I walked up to Carrier rtu today that was suspected of not having power. when I pushed the contacter in the compressor would start. When i tried jumping r-w or r-g or r-y Nothing would activate. I checked voltage and was drawing 9 volts from r to ground. what would cause this voltage reading? bad transformer.?
-
01-07-2013, 08:06 PM #2
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,403
Did you check the secondary voltage at the transformer with load then no load ?
-
01-07-2013, 08:08 PM #3
What he said. This is basic troubleshooting, start at the source, and trace until you find where your loosing Vac.
-
01-07-2013, 08:09 PM #4
Regular Guest
- Join Date
- Dec 2012
- Posts
- 6
Check ur transformer if it's good then check ur low voltage wiring even wire nut nuts and plugs.
-
01-07-2013, 08:11 PM #5
Check your supply voltage to your primary side of transformer, make sure correct voltage is being used.
Then i would check on output side of transformer,
If all good there check for loose connections, and possible bad coils.
-
01-07-2013, 08:21 PM #6
Regular Guest
- Join Date
- Jun 2001
- Location
- Oklahoma City
- Posts
- 2,573
Bad splices/connections can be gremlins in a machine. Look for connections that are twisted and taped instead of having wire nuts on them. I've seen a few bad ones.
-
01-07-2013, 08:36 PM #7
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,209
"pushing" the contactor in will bite you inn the ass one of these days
if you never see a part start compressor winding, you'll be fine
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
01-07-2013, 09:17 PM #8
-
01-08-2013, 05:19 PM #9
In a carrier RTU, if I have low voltage, the very first place I go is that high temp cut out with the little red button over in the blower section. Then I look to see if there's a smoke detector wired in.
After that, I look at the transformer as explained above.[Avatar photo from a Florida training accident. Everyone walked away.]