Results 1 to 2 of 2
  1. #1
    Join Date
    Jul 2011
    Location
    NEW YORK
    Posts
    58
    Post Likes

    Pressure Reducing Station Information.

    To Whom It May Concern:
    With regard to a Pressure reducing station 100# to 30# to 5#. The 5# end stage of reducer that goes downline to HX Control Valve. Can that end Prs fluctuate a little under 5# to a little over 6#. Is that just a demand +/-1# differential for load varying? We have a watts regulator. Should This 5# be on the money?

    Bob C.

  2. #2
    Join Date
    Sep 2004
    Location
    crossville
    Posts
    619
    Post Likes
    i am guessing your reffering to a gas( vaporous) system. or are you asking about a different fluid?

    flucation will be more about the demand load. especialy if its a load close to the regulators max flow. regulators are rated for minimum and max load size. generally one should size regulator size so that minimum load is higher than 25% of regulator rated , and max load is 7/8 of max rated, this cuts down on hunting of regulator,

    and the flucation is the regulator working. and load of demand.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365