    Antiqued 4 ton condenser unit responsible of damaging 3.5 ton evaporator coil?

    Hey guys! I'll give y'all the Reader's Digest version of what happened....

    Note: The original installed equipment was confirmed to be a 3.5 ton Carrier condenser unit and 3.5 ton Carrier evaporator coil.

    So, approximately one week prior to the signing of the purchase settlement statement regarding our property purchase (February 2011), the previous homeowner contacted a local Texas-based HVAC contractor - mainly due to a problem with the central A/C system while testing its functionally (he was not living in the home for months prior) - especially after being shut down during the winter months, and with us closing on the property. Their service technician purportedly conducted a system check, and reported that the freon level tested low, and subsequently conducted a system leak check...at which time, it was determined by him, that the purported leak was originating from the location of the evaporator coil. Subsequently, the original, supposedly “damaged” 3.5 ton Carrier evaporator coil was removed/replaced ($) with a 4 ton Carrier evaporator coil (model # CNPHP4821ATAABAA) and recharged with an unknown amount of R-22 refrigerant, which was supposedly lost as a result of the leakage. As of date, the company's owner refuses to speak with us, or release any information regarding this particular installation.

    Well, we officially moved into the property in June of 2011. The A/C system appeared to be operating adequately throughout the Summer of 2011, with no reported issues. We shut down the A/C system for the winter months - from approximately late November 2011 thru mid/late April 2012. Only when the interior house temperature started reaching the mid-to-upper 70's during late April or so, did we start using the A/C system again. Initially, it would run cold for maybe a few hours or so, but then began to feel progressively warmer...not hot, just warmer. After several weeks of this, the blower would continue to run for hours at a time; forcing warm air through the vents...at this time, we were having a difficult time maintaining temperatures below 80°. At which time, I called and spoke with the previous homeowner about, whom advised me to contact the company whom originally installed the evaporator coil - since they were the last to service the system as of February 2011.

    I contacted and spoke with the company's owner via phone, and explained our situation regarding the loss of cooling relating to the A/C...I also asked if it could possibly be related to the evaporator coil they recently installed, and asked if it might/could be from a bad weld or seal, which he replied, “absolutely not”. After that point, he became extremely defensive and was a bit difficult to reason with. After going around in circles with him, we finally agreed to have one of his service techs come by to check it out, which would cost us a service fee of about $ or so. The service technician was “tentatively” scheduled to show up sometime after 4pm a few days from that time. So, I decided to call around, to try and find another company that could possibly come out before that time - especially with the outside temps being in the low 90's for the past day or so...I also wanted to find someone who wouldn't charge as much regarding the service fee.

    After contacting a few companies, I found one that agreed to send someone out around 9am the next day or so, and charging a service fee of around $ or thereabouts. By the time the technician arrived, the condenser unit was completely frozen and needed to be thawed out. After shutting down the system and waiting about an hour or so - and with the help of a heat gun - he was able to test the refrigerant levels, which tested noticeably low. We then sat down and discussed options regarding recharging the system to replace the lost freon - and possibly conducting a leak search, which would have been an additional $ or thereabouts. With the results of the gauge test, I asked about how much refrigerant might be required to recharge the system, which he said, he had no way of really being able to determine the exact amount needed. The system ended up requiring 5 lbs. 5.4 oz. of R-22 refrigerant, which resulted in a service bill of $ ($/lb. R-22 + service call fee + slight discount applied). Subsequently, I found out later that the unit holds a total of approximately 11 lbs of R-22...losing half of its refrigerant capacity!?

    Well, before leaving, the technician asked me if I knew anything about the condenser unit being over 20+ years old...I told him, that can't be right, the house was only about 10-years-old itself at that point. He walked me out to the unit and showed me the plate, showing a manufactured date of June 1991. Not only did I discover that the outside condenser unit was approximately 21 years old, which again, is approximately 10 years older than the house itself, but that it was a 4 ton condenser unit manufactured by Trane. I also discovered that it was also installed by the same HVAC company a few years prior (according to the service tag adhered to it)...which I'm assuming could have/may have been responsible for the failures (leakage) of the original evaporator coil, and now the condenser unit itself.

    Since that time, I've had 2 separate 'basic' leak tests performed by other HVAC companies offering free leak tests via radio commercials, and both confirmed that the leakage is now in the outside condenser unit.

    Anyway, so, I guess now my questions are...

    Q: Could this antiqued 4 ton Trane condenser unit been responsible of damaging the 3.5 ton Carrier evaporator coil, which was then replaced with a 4 ton Carrier evaporator coil...which in turn, could have caused the 21 year-old outside condenser unit to fail/leak now?

    Q: Is installing such an antiqued P.O.S. unit on a newer residential home even legal or is it a possible violation of some kind?


    I'd really appreciate any/all thoughts/comments/information regarding this situation...Thanx in advance!


    P.S. Sorry for using the word "subsequently" so much, too!
    Last edited by beenthere; 01-06-2013 at 06:41 AM. Reason: Prices

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Had nothing to do with causing a leak in the evaporator coil.

