    Fan cycler was set too high to leave the condenser run? Good chance its not working and is the cause of the restriction.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Sep 2011
    Posts
    79
    i don't think it is the fan cycle so much as the pressure issue. the fan cycle is detecting the liquid pressure (which is too low), and isn't cycling the fan on soon enough, by the time it does, the compressor relief is already bypassing.

  3. #16
    Join Date
    Dec 2008
    Location
    New York, ny
    Posts
    182
    What kind if unit is this your working on?

    Sent from my SGH-T999 using Tapatalk 2

  4. #17
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,285
    Quote Originally Posted by qwerty hvac View Post
    Why sell a new unit when you can fix the old one? Must be a glorified sales tech!


    Sent from my iPad using Tapatalk HD
    Highly glorified must add!! thats why I make the big bucks

  5. #18
    Join Date
    May 2007
    Location
    City That Never Sleeps
    Posts
    66
    This should be a good one, the high superheat indicates a starving evaporator but the lack of subcooling is trouble.

    The high excess compressor amperage is obviously telling you there is an issue. Im assuming this is a R22 system. Is it metering correctly? Can you range the SH? Your restriction could wind up being the TXV if its not the drier, kinked lines or the obvious.

  6. #19
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    1,749
    It's been over a week now. Hopefully it's solved. Hopefully we'll hear about it...

  7. #20
    Join Date
    Sep 2011
    Posts
    79
    Problem solved!

    Internal filter drier was restricting flow. You know the ones i'm talking about, those POS copper FD's that trane put inside the unit. The mesh had actually come apart and the dessicant had come out of it.

    Anyway, long story short, dumbass had low pressures, so he just kept adding refrigerant until the suction got above freezing.

    Anyway, i speculate that because the system was so grossly overcharged there wasnt a temp drop across the internal FD. (There wasnt, i checked)

    I recovered 18.5lbs of refrigerant, factory charge is 7.75, and i charged it to 13.75. System is running well, but there are some other issues that need attention.

  8. #21
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    1,749
    Quote Originally Posted by wdshea View Post
    ... factory charge is 7.75, and i charged it to 13.75.
    ? Never mind. I just reviewed first post saw "split system". Congrats on solving it, Wdshea.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event