    JCI - FEC / NCE pulse

    Hello,

    Can anyone shed light on if the JCI - FEC and NCE use a certain BI point for a pulse meter.

    I know that in the N2 product line, you can use DI2 (CNT2), and BI4 for the DX9100 and UNT. Can't really find anything online for the FEC or NCE.

    Thanks

  2. #2
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    FEC/NCE only uses the BIs for pulse inputs not UI's
    UA Local 141

  3. #3
    Join Date
    Mar 2012
    Posts
    43
    Post Likes
    Quote Originally Posted by berg2666 View Post
    FEC/NCE only uses the BIs for pulse inputs not UI's
    It has to be a BI and it has to be assigned as accumulator object in cct.

  4. #4
    Join Date
    May 2006
    Posts
    725
    Post Likes
    Thread Starter
    Quote Originally Posted by MikeAdams View Post
    It has to be a BI and it has to be assigned as accumulator object in cct.
    Thanks - that's the part I was missing.