    May or may not be legal in your area.

  3. #3
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Quote Originally Posted by beenthere View Post
    Had nothing to do with causing a leak in the evaporator coil.

    May or may not be legal in your area.
    X2
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  4. #4
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by MisterMeanerTX View Post
    Hey guys! I'll give y'all the Reader's Digest version of what happened....
    That was the Reader's Digest version?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  5. #5
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by MisterMeanerTX View Post
    Q: Could this antiqued 4 ton Trane condenser unit been responsible of damaging the 3.5 ton Carrier evaporator coil, which was then replaced with a 4 ton Carrier evaporator coil...which in turn, could have caused the 21 year-old outside condenser unit to fail/leak now?

    Q: Is installing such an antiqued P.O.S. unit on a newer residential home even legal or is it a possible violation of some kind?
    A: NO
    A: NO


    We have units that were still in great physical and mechanical shape when removed from customers homes for upgraded systems, that we sell, or sell and install all the time.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  6. #6
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    That sounds ridiculous. It's hard to believe someone would install a 10 year old unit (at the time) on a brand new home. But, I have seen some crazy things.

    Please post pictures. Along with model and serial numbers. We can then confirm manufactured date and system size.

    And just FYI, the leak in the evap coil had nothing to do with a leak on a 21(?) year old condenser.

  7. #7
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    I had a house last winter that our resident hack put a furnace in when they did the addition, I was talking to the people about replacement because the secondary was rotten and HX was cracked and mentioned the date on it and they said the place wasn't even built till a few years later. It could have been old stock or used who knows.

  8. #8
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by MisterMeanerTX View Post
    Well, before leaving, the technician asked me if I knew anything about the condenser unit being over 20+ years old...I told him, that can't be right, the house was only about 10-years-old itself at that point. He walked me out to the unit and showed me the plate, showing a manufactured date of June 1991..
    This does not really prove anything, maybe the original "builders quality" unit died, and the homeowner chose to buy a used unit and have it installed. I see this all the time, especially on homes were the home owner says they are going to be putting the home on the market soon. How did this system ever pass the home inspection? In Texas the "home inspectors" are liable for some mistakes and carry insurance for this, most good home inspectors would have caught this right away, because they document Mod.#'s and Serial #'s to cover their butts.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  9. #9
    Join Date
    Aug 2010
    Location
    West Monroe, LA
    Posts
    1,594
    Post Likes
    Did you have a home inspector look at the home before you bought it? If so did he not look at the hvac system? If so he missed a very important item that would have let you know that something was not right with your system.

    There are so many things that could had happened before you bought the house. Example the outside condenser failed resulting in someone installing a older unit to get the system back up and going. While not right none the less it is what it is. You have per the last service tech a unit that is many years older in your home for some reason.

    Also just because the company that installed the new coil sticker is on the outdoor unit does not mean that they installed it all though they might have. In service we all sticker all parts of the system for hopes customer will see it and call us back to do the work.

    I would just speak to the owner of the company that installed the new coil and get as much info as possiable. Since you just bought the home odds are you plan to be there for a while so no since in putting band aids on problems.

    The outdoor unit if really that old needs to be changed to match the newer coil at minimum or replace the coil and condenser with R410a equipment then you will have a warranty. There are so many things that could have caused your current system to be like it is but without knowing why and who installed the outdoor unit you will get no where fast.

  10. #10
    Join Date
    Jun 2011
    Location
    Houston area
    Posts
    1,493
    Post Likes
    In Texas a homeowner can pretty much do anything he damn well pleases to his domicile. I'm not aware of any law or regulation that would prevent a homeowner from installing a 21 year old condenser on a new(er) home. It cannot be represented as new or energy efficient because it isn't. In this scenario SEER ratings do not come into play. Manufacturers are required to meet current federal efficiency guidelines but that doesn't mean you can't find an old unit (used or never used) and install it.

    The fact that the inspector didn't make note of something like that is of concern. What else did he miss? I'm not a lawyer but legally I doubt you have any recourse except possibly through the inspector and even that could be more expensive and drawn out than just replacing the system. Having said that, lenders are usually pretty picky about what they are financing and require certified inspectors.

    You signed the purchase agreement.

    caveat emptor (let the buyer beware: the principle that the seller of a product cannot be held responsible for its quality unless it is guaranteed in a warranty.

    BTW - the condenser had NOTHING to do with a failing evaporator coil even if the sizes don't jive.

    Good luck
    The picture in my avatar is of the Houston Ship Channel and was taken from my backyard. I like to sit outside and slap mosquitos while watching countless supertankers, barges and cargo ships of every shape and size carry all sorts of deadly toxins to and fro. It's really beautiful at times.....just don't eat the three eyed fish....

    Ż`·.¸¸ .·´Ż`· .¸>÷÷(((°>

    `·.¸¸..· ´Ż`·.¸ ¸.·´Ż` ·.¸>÷÷(((°>

    .·´Ż`· .¸>÷÷(((°>

    LMAOSHMSFOAIDMT

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •