Thread: Newbie building home..PLEASE help with setting up ideal heating and cooling system?

  1. #1
    Join Date
    Jan 2013
    Posts
    64
    Post Likes

    Newbie building home..PLEASE help with setting up ideal heating and cooling system?

    Just found this site and love it so far! I'm building a home and I want to make sure I make the right decisions on the heating/cooling setup. I'm a newbie but I've spent countless hours online researching things, then found this site and figured this would be a great resource. Here is my information..I figure I'd give you more than less to better help answer my questions.

    -Philadelphia, PA area. Number of days that AVERAGE 32 degrees or below..35. Number of days that the LOW temp drops to 32 degrees or below..100 (basically Dec through mid March). On average, the lowest temp of the year is 23 degrees.
    -House will be well insulated. 2x6 walls. R19 in walls, R50 or so in attic. I have stressed the importance of insulation to the builder. Short of spray foam, the house should be as tight as I can make it.
    -Gas is not available unless I want to spend $60,000 to extend the line
    -Propane about $2.80ish a gallon
    -My current electric with PECO is $.165 a Kwh
    -House is about 3140 sq ft., about 1550 on 1st floor and 1550 on 2nd floor. See attached pictures. Basement is just as big, and will likely be finished in the future.
    -I plan to have an efficient woodburning fireplace (RSF brand..heat capacity 1500-3000 sq ft) in the family room, which should be able to heat much of my home..at least the first floor from what I am told by the fireplace experts. I understand I'll be loading this fireplace several times a day.
    -I prefer propane for the range and hot water heater, and I plan to install a whole house generator in the future, so I want to have an underground propane tank (500 gallon or so?).
    -My contractor is pushing a 85% efficient propane furnace. I want to do an electric heat pump with a propane backup.
    -I plan to be in the home 20+ years.

    1. Do you agree that the heat pump with propane back up is preferable to the propane furnace?

    2. I'd like to utilize the wood fireplace to push heat to the rest of the house. One suggestion is to send it to the basement and duct it directly into the main heating system trunk. This would push the heat throughout the house. Another suggestion is to send it to the basement, duct it across the house to the opposite corner (living room) and have a vent there. This would keep that area from becoming a cold zone when the fireplace is running and keeping the family room/kitchen area toasty. Thoughts on this?

    3. Does it sound like I'd need a 2 unit/zoned heating system, one for each floor? The builder says I'm right on the edge of needing 2 units but he'd have to have the York guys run the numbers to determine, I assume using a Manual J. Also, would they take the fireplace into consideration at all for this calculation, or not b/c it still needs to be big enough for cooling? I assume the latter.

    4. I've researched like crazy and often read that heat pumps aren't too effective once the temp hits, depending on who you talk to, 35 or 30 or 25 degrees or whatever. But then I hear that something like a 2 stage Greenspeed unit WOULD work OK as temperatures plummet into the teens. So what's the deal with the capability of heat pumps in cold weather, and in my area (see the stats above) and my wood burning plan, is it a concern?

    5. Does a heat pump with propane backup, mean that I basically have a heat pump AND a (backup) furnace, or is it one unit? Trying to project the price of it compared to the builder's proposed 85% furnace.

    6. If the house turns out to be 2 zones/units, does that mean I need 2 heat pumps?

    7. If I get a heat pump with propane backup, should the furnace part be ultra efficient (95%) or is it not worth spending the extra money since it hopefully won't be running that much?

    If this is too many questions at once, please let me know for the future so I know to tone it down a bit.

    Thanks so much in advance!
    Attached Images Attached Images   

  2. #2
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,927
    Post Likes
    I'll try to answer your questions.

    A heat pump (HP) is like an air conditioner (AC). It is a separate unit vs. the furnace or air handler (which moves the air and will be the back-up heat).
    Most HPs, to be most efficient, need to shut down around 30 degrees. Then the back-up heat (gas, propane or electric) turns on. The "variable speed" (not 2-stage) Carrier Greenspeed is the most efficient HP and doesn't need to shut down early.

    Some utility companies will give a big (rate) break to a home that is all electric. You then would need electric air handlers (with staged electric heating). I believe you can still have the LP hot water heater, stove and dryer to receive the special rate. Something to look into and consider since you will be heating mostly with wood.

