    I live in N.W. Iowa in a single story ranch home with 1000 sq. feet, with a partial finished basement. We are looking into replacing our 23 year old single stage 74,000 btu furnace only. I have a quote from a local contractor for Trane and was wondering if this setup sounds correct for us. I will be replacing our Central Air some time down the road, but for not it still works so we are trying to save some money. We were quoted a model TVH2B080R9V with a Media Filter and a TCONT802
    thermostat. Can you also advice what is the best way to determine if we have enough cold air return for this system.
    We currently only have one cold air duct and a divider wall between the living room and dinning room. The register is on both sides of the 3.5 inch wall and is 8" x 31", this drops down through the floor into the cold air duct in front of the furnace and it measures 8" x 16" x 5 ft. He suggested adding a cold air return in the basement in the wall into the finished living area to aid in heating that room and also being able to run the fan only when we have the free standing wood stove in the room going to circulate the warm air through the whole house.

  2. #2
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    thats a 2 stage 95% furnace and 80000 btu ,seems huge to me for a 1000 square ft as the base ment probably wont need much heat , a oversized 2 stage furnace will only run in low .they do make one that is 6000 btu .ask for a load calcuation .also its is a tuh

  3. #3
    Join Date
    Dec 2012
    Posts
    9
    Post Likes
    Thread Starter
    Quote Originally Posted by catmanacman View Post
    thats a 2 stage 95% furnace and 80000 btu ,seems huge to me for a 1000 square ft as the base ment probably wont need much heat , a oversized 2 stage furnace will only run in low .they do make one that is 6000 btu .ask for a load calcuation .also its is a tuh

    Thanks, I will contact them to see if they will do a load calculation. I am not sure what the last part of your reply is, asking is it a tuh?

  4. #4
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Quote Originally Posted by firefighter4634 View Post
    Thanks, I will contact them to see if they will do a load calculation. I am not sure what the last part of your reply is, asking is it a tuh?
    It's a TUH2B080*** not TVH is what he was saying.

  5. #5
    Join Date
    Jan 2013
    Location
    California
    Posts
    95
    Post Likes
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 01-05-2013 at 10:27 PM. Reason: non AOP member

  6. #6
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    The model number is TUH not TVH. If the contractor didn't do a load calculation then he is already cutting corners. It's his job to determine the proper size, not yours.

    Call another contractor out. Check out the contractor locator map on this site for help finding a better contractor.

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Strkout449


    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.



  8. #8
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,927
    Post Likes
    Quote Originally Posted by firefighter4634 View Post
    I live in N.W. Iowa in a single story ranch home with 1000 sq. feet, with a partial finished basement. We are looking into replacing our 23 year old single stage 74,000 btu furnace only. I have a quote from a local contractor for Trane and was wondering if this setup sounds correct for us. I will be replacing our Central Air some time down the road, but for not it still works so we are trying to save some money. We were quoted a model TVH2B080R9V with a Media Filter and a TCONT802
    thermostat. Can you also advice what is the best way to determine if we have enough cold air return for this system.
    We currently only have one cold air duct and a divider wall between the living room and dinning room. The register is on both sides of the 3.5 inch wall and is 8" x 31", this drops down through the floor into the cold air duct in front of the furnace and it measures 8" x 16" x 5 ft. He suggested adding a cold air return in the basement in the wall into the finished living area to aid in heating that room and also being able to run the fan only when we have the free standing wood stove in the room going to circulate the warm air through the whole house.
    You do not have enough RA now. You're only getting about 300-400 cfm if two plates were removed and only 700-800 cfm if 4 plates were removed.

    The (added) return in the basement (the easiest place to get the extra RA) will needed to be very large to make up for the shortage. This is not a problem if your basement is open (no door) to the living area. If the basement can be sealed from the rest of the home, then you could end up reversing the flues.

    80,000 btu is what I use to heat my 2,250 s.f. 1946 (no insulation) colonial home (also in Iowa). Your new "2-stage" will almost never go to high fire. Don't feel too badly....it happens more often than not.

  9. #9
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    I'd be surprised if the heat exchanger is not cracked from such little return air. Return air definitely needs to be addressed with new install.

  10. #10
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    I've got 1000 sq ft, decently built. Basement adds little to the heat loss. I have a 60K 95% and have high fire turned off which means I can heat when it's below zero on about 37,000. We're a bit warmer than you, usually don't use an 80K furnace til we get into over 2000 sq ft.

  11. #11
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,927
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    I've got 1000 sq ft, decently built. Basement adds little to the heat loss. I have a 60K 95% and have high fire turned off which means I can heat when it's below zero on about 37,000. We're a bit warmer than you, usually don't use an 80K furnace til we get into over 2000 sq ft.
    Heck.......does it get warm enough for snow down there?

  12. #12
    Join Date
    Dec 2012
    Posts
    9
    Post Likes
    Thread Starter
    Quote Originally Posted by George2 View Post
    You do not have enough RA now. You're only getting about 300-400 cfm if two plates were removed and only 700-800 cfm if 4 plates were removed.

    The (added) return in the basement (the easiest place to get the extra RA) will needed to be very large to make up for the shortage. This is not a problem if your basement is open (no door) to the living area. If the basement can be sealed from the rest of the home, then you could end up reversing the flues.

    80,000 btu is what I use to heat my 2,250 s.f. 1946 (no insulation) colonial home (also in Iowa). Your new "2-stage" will almost never go to high fire. Don't feel too badly....it happens more often than not.
    Thanks for the reply. Our basement is open and it can not be sealed from the rest of the house. The stairway going upstairs is open into the kitchen, with a 30" tall knee wall along the top of the stairs. Can you please explain what you mean by removing plates?

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •