500 psig at discharge, 250 at LLSV
likely restriction, or is this possible?
5 ton trane split system, condenser is on the roof. system cools a server room. at 55* ambient, i have ~100psig liquid pressure, close to zero subcooling, and amps in excess of RLA at the compressor.
Any ideas? i'm starting to think air in system.
p.s. 20* evaporator, with excessive superheat (TXV).
-
01-07-2013, 11:42 PM #2
you must have a restriction otherwise you would have nearly 500 psig at the LL solenoid valve too. not to say that you don't have air too, but your biggest problem is a restriction of some sort.
The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
-
01-08-2013, 10:05 PM #3
You state 250 at the LLSV and then say ~100 liquid pressure.
Which is it???
-
01-09-2013, 07:55 AM #4
Regular Guest
- Join Date
- Sep 2011
- Posts
- 57
sorry, it had been a long day. the 100 psig was after i bypassed the fan cycle control so the unit would run. the 500/250 was what i was getting, but since the fan cycle control cut in was too high, the system couldn't run. i don't even know what the cut in is, couldn't read it.
-
01-09-2013, 05:09 PM #5
Regular Guest
- Join Date
- Sep 2011
- Posts
- 57
if it were air, could i pump down the system, and check the pressure against my PT chart? i realize that the LL Schraeder Valve would be blocked by the LL Service valve (when closed), but there is a schraeder on the discharge manifold. what do ya'll think?
-
01-09-2013, 05:17 PM #6
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 939
-
01-09-2013, 05:21 PM #7
Regular Guest
- Join Date
- Sep 2011
- Posts
- 57
...
first of all, i don't want to sell them something they don't need, second i want to know why this system is acting the way it is.
third, i assume you are kidding
-
01-09-2013, 06:03 PM #8
Is there anything between the discharge and LLSV that could cause a restriction? Filter/Drier perhaps?
To remove air I was taught to recover the refrigerant into a clean tank and let it sit for a while. Then bleed the air out of the gas valve. This way you could weigh out the charge to verify charge, remove any non-condensable gases, and weigh the correct charge in to eliminate the charge as a possible problem."The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
"Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
"Beer is living proof that God loves us and wants us to be happy" --Benjamin Franklin
-
01-09-2013, 06:05 PM #9
R-22,407C ,410A?? Check valve in discharge line?? Compressor on the the roof or at the air handler??
Model and serial number of unit??
More info please...
-
01-09-2013, 06:06 PM #10
Regular Guest
- Join Date
- Sep 2011
- Posts
- 57
the thing is, i was hoping to save time by pumping all the refrigerant into the condenser and essentially do the same thing... there is a cheap copper FD that was in the unit, then another filter drier out of the unit... though no temp drop on the internal FD.
-
01-09-2013, 06:10 PM #11"The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
"Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
"Beer is living proof that God loves us and wants us to be happy" --Benjamin Franklin
-
01-09-2013, 07:05 PM #12
-
01-09-2013, 08:07 PM #13
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 939


Reply With Quote