    I would recommend two systems (that'll be 4 major pieces, 2 inside and 2 outside). Both furnaces could be located in the basement or a utility room for the second floor system is even better. Both furnaces should be designed to have zoning. Note: Carrier also makes a killer (Infinity) zone system.

    Regarding the furnace efficiency needed. I like the 90+% AFUE because they use (you need to ask) outdoor combustion air. This should be an obvious reason in itself. But it also keeps the units quieter than the 80% furnaces. Of course, if you go with electric AHs none of the venting or combustion air becomes an issue.

    The major problem you'll face is finding a good HVAC contractor to properly size and install the equipment. Make sure to go with "variable-speed" blowers and good air cleaners. Carrier offers the best options there as well. Some on this site say they don't like Carrier. However, ALL the technology we now enjoy, came from Carrier's R&D.

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Yes the fireplaces are accounted for in a manual J. They add a little loss unless they are air tight.

    2 units, or zone it. Other wise you probably won't get even temps from one floor to the other.

    With dual fuel, you'll an outdoor unit, and a furnace with a coil attached to it. You would be better off with a 95% furnace then a 85%.

    At the propane rate you posted, 85% furnace is 3.57 for 100,000 BTUs of delivered heat, 95% is 3.20 for that same 100,000 BTUs of delivered heat.

  4. #4
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Are concerned about about indoor air quality? Mainly fresh air ventilation and humidity control? If not disregard.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  5. #5
    Join Date
    Jan 2013
    Posts
    64
    Post Likes
    Thread Starter
    Got it, variable speed, not 2 stage. I have read that the Greenspeed is the most efficient HP, just wondering if it's something I should push for in my situation (with my weather), as opposed to just a typical heat pump.

    I'll check with the utility on the electric break rate.

    With the 2 systems, I don't have a utility closet space upstairs (there's likely enough room but we'd have to redesign the home) so they'd likely put both in the basement.

    So back to my other confusion (questions 5 and 6), does that mean I'd have, on the inside, 2 heat pumps along with 2 furnace/air handlers?

    I agree about the challenge of finding the proper HVAC guys who know what they're doing. My fear is with the builder pushing propane, that is what he and his subs are used to. I want to make sure we use someone who knows what they're doing with a heat pump install. I'll mention the variable speed blowers and good air cleaners.. but what exactly do these do to benefit the system?


    Quote Originally Posted by George2 View Post
    I'll try to answer your questions.

    A heat pump (HP) is like an air conditioner (AC). It is a separate unit vs. the furnace or air handler (which moves the air and will be the back-up heat).
    Most HPs, to be most efficient, need to shut down around 30 degrees. Then the back-up heat (gas, propane or electric) turns on. The "variable speed" (not 2-stage) Carrier Greenspeed is the most efficient HP and doesn't need to shut down early.

    Some utility companies will give a big (rate) break to a home that is all electric. You then would need electric air handlers (with staged electric heating). I believe you can still have the LP hot water heater, stove and dryer to receive the special rate. Something to look into and consider since you will be heating mostly with wood.

    I would recommend two systems (that'll be 4 major pieces, 2 inside and 2 outside). Both furnaces could be located in the basement or a utility room for the second floor system is even better. Both furnaces should be designed to have zoning. Note: Carrier also makes a killer (Infinity) zone system.

    Regarding the furnace efficiency needed. I like the 90+% AFUE because they use (you need to ask) outdoor combustion air. This should be an obvious reason in itself. But it also keeps the units quieter than the 80% furnaces. Of course, if you go with electric AHs none of the venting or combustion air becomes an issue.

    The major problem you'll face is finding a good HVAC contractor to properly size and install the equipment. Make sure to go with "variable-speed" blowers and good air cleaners. Carrier offers the best options there as well. Some on this site say they don't like Carrier. However, ALL the technology we now enjoy, came from Carrier's R&D.

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    If the HVAC subs your builder uses aren't carrier dealers. You don't want someone installing a Greenspeeed.

  7. #7
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,927
    Post Likes
    Yes...you'll have two furnaces/fan coils inside and two HPs outside. The Carrier dealer will have a program that will show you exactly (in a matter of seconds) the operating costs of all the systems that are of interest.

    Did I also mention that Carrier has the best zoning. Note: Some have copied it (the modulating zoning) as well and try to take the credit. Just a FYI.

    Regarding the use of propane, check with your utility company to see if they'll give you a electric rate break.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by George2 View Post
    Some on this site say they don't like Carrier. However, ALL the technology we now enjoy, came from Carrier's R&D.
    Carrier wasn't the first to come out with a Mod furnace. Rheem/Ruud was, and it was about 15 years before carrier. carrier wasn't the first to come out with a variable AC, Trane was, about 20 years ago. Nordyne came out with a modulating heat pump 4 or 5 years ago, so carrier didn't invent that technology either. Not even sure Carrier was first to come out with a 2 stage A/C. So Carrier's R&D didn't come out with all the technology we enjoy in HVAC today.

  9. #9
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,927
    Post Likes
    Okay, maybe I exaggerated just a wee bit............ They do offer a few good ideas. It's not a bad line is my main point.

  10. #10
    Join Date
    Jan 2013
    Posts
    64
    Post Likes
    Thread Starter
    OK, got it. So the heat pump sits outside much like my current compressor does for my AC unit? I guess that's where I was confused. I thought it was on the inside. I told you I was a newbie.

    So with that said, if my builder currently includes a 85% propane furnace (doesn't state single or dual zone/unit) in the contract, and I say I want a dual zone heat pump with propane backup, that essentially means he has to put in 2 more heat pumps and 1 more furnace than he had planned, right? How much in material and labor am I looking at for this? Just trying to budget as best I can and not be shocked by the numbers.

    I plan to check with my electric supplier for any breaks.

    Thanks!

    Quote Originally Posted by George2 View Post
    Yes...you'll have two furnaces/fan coils inside and two HPs outside. The Carrier dealer will have a program that will show you exactly (in a matter of seconds) the operating costs of all the systems that are of interest.

    Did I also mention that Carrier has the best zoning. Note: Some have copied it (the modulating zoning) as well and try to take the credit. Just a FYI.

    Regarding the use of propane, check with your utility company to see if they'll give you a electric rate break.

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by George2 View Post
    Okay, maybe I exaggerated just a wee bit............ They do offer a few good ideas. It's not a bad line is my main point.
    No its not a bad line. You pay for all the advertising they do, and that large R&D department they have.

    And their mod zoning system is top of the line.

  12. #12
    Join Date
    Jan 2013
    Posts
    64
    Post Likes
    Thread Starter
    Noted. My fear is that unless the Greenspeed is stated in the contract, and he usually works with York guys (York unit is stated in the contract), the builder may give pushback on me wanting to use the GreenSpeed unit. Or may charge an arm and a leg since I'm not using his normal subs.

    I guess that's why I'm curious, for MY SITUATION, would I definitely be better off with the Greenspeed or would I be OK with a standard heat pump?

    Thanks!

    Quote Originally Posted by beenthere View Post
    If the HVAC subs your builder uses aren't carrier dealers. You don't want someone installing a Greenspeeed.

  13. #13
    Join Date
    Jan 2007
    Location
    Minneapolis, MN
    Posts
    421
    Post Likes
    1
    Last edited by mbarson; 01-06-2013 at 05:06 PM. Reason: Forgot the rules! Deleted post.

  14. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I wouldn't push for the greenspeed. You would be limited on who could work on it later.

  15. #15
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,927
    Post Likes
    Quote Originally Posted by lithnights View Post
    Noted. My fear is that unless the Greenspeed is stated in the contract, and he usually works with York guys (York unit is stated in the contract), the builder may give pushback on me wanting to use the GreenSpeed unit. Or may charge an arm and a leg since I'm not using his normal subs.

    I guess that's why I'm curious, for MY SITUATION, would I definitely be better off with the Greenspeed or would I be OK with a standard heat pump?

    Thanks!
    I hear your concerns all the time about "upsetting the builder feeling"........Really? Is it his money or yours? YOU are the boss, period. You should be able to tell him to jump and he should ask, "how far". Grow some balls. I'm done trying to give information if you're going to be too afraid to hurt the builders sensitive feeling. Is he the only guy in town?

    If I were building a house and the contractor was not willing to work for ME.......then it would be a very, very quick adios.

