Results 1 to 9 of 9

Thread: drawing 9 volts

  1. #1
    Join Date
    May 2007
    Location
    Chicago
    Posts
    242
    Post Likes

    drawing 9 volts

    I walked up to Carrier rtu today that was suspected of not having power. when I pushed the contacter in the compressor would start. When i tried jumping r-w or r-g or r-y Nothing would activate. I checked voltage and was drawing 9 volts from r to ground. what would cause this voltage reading? bad transformer.?

  2. #2
    Join Date
    Jan 2010
    Posts
    13,240
    Post Likes
    Did you check the secondary voltage at the transformer with load then no load ?

  3. #3
    Join Date
    May 2009
    Location
    Waterloo Ontario
    Posts
    73
    Post Likes
    What he said. This is basic troubleshooting, start at the source, and trace until you find where your loosing Vac.

  4. #4
    Join Date
    Dec 2012
    Posts
    6
    Post Likes
    Check ur transformer if it's good then check ur low voltage wiring even wire nut nuts and plugs.

  5. #5
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes
    Check your supply voltage to your primary side of transformer, make sure correct voltage is being used.
    Then i would check on output side of transformer,
    If all good there check for loose connections, and possible bad coils.

  6. #6
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Bad splices/connections can be gremlins in a machine. Look for connections that are twisted and taped instead of having wire nuts on them. I've seen a few bad ones.

  7. #7
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,704
    Post Likes
    "pushing" the contactor in will bite you inn the ass one of these days

    if you never see a part start compressor winding, you'll be fine
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  8. #8
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by dandyme View Post
    "pushing" the contactor in will bite you inn the ass one of these days

    if you never see a part start compressor winding, you'll be fine
    Or a compressor shorted to ground....

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    28,089
    Post Likes
    In a carrier RTU, if I have low voltage, the very first place I go is that high temp cut out with the little red button over in the blower section. Then I look to see if there's a smoke detector wired in.

    After that, I look at the transformer as explained above.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.