    Niagara AX- Need a Pressure Temperature Conversion block

    Does anyone have refrigerant pressure temperature logic blocks or something they can share with me? I need to control exv's from superheat directly in the jace. I was trying to play around with writing something in the program editor but my skill level is not up to par with line by line code.

  2. #2
    Join Date
    Jul 2009
    Location
    Westside
    Posts
    2,083
    Post Likes
    Can you just use a PID those work well in kit control. Or a reset??

  3. #3
    Join Date
    Apr 2003
    Posts
    115
    Post Likes
    Thread Starter
    Yea I am going to use a pid but I need the chart to know what the superheat is. I would need 50 reset blocks to try to make this so I'd rather write a custom module

  4. #4
    Join Date
    Jul 2009
    Location
    Westside
    Posts
    2,083
    Post Likes
    Any suction pressure transducers?? Suction line temp?? This could all help. R-22?? 410??

  5. #5
    Join Date
    Jan 2002
    Location
    Fort Worth\Dallas, Texas
    Posts
    2,339
    Post Likes
    I have a program object for R22.
    Go Rangers!

  6. #6
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    2,062
    Post Likes
    Lane I would be interested in that program too


    Thanks


    Kevin


    Email in my profile

    Sent from my DROID RAZR using Tapatalk 2

    Controls is a lifestyle not a job

  7. #7
    Join Date
    Jan 2002
    Location
    Fort Worth\Dallas, Texas
    Posts
    2,339
    Post Likes
    Shoot me an email and I will send it to you. It took me forever to find the right equation for this and then when I did I had trouble getting it in the program object and functioning correctly. I have to give the final credit to Ron aka Codewriter for getting it completed for me. You can set the input to PSIG,PSIA, or KPA.
    Go Rangers!

  8. #8
    Join Date
    Jul 2008
    Location
    Melbourne
    Posts
    1,611
    Post Likes
    Quote Originally Posted by lwarren View Post
    I have a program object for R22.
    PV=mRT ... hmm would like a look at the program object too if poss.
    1 + 1 = 3 ( *** for very large values of 1)

    ...everybody wants a box of chocolates and long stemmed rose

    Be brave. You cannot get eaten by an imaginary tiger.

  9. #9
    Join Date
    May 2006
    Location
    Greater Atlanta Area
    Posts
    614
    Post Likes
    I would be interested in a copy as well.

    tia

  10. #10
    Join Date
    Jan 2002
    Location
    Fort Worth\Dallas, Texas
    Posts
    2,339
    Post Likes
    I don't see your email listed Matrix. Whoever wants it just send me an email.
    Go Rangers!

  11. #11
    Join Date
    Apr 2003
    Posts
    115
    Post Likes
    Thread Starter
    Quote Originally Posted by Norriski Tech View Post
    Any suction pressure transducers?? Suction line temp?? This could all help. R-22?? 410??
    yes i have suction pressure transducers and suction line temp. This is r134, but i can take the r-22 table and edit all the values to change it to 134.

  12. #12
    Join Date
    Feb 2009
    Location
    Pawtucket, RI
    Posts
    34
    Post Likes
    I would appreciate a copy, thank you.

  13. #13
    Join Date
    Jan 2013
    Location
    San Diego, CA
    Posts
    1
    Post Likes
    Me too, I would appreciate a copy of this program object. Thank you!

  14. #14
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    730
    Post Likes
    This can be done with kitControl math blocks and a little help from excel's Trendline feature. Copy and paste the temperature vs pressure values in to excel. Convert to PSIA and Deg R (curve fitting works better). Create a graph and try the various Trendlines until you get a good fit. I came up with this for R134a. y = 0.00003561 x^3 - 0.01308796 x^2 + 2.12259171 x + 421.11910836 With x = PSIA and a range of 20.7 to 149.7 and y = deg R.
    Name:  R134a.jpg
Views: 1883
Size:  42.4 KB
    UA LU 562

  15. #15
    Join Date
    Jul 2010
    Location
    Az
    Posts
    95
    Post Likes
    Could I get a copy of the program objects also, email is in my profile, Thank you.

  16. #16
    Join Date
    Jul 2008
    Location
    Melbourne
    Posts
    1,611
    Post Likes
    Quote Originally Posted by DaveCR View Post
    I came up with this for R134a. y = 0.00003561 x^3 - 0.01308796 x^2 + 2.12259171 x + 421.11910836 ]
    nice work ... though I think it maybe time to make a generic curve-fit Program Object to the 4th or 5th order.

    ...maybe even have an Enum setting for different refrigerants
    1 + 1 = 3 ( *** for very large values of 1)

    ...everybody wants a box of chocolates and long stemmed rose

    Be brave. You cannot get eaten by an imaginary tiger.

  17. #17
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    730
    Post Likes
    Thanks. For 134a:
    y = 9.20621E-10 x^5 - 6.26875E-07 x^4 + 1.65989E-04 x^3 - 2.26106E-02 x^2 + 2.14070E+00 x - 1.32707E+01
    Input pressure range (PSIA) 14.7 to 244.7. Output °R. This turns out to be quite a good fit with R squared = 0.9999
    Last edited by DaveCR; 01-27-2013 at 10:44 AM. Reason: punctuation
    UA LU 562

  18. #18
    Join Date
    Mar 2007
    Posts
    554
    Post Likes
    Quote Originally Posted by DaveCR View Post
    This can be done with kitControl math blocks and a little help from excel's Trendline feature. Copy and paste the temperature vs pressure values in to excel. Convert to PSIA and Deg R (curve fitting works better). Create a graph and try the various Trendlines until you get a good fit. I came up with this for R134a. y = 0.00003561 x^3 - 0.01308796 x^2 + 2.12259171 x + 421.11910836 With x = PSIA and a range of 20.7 to 149.7 and y = deg R.
    Name:  R134a.jpg
Views: 1883
Size:  42.4 KB
    I've been attempting to set this up all morning for R410A and I can't seem to figure out for the life of me how to get it to output properly. I know lynxspring has an actual conversion block in their lynxKitControl, but unfortunately it only works with their certificate on the JACE.

    Anyone else sucessfully made this work for 410?
    Friends don't let friends Lon.

  19. #19
    Join Date
    Jan 2002
    Location
    Fort Worth\Dallas, Texas
    Posts
    2,339
    Post Likes
    Quote Originally Posted by noskilltech View Post
    I've been attempting to set this up all morning for R410A and I can't seem to figure out for the life of me how to get it to output properly. I know lynxspring has an actual conversion block in their lynxKitControl, but unfortunately it only works with their certificate on the JACE.

    Anyone else sucessfully made this work for 410?
    I have a program object for 134 that you could probably change the pressure-temp tables in for 410.
    Go Rangers!

  20. #20
    Join Date
    Mar 2007
    Posts
    554
    Post Likes
    I'll send you an email here in just a second. Thanks
    Friends don't let friends Lon.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •