Results 1 to 9 of 9
Thread: drawing 9 volts
    Chicago
    drawing 9 volts
    I walked up to Carrier rtu today that was suspected of not having power. when I pushed the contacter in the compressor would start. When i tried jumping r-w or r-g or r-y Nothing would activate. I checked voltage and was drawing 9 volts from r to ground. what would cause this voltage reading? bad transformer.?
    Jan 2010
    Did you check the secondary voltage at the transformer with load then no load ?
    May 2009
    Waterloo Ontario
    What he said. This is basic troubleshooting, start at the source, and trace until you find where your loosing Vac.
    Dec 2012
    Check ur transformer if it's good then check ur low voltage wiring even wire nut nuts and plugs.
    Jun 2012
    East tx
    Check your supply voltage to your primary side of transformer, make sure correct voltage is being used.
    Then i would check on output side of transformer,
    If all good there check for loose connections, and possible bad coils.
    Jun 2001
    Bad splices/connections can be gremlins in a machine. Look for connections that are twisted and taped instead of having wire nuts on them. I've seen a few bad ones.
    "pushing" the contactor in will bite you inn the ass one of these days
    if you never see a part start compressor winding, you'll be fine
    Mar 2009
    Mid-Mo
    Quote Originally Posted by dandyme View Post
    Or a compressor shorted to ground....
    Southeastern Pa
    In a carrier RTU, if I have low voltage, the very first place I go is that high temp cut out with the little red button over in the blower section. Then I look to see if there's a smoke detector wired in.
    After that, I look at the transformer as explained above.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
