then take that number, divide by 12 and that is how many tons the unit is for about 98% of equipment.

    All companies have half sizes until you get to two stage units.
    Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
    Like us on FACEBOOK if you like our advice here!

  13. #13
    Join Date
    Dec 2012
    Posts
    62
    Post Likes
    Thread Starter
    Thanks for the info.

    Q: Let's say for example then that you have/need 3.5 tons. If you get a 2 stage HP, then how do you size that ?
    Q: What's your opinion on 2 stage units from Carrier or Trane ?