  16. #16
    Join Date
    Jan 2013
    Posts
    64
    Post Likes
    Thread Starter
    Ahh... I never thought of it from that angle. Good point.
    So beenthere, you're not far from me and probably have the same weather. Do you think we NEED a HP like the Greenspeed or would I be OK with a standard HP, knowing that I plan to keep my wood fireplace kicking all winterlong, and that the HP would have a propane backup? There are winters where we can get cold (I think last year the lowest we got to was 15 degrees or so one night and it stayed below freezing for a couple days straight.) But those below freezing spells are not the norm, so I often wonder if our area needs something like the Greenspeed as much as a more northern climate would.

    Thoughts?

    Thanks!

    Quote Originally Posted by beenthere View Post
    I wouldn't push for the greenspeed. You would be limited on who could work on it later.

  17. #17
    Join Date
    Jan 2013
    Posts
    64
    Post Likes
    Thread Starter
    Ouch. I'm not afraid of upsetting the builder, I'm fearing he simply may not do it CONTRACTUALLY, since it's not written in the contract. I've never built a home before so I don't know how flexible a builder would be once that contract is signed. Hoping for the best, expecting the worst. And more than that, I'm not as much fearing he wouldn't do it, but more that he would do it but then charge an arm and a leg more b/c he's not using his York guy (who he uses all the time I'm sure and has deals worked out). That's why I'm trying to figure out if it's truly needed or if I'd be OK with a standard heat pump, based on my weather.

    And so far he has been very flexible with us, from the design of the home, to the rewriting of his contract etc.

    And quite simply, he IS the only builder in town. Open space around us is simply non-existent. We're right outside Philly. It's built up. If a random lot ever does pop up, it's certainly not in a neighborhood, which is important to us. This lot is in our existing neighborhood, in the area we love, and we are able to build a custom home, so it's pretty much a once in a lifetime opportunity. We could always move 45 minutes away from where we're at to build. But that would give us a one hour and 20 minute commute to work, so basically that isn't happening.

    Hopefully that clears up where I'm coming from.

    Quote Originally Posted by George2 View Post
    I hear your concerns all the time about "upsetting the builder feeling"........Really? Is it his money or yours? YOU are the boss, period. You should be able to tell him to jump and he should ask, "how far". Grow some balls. I'm done trying to give information if you're going to be too afraid to hurt the builders sensitive feeling. Is he the only guy in town?

    If I were building a house and the contractor was not willing to work for ME.......then it would be a very, very quick adios.

  18. #18
    Join Date
    Jul 2007
    Location
    Delaware
    Posts
    3,825
    Post Likes
    The thing you should be worrying about is the location of the mechanical systems. Do you have a basement? Don't use any recessed lights on the top floor. In-fact don't cut any holes in the floor or the ceiling and you could put a 13 SEER system in there and save plenty! Those penetrations over time cost you BIG money! Use a closet for your equipment or add a small mechanical room "inside the envelope" Sheetrock the house first, hang the duct, then build your soffits...you'll save thousands over the years. Check out green home building sites.
    Always here

  19. #19
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Have you considered a geothermal heat pump? They are the most efficient heat pump out there and you do not have an outside unit. They are actually quieter than a furnace or air handler. They do cost more up front but the payback is very good.

  20. #20
    Join Date
    Jan 2013
    Posts
    64
    Post Likes
    Thread Starter
    Yes, the basement (9ft ceilings) is essentially the same footprint of the 1st floor..minus the garage area of course.
    I had thought about the location of the mechanical systems but wasn't sure how the HVAC guys figure out where to place that.

    I hadn't thought much about using or not using recessed lights on the 2nd floor..although our current home does have them in the master bath which is very nice. But I can see the potential heat loss with them.

    If the mechanical room is in the basement, is that considered inside the envelope? The basement won't have a designated heating zone (at least not until we finish it eventually) but it shouldn't be that much below room temp of the house, right?


    Quote Originally Posted by energy star View Post
    The thing you should be worrying about is the location of the mechanical systems. Do you have a basement? Don't use any recessed lights on the top floor. In-fact don't cut any holes in the floor or the ceiling and you could put a 13 SEER system in there and save plenty! Those penetrations over time cost you BIG money! Use a closet for your equipment or add a small mechanical room "inside the envelope" Sheetrock the house first, hang the duct, then build your soffits...you'll save thousands over the years. Check out green home building sites.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •