01-17-2013, 08:29 PM #14
Regular Guest
- Join Date
- Jan 2013
- Posts
- 10
I'm glad it's working correctly. I did notice that when I had it set to 72 degrees it shut off for a couple minutes. I set it to 74 degrees and it hasn't shut off since (it has been a couple hours). What determines if it shuts off completely or not?
I am off with the square footage because I don't remember what it is exactly. I know the whole house is around 2,000 square feet. I believe the old part of the house is 360 - 500 square feet, so the addition is probably around 1,500 square feet. The addition has the duct work in the walls. The old portion of the house has duct work under in the craw space, and we were told that duct work would need to be redone, and we got the mini-split instead.
I will look into insulating the house better.
Thank you both!
-
01-17-2013, 11:13 PM #15
If the room temperature meets set point and the compressor is already running at its minimum speed then the outdoor unit will shut off. The indoor unit will continue to operate its fan. The room temperature is read at the indoor unit so it's fan never shuts off completely. If the indoor unit shut it's louver then the system may be in defrost. The compressor is capable of running at a small fraction of it's full speed and it's control will try to maintain exact set point without shutting off.
-
01-18-2013, 08:12 PM #16
Regular Guest
- Join Date
- Jan 2013
- Posts
- 10
The outdoor fan has been running nonstop. It only shut off once today when it was in defrost mode.
Also, the unit outside has been loud all day. It usually gets quiet but today it has been loud. Is it because it is cold, 32 degrees or so? I just found it odd that it has been loud since it usually isn't.
You said at the beginning of your post that the outdoor unit will shut off if it meets the desired temperature, but at the end of your post you said it will try to maintain the temperature without shutting off. I don't understand.
Thank you, I appreciate you explaining how the system works.
-
01-19-2013, 12:03 AM #17
-
01-19-2013, 11:31 AM #18
Regular Guest
- Join Date
- Jan 2013
- Posts
- 10
It is the Fujitsu 15RLS2. I've been reading a lot about them online but haven't found the answers to my questions. I've also looked on Fujitsu's website and read through the user manual.
It has been quiet today so I'm assuming it was noisy yesterday because of the cold.
Thank you.
-
01-19-2013, 11:47 AM #19
Might want to have a crankcase heater installed if it didn't come with one.
-
01-19-2013, 11:53 AM #20
I think inverter compressors take care of crankcase heat with trickle heat.
-
01-21-2013, 05:46 PM #21
Regular Guest
- Join Date
- Jan 2013
- Posts
- 10
What is trickle heat? I read something about it heating when the compressor is off, is that right? How do I tell if the compressor is on?
I was told to leave the fan setting on "High" instead of "Auto" and that "High" would put less stress on the unit. Do you agree?
Thank you.
-
01-21-2013, 11:14 PM #22
The "trickle heat" refers to a method of keeping the compressor warm whenever it's off for extended periods. I honestly don't know if the fujitsu systems have it.
I personality tell my customers to leave the fan setting in auto. You can't really enjoy just how quiet these systems can be otherwise.
Leaving the fan speed locked in high may have it's purpose, but it will also generate a much cooler heat and during the summer months the system will not be able to dehumidify the space as affectively.
-
01-22-2013, 12:17 PM #23
Professional Member*
- Join Date
- May 2004
- Location
- south louisiana
- Posts
- 2,179
isn't trickle heat a very very small amount of power
used to keep compressor from slugging?
fan speed should be lower for summer for colder
air & dehumidification.The cure of the part should not be attempted without the cure of the whole. ~Plato
-
01-22-2013, 12:29 PM #24
-
01-22-2013, 12:42 PM #25
Regular Guest
- Join Date
- Jan 2013
- Posts
- 10
Thank you for answering my questions.
I set the unit on 76 to see how warm it will get with it being 20 degress outside, and it is 71 - 72 in here. I guess that is normal for it being so cold outside.
I worry a lot, and I'm worried that the unit is running too much, or that it isn't sized correctly. I should take the advice from a poster earlier and leave the room if I think it isn't working properly.
I just want clarification on this:
Is it normal for the mini-split to run constantly, non-stop?
It was mentioned earlier about the inverter technology, so I guess that makes it all right if it runs non-stop.
Thank you for all of your help. I really appreciate your patience. I'm new at this and I'm trying to make sure I understand it correctly.