    Confused Does my furnace use too much gas?
    The york 80kbtu/hour natural gas furnace use 0.1 cubic meter per 20 seconds which read from gas meter. It should use 0.1 cubic meter per 152 seconds calculated from the installation manual. I tried to decrease the gas pressure but doesn't help. Read the 0.1 cubic meter from outside gas meter which has dial marked 0.01 cubic meter and ten units. It should be 0.1 when the needle runs one circle. Is it normal in Canada? or the outside gas meter is not accurate? Neighbor's meter needle runs at same speed.
    Calgary, Alberta
    *sigh*
    Why did you play with your gas pressure before you started asking questions? That's not good... Especially since you don't know what you're doing.
    Gas meters in Canada are temperature compensated to 60*F.
    This affects how fast the dial spins when it's freezing cold.
    Are you sure no other appliances were running when you took your readings?
    Jan 2013
    Quote Originally Posted by syndicated View Post
    *sigh*
    It's not good but I just decrease the pressure. The temp rise on furnace is only 27 degree c but it overheating shut down when running longer someday. The fan speed is already high. Everything is clean. Only thing I think that is gas. So I checked the gas heating vale and found the meter run so fast. Any suggestion? Thanks.
    Call a pro out to do a combustion analysis and properly tune the furnace. 27*F temp rise seems a bit low to me for a gas furnace.
    Calgary, Alberta
    He said 27*C not *F
    That's about 50*f
    Call someone out, there is something wrong with your furnace, you messing around with it will only cost you more money
    Cincinnati, Oh
    Using a gas meter to diagnose whats wrong with your furnace is insane.
    You'll be lucky if you don't kill yourself, and I stress this to you more than other DIY tools, because your directly modifing the combustion.
    "Just get it done son."
    Dad adjusted
    Athens, Ohio
    This is the reason there is no DIY on this site.
    You are tinkering with a regulating device for an explosive substance. Just because you CAN do something does not mean you SHOULD do it.
    Please keep your hands off of it and call in a pro.
    .1 CM in 152 seconds would be 83,000 BTUs. You said its doing .1 CM in 20 seconds. Thats 7.6 times more then the furnace is rated for. Or 630,800 BTUs an hour. If it was, it would be able to light the gas, there wouldn't be enough O2. Your meter is probably out of calibration.
    Jan 2013
    I checked neighbor's meters. They all run at the similar fast speed. Meter is outside of house, that belongs to enbridge. Are they all wrong? Whom should I ask to check, the gas supplier or furnace tech? Thanks.
    Calgary, Alberta
    Get your furnace serviced by a good company, then you'll know it's working right. You should do this every year.
    Ask them, when you book the call if they do combustion analysis.
    Then when you call enbridge to check the meter, they can't tell you that it's you appliances causing the problem.
    The gas company. Its there meter.