    5 ton trane split system, condenser is on the roof. system cools a server room. at 55* ambient, i have ~100psig liquid pressure, close to zero subcooling, and amps in excess of RLA at the compressor.
    Any ideas? i'm starting to think air in system.
    p.s. 20* evaporator, with excessive superheat (TXV).
    you must have a restriction otherwise you would have nearly 500 psig at the LL solenoid valve too. not to say that you don't have air too, but your biggest problem is a restriction of some sort.
    May 2003
    Utah
    You state 250 at the LLSV and then say ~100 liquid pressure.
    Which is it???
    Sep 2011
    sorry, it had been a long day. the 100 psig was after i bypassed the fan cycle control so the unit would run. the 500/250 was what i was getting, but since the fan cycle control cut in was too high, the system couldn't run. i don't even know what the cut in is, couldn't read it.
    Sep 2011
    if it were air, could i pump down the system, and check the pressure against my PT chart? i realize that the LL Schraeder Valve would be blocked by the LL Service valve (when closed), but there is a schraeder on the discharge manifold. what do ya'll think?
    up in the hizzy
    Quote Originally Posted by wdshea View Post
    sell them a new unit, tell the customer tranes are junk, parts are expensive and the problem could be electrical,mechanical or both combined. that approach has never fail me, trust on this one.
    Sep 2011
    first of all, i don't want to sell them something they don't need, second i want to know why this system is acting the way it is.
    third, i assume you are kidding
    Eugene, Oregon
    Is there anything between the discharge and LLSV that could cause a restriction? Filter/Drier perhaps?
    To remove air I was taught to recover the refrigerant into a clean tank and let it sit for a while. Then bleed the air out of the gas valve. This way you could weigh out the charge to verify charge, remove any non-condensable gases, and weigh the correct charge in to eliminate the charge as a possible problem.
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com
    Aug 2008
    R-22,407C ,410A?? Check valve in discharge line?? Compressor on the the roof or at the air handler??
    Model and serial number of unit??
    More info please...
    Sep 2011
    the thing is, i was hoping to save time by pumping all the refrigerant into the condenser and essentially do the same thing... there is a cheap copper FD that was in the unit, then another filter drier out of the unit... though no temp drop on the internal FD.
    Eugene, Oregon
    You could still have a substantial pressure drop across the FD without a noticeable temperature drop. There was a thread about this very issue recently.
    Dec 2008
    Buffalo NY
    Quote Originally Posted by valdelocc View Post
    Why sell a new unit when you can fix the old one? Must be a glorified sales tech!
    Join http://scopeny.org/ Shooter’s Committee on Political Education
    The world is full of sheep,try not to join the flock.
    Support the Skilled Trades, Don't DIY
    Dec 2008
    Buffalo NY
    Quote Originally Posted by air1 View Post
    X2